[Equest-users] eQUEST Transformer Loss - incorrect error if < 1
Shaun Martin
smartin at shaunmartinconsulting.com
Mon Jan 19 11:54:09 PST 2015
Hi Brian,
Im not sure which version of eQuest youre using. Version 3.64 defaults to
0.02. If you right click on the transformer loss box you can change this to
whatever you want.
Shaun
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
Behalf Of bfountain at greensim.com
Sent: Monday, January 19, 2015 7:47 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQUEST Transformer Loss - incorrect error if < 1
The transformer loss in eQUEST should be the fraction of output power lost
at full load. It should be in the order of 1 to 3% so an input of 0.02 for
example. However the range checking in eQUEST is looking for a value
greater than 1 (in the range of 1 1.5). A value of 1 does in fact double
your electrical usage (with ½ going to Pumps and Aux for the transformer
loss) so the range checking is in error.
Is there a way to access and change the error checking values?
Thank you.
Brian
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150119/db290681/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3923 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150119/db290681/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 33658 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150119/db290681/attachment-0003.png>
More information about the Equest-users
mailing list