Table G3.1#6(Baseline indicates that the same categorization procedure
should be used. If you want to use the building area method in the Baseline
then the same method should be used in the Proposed. If the project includes
more than one building type in Table 9.5.1, then the average LPD in the
proposed case must be calculated separately and applied for each area
separately.
Hope this helps!
Cam Fitzgerald
Energy Opportunities/a 7group company
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
Behalf Of Steve Jacobs
Sent: Thursday, March 12, 2015 11:31 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Building Area Method
When modeling a building using the "Building Area Method" are you also
allowed to model the proposed model with the average LPD of the whole
building? Or do I still need to break the proposed down space by space? For
example, I'm working on a renovated school. I have a very detailed breakdown
of the new lighting in the school, but it is just a list. Not drawings that
break it down by space. I want to use the building area method in the
baseline and then model all the proposed spaces with the average LPD of the
whole facility. Is there some there something that gives definitive guidance
one way or another to this approach?