[Equest-users] Electric Peak Demand

Jones, Christopher cjones at halsall.com
Mon Mar 2 14:41:14 PST 2015


Thank you guys.  I am so used to looking in the sim file that I never noticed those reports.

Christopher Jones, P.Eng.
Tel: 416.644.4226 • Toll Free: 1.888.425.7255 x 527

From: Nicholas Caton [mailto:ncaton at catonenergy.com]
Sent: Monday, March 02, 2015 5:15 PM
To: Chris Baker; Jones, Christopher
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Electric Peak Demand

Just as Chris B advised ;)!
[cid:image001.png at 01D05510.14368760]

NICK CATON, P.E.
Owner

Caton Energy Consulting
  1150 N. 192nd St., #4-202
  Shoreline, WA 98133
  office:  785.410.3317
www.catonenergy.com

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Chris Baker
Sent: Monday, March 02, 2015 1:59 PM
To: Jones, Christopher
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Electric Peak Demand

With results view open, left click on “reports” tab at the bottom left of the screen.

Your energy demand reports will be listed.

You can use those reports to get your peak demand numbers.

You may even want to check the eap2 tables (excel file), if you know what that is, to check the electrical demand being claimed for lighting, plug load power density, etc…

That would also help find inconsistencies in peak demand being claimed.

-Chris

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher
Sent: Monday, March 02, 2015 11:42 AM
To: Nicholas Caton; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Electric Peak Demand

Nick,
I must admit I haven’t actually looked at the eQuest graphs and tables you included in your email.  So, I thought I would give it a try.  When I press the Results View button, I get the consumption graphs and tables for electricity and gas but I don’t get the second page with the demand information.  I am using eQuest v 3.65 7158.



Christopher Jones, P.Eng.
Tel: 416.644.4226 • Toll Free: 1.888.425.7255 x 527

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nicholas Caton
Sent: Monday, March 02, 2015 2:56 PM
To: Harmon, Amy; Steve Jacobs; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Electric Peak Demand

Amy:  Sounds like a simple mix-up.

The BEPU report displays annual consumption totals for each meter.  The PS-F reports by contrast include both consumption sums and demand values corresponding to the hour of maximum draw for each end-use (scroll to the bottom for annual peaks and consumption totals).

You might find it easier for documenting your first few LEED models to reference the graphical end-use reports for consumption and demand – that’s how I started out:
[cid:image002.png at 01D05510.14368760]
[cid:image003.png at 01D05510.14368760]



NICK CATON, P.E.
Owner

Caton Energy Consulting
  1150 N. 192nd St., #4-202
  Shoreline, WA 98133
  office:  785.410.3317
www.catonenergy.com

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Harmon, Amy
Sent: Monday, March 02, 2015 10:38 AM
To: Steve Jacobs; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Electric Peak Demand

I used the values found in the BEPU report to put in the online template.

From: Steve Jacobs [mailto:sjacobseng at gmail.com]
Sent: Monday, March 02, 2015 1:14 PM
To: Harmon, Amy; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] (no subject)

This doesn’t sound like an issue with your electric rates. They are saying that the actual peak demand that you reported in the LEED template does not match the peak demand by end use stated in the PS-F report. What was the source of the values you inputted in Table EAp2-5?




From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Harmon, Amy
Sent: Monday, March 2, 2015 2:48 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] (no subject)

I received the following comment back from USGBC and was hoping someone could help shed some light on this for me.

Table EAp2-5 indicates peak demands have been reported for the Baseline and Proposed cases; however, these values do not coincide with the energy modeling outputs provided.  For example, Table EAp2-5 indicates the Proposed Case lighting peak is 879.8 MBH (257.8 kWh); however, the PS-F report indicates the peak Proposed Case lighting power is 34.022 KW.  Review the energy modeling output reports and remove any demand value inconsistencies.

The project was designed around a uniform electric rate of $0.0703/kWh and this amount was entered in the Electric Utility Charge screen 4 of 7 in the wizard mode (photo attached).

Is the USGBC comment aimed at the utility rate or is it something that needs addressed back in Wizard mode?  If so, how do I go about fixing it?

Any help / guidance is much appreciated.
Thanks!


Amy Harmon
Mechanical Engineer
Scheeser Buckley Mayfield LLC
1540 Corporate Woods Parkway
Uniontown, OH 44685
Phone: (330) 896-4664 ext. 107
Direct: (330) 526-2707
Fax: (330) 896-9180
aharmon at sbmce.com<mailto:aharmon at sbmce.com>
www.sbmce.com<http://www.sbmce.com/>

Please consider the environment before printing this email. This e-mail (including any attachments) is confidential and may be legally privileged. If you are not an intended recipient or an authorized representative of an intended recipient, you are prohibited from using, copying or distributing the information in this e-mail or its attachments. If you have received this e-mail in error, please notify the sender immediately by return e-mail and delete all copies of this message and any attachments.

Thank you


______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.

________________________________

CCI-Alliance Confidentiality notice: This message is intended only for the person to whom addressed in the text above and may contain privileged or confidential information. If you are not that person, any use of this message is prohibited. We request that you notify us by reply to this message, and then delete all copies of this message including any contained in your reply. Thank you.

______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150302/fd5e9f0c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 54954 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150302/fd5e9f0c/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 46998 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150302/fd5e9f0c/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 45480 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150302/fd5e9f0c/attachment-0002.png>


More information about the Equest-users mailing list