[TRNSYS-users] Error message

David BRADLEY d.bradley at tess-inc.com
Mon Aug 26 08:16:47 PDT 2013


I have also seen this error occur if the atmospheric pressure input 
doesn't get connected from the weather file to the other components in 
the HVAC system.
Best,
  David


On 8/25/2013 19:10, a8304506 at graduate.hku.hk wrote:
> Hello, Bharath.
>
> This error usually arise from the inappropriate selection of parameter/input
> values for the cooling tower.  Try increase the air flowrate or decrease the
> water flowrate to see if the error disappears.
>
> Best Regards
> Chun Kwong LEE
> City Universtiy of Hong Kong
>
>
> Quoting Bharath Seshadri <s.bharath at ntu.edu.sg>:
>
>> Dear TRNSYS users,
>>
>> I get the following error message (I suspect from a cooling tower component).
>> Any idea how I can correct this?
>>
>> "The utility routine PSYCHROMETRICS, which calculates thermodynamic
>> properties of moist air, has been called with a wet bulb temperature above
>> maximum wet bulb temperature for given pressure. Please check routine which
>> calls PSYCHROMETRICS routine for possible sources of errors. "
>>
>> Thanks,
>> Bharath
>>
>> -----Original Message-----
>> From: trnsys-users-bounces at cae.wisc.edu
>> [mailto:trnsys-users-bounces at cae.wisc.edu] On Behalf Of
>> trnsys-users-request at cae.wisc.edu
>> Sent: Friday, August 23, 2013 7:52 PM
>> To: trnsys-users at cae.wisc.edu
>> Subject: TRNSYS-users Digest, Vol 104, Issue 38
>>
>> Send TRNSYS-users mailing list submissions to
>>          trnsys-users at cae.wisc.edu
>>
>> To subscribe or unsubscribe via the World Wide Web, visit
>>          https://mailman.cae.wisc.edu/listinfo/trnsys-users
>> or, via email, send a message with subject or body 'help' to
>>          trnsys-users-request at cae.wisc.edu
>>
>> You can reach the person managing the list at
>>          trnsys-users-owner at cae.wisc.edu
>>
>> When replying, please edit your Subject line so it is more specific than "Re:
>> Contents of TRNSYS-users digest..."
>>
>> CONFIDENTIALITY:This email is intended solely for the person(s) named and may
>> be confidential and/or privileged.If you are not the intended
>> recipient,please delete it,notify us and do not copy,use,or disclose its
>> content.
>>
>> Towards A Sustainable Earth:Print Only When Necessary.Thank you.
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at cae.wisc.edu
>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com




More information about the TRNSYS-users mailing list