[Equest-users] Using an Equip-Control as a Parametric Run

John Aulbach jra_sac at yahoo.com
Mon Jun 29 08:40:15 PDT 2015


Hi Chris:
No apologies needed. Just to let you know, I have been doing eQuest for 10 years and DOE-2 for 35 years, so I am familiar with a few straight forward strategies such as you suggest. Let me elaborate on the entire situation and my "solution" (yes, I worked this weekend).
I have a two story structure with a lower level as well, about 280,000 sf. Some areas of the building are straight shot reheat systems - these go 24/7. Then there are areas in ALL levels that serve mainly offices that are not occupied all the time (and certainly not on weekends). These areas are served by single fan double duct systems.
My desire was to back off the double duct heating and cooling during off hours during the weekdays and completely on weekends.
Since a single fan double duct system will increase the heating for a reduction in cooling (and respond only to the HEAT-SET-T side), I first made the units dual fan (but not VAV). This separated the thermostats. So I then backed off on those during the off hours.
I also made two CIRCULATION-LOOPS for the 24/7 zones and the exterior office areas. I then shut off the exterior zones hot water circ pump when the spaces were not occupied.
And with this approach, I got the expected 165,000 kWh annual cooling savings and about 25% gas heating savings for the entire building. The setbacks are OK, as this building in the Southern California.
AS Mr. Spock would say "What do you think of my Solution?'
Your response on a weekend was MOST appreciated.
John R. Aulbach, PE 


     On Monday, June 29, 2015 5:05 AM, "Jones, Christopher" <Christopher.r.Jones at wspgroup.com> wrote:
   

 #yiv6592925723 #yiv6592925723 -- _filtered #yiv6592925723 {font-family:Helvetica;panose-1:2 11 6 4 2 2 2 2 2 4;} _filtered #yiv6592925723 {font-family:Helvetica;panose-1:2 11 6 4 2 2 2 2 2 4;} _filtered #yiv6592925723 {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;} _filtered #yiv6592925723 {font-family:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;} _filtered #yiv6592925723 {panose-1:2 11 5 3 2 1 2 2 2 4;}#yiv6592925723 #yiv6592925723 p.yiv6592925723MsoNormal, #yiv6592925723 li.yiv6592925723MsoNormal, #yiv6592925723 div.yiv6592925723MsoNormal {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;}#yiv6592925723 a:link, #yiv6592925723 span.yiv6592925723MsoHyperlink {color:blue;text-decoration:underline;}#yiv6592925723 a:visited, #yiv6592925723 span.yiv6592925723MsoHyperlinkFollowed {color:purple;text-decoration:underline;}#yiv6592925723 p.yiv6592925723MsoAcetate, #yiv6592925723 li.yiv6592925723MsoAcetate, #yiv6592925723 div.yiv6592925723MsoAcetate {margin:0in;margin-bottom:.0001pt;font-size:8.0pt;}#yiv6592925723 p.yiv6592925723msoacetate, #yiv6592925723 li.yiv6592925723msoacetate, #yiv6592925723 div.yiv6592925723msoacetate {margin-right:0in;margin-left:0in;font-size:12.0pt;}#yiv6592925723 p.yiv6592925723msonormal, #yiv6592925723 li.yiv6592925723msonormal, #yiv6592925723 div.yiv6592925723msonormal {margin-right:0in;margin-left:0in;font-size:12.0pt;}#yiv6592925723 p.yiv6592925723msochpdefault, #yiv6592925723 li.yiv6592925723msochpdefault, #yiv6592925723 div.yiv6592925723msochpdefault {margin-right:0in;margin-left:0in;font-size:12.0pt;}#yiv6592925723 span.yiv6592925723msohyperlink {}#yiv6592925723 span.yiv6592925723msohyperlinkfollowed {}#yiv6592925723 span.yiv6592925723emailstyle17 {}#yiv6592925723 p.yiv6592925723msonormal1, #yiv6592925723 li.yiv6592925723msonormal1, #yiv6592925723 div.yiv6592925723msonormal1 {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;}#yiv6592925723 span.yiv6592925723msohyperlink1 {color:blue;text-decoration:underline;}#yiv6592925723 span.yiv6592925723msohyperlinkfollowed1 {color:purple;text-decoration:underline;}#yiv6592925723 p.yiv6592925723msoacetate1, #yiv6592925723 li.yiv6592925723msoacetate1, #yiv6592925723 div.yiv6592925723msoacetate1 {margin:0in;margin-bottom:.0001pt;font-size:8.0pt;}#yiv6592925723 span.yiv6592925723emailstyle171 {color:#1F497D;}#yiv6592925723 p.yiv6592925723msochpdefault1, #yiv6592925723 li.yiv6592925723msochpdefault1, #yiv6592925723 div.yiv6592925723msochpdefault1 {margin-right:0in;margin-left:0in;font-size:10.0pt;}#yiv6592925723 span.yiv6592925723EmailStyle29 {color:#1F497D;}#yiv6592925723 span.yiv6592925723BalloonTextChar {}#yiv6592925723 .yiv6592925723MsoChpDefault {font-size:10.0pt;} _filtered #yiv6592925723 {margin:1.0in 1.0in 1.0in 1.0in;}#yiv6592925723 div.yiv6592925723WordSection1 {}#yiv6592925723 My apologies John, I am not fully understanding what you are trying to simulate.  To paraphrase, you are trying to show savings by implementing a heating set-back schedule during unoccupied hours.  And, you want the boiler to shut off during those unoccupied hours when no heating is required?    Setting the heating loop LOOP-OPERATION = DEMAND-ONLY (as opposed to STANDBY) will run the boiler only when there is a call for heating.     Am I still missing something?     Christopher Jones,P.Eng.
Senior Engineer    WSP Canada Inc. 2300 Yonge Street, Suite 2300 Toronto, ON M4P 1E4
T +1 416-644-4226 F +1 416-487-9766 C +1 416-697-0065    www.wspgroup.com    From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]On Behalf Of John Aulbach
Sent: Sunday, June 28, 2015 11:21 AM
To: Equest-users
Subject: [Equest-users] Using an Equip-Control as a Parametric Run   To the Royal order of eQuesters (and other such people):   I am trying to show savings from basically setting back a perimeter double duct system after hours. I believe I have it figures that I actually need to reset the Heat-Set-T, as a single fan DD system seems to only react to that set-point. I must then figure out how to shut off ther boiler on a nightly basis.   This of course would use the Equipment-Control and Load-Management. But what parameters within would be my change elements? The Flags? Has anyone ever set this up?   Thanks.   John R. Aulbach, PE 
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitmentwww.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us atcaslcompliance at wspgroup.com so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership   
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitmentwww.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us atcaslcompliance at wspgroup.com so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership

  
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150629/7a858a54/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150629/7a858a54/attachment.png>


More information about the Equest-users mailing list