[Equest-users] Unmet hours Sim File Discrepancy
Bishop, Bill
bbishop at pathfinder-ea.com
Tue Jan 6 11:52:51 PST 2015
Kevin,
It has something to do with your Cooling Design Day. When I change NUMBER-OF-DAYS from 120 to the default (1), the unmet cooling hours goes to down to 11. Cue the Spinal Tap jokes…
Regards,
Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image002.jpg at 01D029C0.70431AD0] [cid:image004.jpg at 01D029C0.70431AD0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kevin Kyte
Sent: Tuesday, January 06, 2015 1:37 PM
To: John Aulbach; Matthew J. Baron
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Unmet hours Sim File Discrepancy
Ok guys, thanks for your insight.
From: John Aulbach [mailto:jra_sac at yahoo.com]
Sent: Tuesday, January 06, 2015 10:54 AM
To: Kevin Kyte; Matthew J. Baron
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Unmet hours Sim File Discrepancy
Kevin:
If you could share your .INP and .PD2, it would help us help you.
John R. Aulbach, PE
On Tuesday, January 6, 2015 6:57 AM, Kevin Kyte <KKyte at watts-ae.com<mailto:KKyte at watts-ae.com>> wrote:
Thanks Matthew, the Air-side Summary Report is showing 0% hrs ouside thrl-range and also has the whopping total of 25 unmet hours as seen in the SS-R report.
Still trying to identify why the BEPS states 1320 unmet hours.
Maybe if I uninstall the program and reinstall it might work.
Kevin
-----Original Message-----
From: Matthew J. Baron [mailto:mbaron at wendelcompanies.com<mailto:mbaron at wendelcompanies.com>]
Sent: Tuesday, January 06, 2015 9:52 AM
To: Kevin Kyte; bfountain at greensim.com<mailto:bfountain at greensim.com>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] Unmet hours Sim File Discrepancy
Hi Kevin,
What I like to do is look at the summary tab for each system. If you go to "air-side hvac" and highlight a system in the component tree the select the "summary" tab you will be able to see the space and system total unmet hours for both heating and cooling. By going through each system in the component tree you should be able to identify the problem spaces/system.
Thanks,
Matthew J. Baron, PE
Wendel, 140 John James Audubon Pkwy, Suite 201, Buffalo, NY 14228
p 716.688.0766 f 716.625.6825 e mbaron at wendelcompanies.<mailto:mbaron at wendelcompanies.> com w wendelcompanies. com
ARCHITECTURE ENGINEERING PLANNING ENERGY SERVICES CONSTRUCTION MANAGEMENT
CONFIDENTIALITY NOTICE: This email transmission is confidential and is intended only for the person(s) named above. Its contents may also be protected by privilege, and all rights to privilege are expressly claimed and not waived. If you have received this email in error, please call us immediately and destroy the entire email. If this email is not intended for you, any reading, distribution, copying or disclosure of this email is strictly prohibited.
Please consider the environment before printing this email.
-----Original Message-----
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Kevin Kyte
Sent: Tuesday, January 06, 2015 9:47 AM
To: bfountain at greensim.com<mailto:bfountain at greensim.com>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Unmet hours Sim File Discrepancy
Thanks Brian, SS-R shows a whopping total of 25 unmet hours for all systems.
Kevin
-----Original Message-----
From: bfountain at greensim.com<mailto:bfountain at greensim.com> [mailto:bfountain at greensim.com<mailto:bfountain at greensim.com>]
Sent: Tuesday, January 06, 2015 9:44 AM
To: Kevin Kyte
Subject: Re: [Equest-users] Unmet hours Sim File Discrepancy
Check SS-R -- although it will show what the air-side summary shows.
Brian Fountain
bfountain at greensim.com<mailto:bfountain at greensim.com>
-----Original Message-----
From: Kevin Kyte <KKyte at watts-ae.com<mailto:KKyte at watts-ae.com>>
Sender: "Equest-users" <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>>
Date: Tue, 6 Jan 2015 09:39:54
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org><equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Subject: [Equest-users] Unmet hours Sim File Discrepancy
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150106/9df5e88e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150106/9df5e88e/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150106/9df5e88e/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 3856 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150106/9df5e88e/attachment.png>
More information about the Equest-users
mailing list