[Equest-users] Electric Peak Demand

Nicholas Caton ncaton at catonenergy.com
Mon Mar 2 11:56:17 PST 2015


Amy:  Sounds like a simple mix-up.



The BEPU report displays annual consumption totals for each meter.  The
PS-F reports by contrast include both consumption sums and demand values
corresponding to the hour of maximum draw for each end-use (scroll to the
bottom for annual peaks and consumption totals).



You might find it easier for documenting your first few LEED models to
reference the graphical end-use reports for consumption and demand – that’s
how I started out:







*NICK CATON, P.E.*
*Owner*



*Caton Energy Consulting*
  1150 N. 192nd St., #4-202

  Shoreline, WA 98133
  office:  785.410.3317

www.catonenergy.com



*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
Behalf Of *Harmon, Amy
*Sent:* Monday, March 02, 2015 10:38 AM
*To:* Steve Jacobs; equest-users at lists.onebuilding.org
*Subject:* Re: [Equest-users] Electric Peak Demand



I used the values found in the BEPU report to put in the online template.



*From:* Steve Jacobs [mailto:sjacobseng at gmail.com <sjacobseng at gmail.com>]
*Sent:* Monday, March 02, 2015 1:14 PM
*To:* Harmon, Amy; equest-users at lists.onebuilding.org
*Subject:* RE: [Equest-users] (no subject)



This doesn’t sound like an issue with your electric rates. They are saying
that the actual peak demand that you reported in the LEED template does not
match the peak demand by end use stated in the PS-F report. What was the
source of the values you inputted in Table EAp2-5?









*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
<equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Harmon, Amy
*Sent:* Monday, March 2, 2015 2:48 PM
*To:* equest-users at lists.onebuilding.org
*Subject:* [Equest-users] (no subject)



I received the following comment back from USGBC and was hoping someone
could help shed some light on this for me.



*Table EAp2-5 indicates peak demands have been reported for the Baseline
and Proposed cases; however, these values do not coincide with the energy
modeling outputs provided.  For example, Table EAp2-5 indicates the
Proposed Case lighting peak is 879.8 MBH (257.8 kWh); however, the PS-F
report indicates the peak Proposed Case lighting power is 34.022 KW.
Review the energy modeling output reports and remove any demand value
inconsistencies.*



The project was designed around a uniform electric rate of $0.0703/kWh and
this amount was entered in the Electric Utility Charge screen 4 of 7 in the
wizard mode (photo attached).



Is the USGBC comment aimed at the utility rate or is it something that
needs addressed back in Wizard mode?  If so, how do I go about fixing it?



Any help / guidance is much appreciated.

Thanks!





Amy Harmon

Mechanical Engineer

Scheeser Buckley Mayfield LLC

1540 Corporate Woods Parkway

Uniontown, OH 44685

Phone: (330) 896-4664 ext. 107

Direct: (330) 526-2707

Fax: (330) 896-9180

aharmon at sbmce.com

www.sbmce.com



Please consider the environment before printing this email. This e-mail
(including any attachments) is confidential and may be legally privileged.
If you are not an intended recipient or an authorized representative of an
intended recipient, you are prohibited from using, copying or distributing
the information in this e-mail or its attachments. If you have received
this e-mail in error, please notify the sender immediately by return e-mail
and delete all copies of this message and any attachments.



Thank you
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150302/29eec2db/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 46998 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150302/29eec2db/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 45480 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150302/29eec2db/attachment-0001.png>


More information about the Equest-users mailing list