Dev,

in the standard trnsys model, the absorption chiller capacity is set as a
function of the temperature difference and flow rate on the evaporator, in
other words, there is no relation on the capacity neither with the
generator flow rate nor inlet temperature. Once identified the fraction of
nominal capacity depending on the chilled water conditions, and corrected
as per the external file, the model imposes the necessary temperature
differences to the other flow rates. Therre are no internal controls on
type 107, while real chillers usually have some kind of control on flow
rates and temperatures in the fluid loops.
I recommend you to take a look the type 107 description in the mathematical
reference to understand what's going on inside the type.

Angel


2013/5/2 dev sharma <devsharmami at gmail.com>

> Hej All,
>
> I am trying to model a solar based absorption cycle.
>
> The experimental data with me, has following observations:
> 1. If I change just the hot water flowrate (reduced to half), the
> capacity of the chiller reduces considerably (approx by 40%).
> In model: Instead of reduction in capacity, the temperature drop of
> hot water increases.
> 2. If I change just the hot water inlet temperature (by over 10 DegC
> i.e 92-80), the capacity drop is considerable again( approx 60%)
> In model: Instead of reduction in capacity, the temperature drop of
> hot water is in w different range that's all. (80-70 DegC).
>
> I have changed the data file for type 107 in terms of operating
> temperature i.e from initial 108-116DegC to 70-95DegC.
>
> I am attaching the modified data file.
>
> Can someone please help me to modify this data file to suit the above
> mentioned trends?
>
> Thanks
> Dev Sharma
>
> --
> Dev Sharma
> Erasmus Mundus Masters in Sustainable Energy
> KTH, Stockholm & UPC, Barcelona
> Mobile: +34635104882 (Spain)
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>


-- 
*Àngel Carrera*

*Consultor Senior
Àrea tècnica*

Sistemes Avançats d'Energia Solar Tèrmica SCCL
C/ Roger de Llúria, 29 3r 2a 08009 Barcelona
Mòbil: (+34) 663 27 66 80
Tel: (+34) 93 342 47 55
Fax: (+34) 93 342 47 56

angel.carrera at aiguasol.coop
http://www.aiguasol.coop
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130502/70d8c389/attachment-0001.htm>


More information about the TRNSYS-users mailing list