[Equest-users] eQUEST Transformer Loss - incorrect error if < 1
bfountain at greensim.com
bfountain at greensim.com
Mon Jan 19 07:46:59 PST 2015
The transformer loss in eQUEST should be the fraction of output power lost
at full load. It should be in the order of 1 to 3% so an input of 0.02 for
example. However the range checking in eQUEST is looking for a value
greater than 1 (in the range of 1 1.5). A value of 1 does in fact double
your electrical usage (with ½ going to Pumps and Aux for the transformer
loss) so the range checking is in error.
Is there a way to access and change the error checking values?
Thank you.
Brian
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150119/899e5eb1/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 33658 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150119/899e5eb1/attachment-0001.png>
More information about the Equest-users
mailing list