David BRADLEY d.bradley at tess-inc.com
Tue Nov 26 07:33:26 PST 2013


Wang,
   That error usually indicates that too large a value is trying to be 
written into a formatted output file. For example, if a Type (56 in this 
case) tries to write the number 100 to an output file using a format 
statement that only allows two digit numbers. Unfortunately there is 
nothing that a user can do to solve the problem. If you send your 
project and all the files needed to run it to your distributor they can 
correct the error.
Regards,
  David


On 11/26/2013 03:42, 王洋 wrote:
>
> Dear all,
>
> Good day!
>
> I met an error "Forrtl: severe (38): error during write, unit 44, file 
> SUMMARY.BAL", which was attached by a file.
>
> Did you meet this problem? How could you deal with it?
>
> Many thanks in advance!
>
> Br.
>
> yang wang
>
> 2013/11/25 <trnsys-users-request at cae.wisc.edu 
> <mailto:trnsys-users-request at cae.wisc.edu>>
>
>     Send TRNSYS-users mailing list submissions to
>     trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>
>     To subscribe or unsubscribe via the World Wide Web, visit
>     https://mailman.cae.wisc.edu/listinfo/trnsys-users
>     or, via email, send a message with subject or body 'help' to
>     trnsys-users-request at cae.wisc.edu
>     <mailto:trnsys-users-request at cae.wisc.edu>
>
>     You can reach the person managing the list at
>     trnsys-users-owner at cae.wisc.edu
>     <mailto:trnsys-users-owner at cae.wisc.edu>
>
>     When replying, please edit your Subject line so it is more specific
>     than "Re: Contents of TRNSYS-users digest..."
>
>     Today's Topics:
>
>        1. Where can I find some example to couple the Type56 Multizone
>           and Type101 Fluent? (Yi Lu)
>        2. Re: help (David BRADLEY)
>
>
>     ---------- 已转发邮件 ----------
>     From: Yi Lu <yi.lu at funature.net <mailto:yi.lu at funature.net>>
>     To: "TRNSYS users mailing list at the Solar Energy Lab,
>     UW-Madison" <trnsys-users at cae.wisc.edu
>     <mailto:trnsys-users at cae.wisc.edu>>
>     Cc:
>     Date: Mon, 25 Nov 2013 17:50:20 +0100
>     Subject: [TRNSYS-users] Where can I find some example to couple
>     the Type56 Multizone and Type101 Fluent?
>     Hello,
>
>     I'm doing some research on the coupling of Trnsys(TYPE56
>     Multizone) and CFD program recently. The most referenced work is
>     the doctoral thesis of Z. Zhai, “Developing an integrated building
>     design tool by coupling building energy simulation and
>     computational fluid dynamics programs,” Thesis, Massachusetts
>     Institute of Technology, 2003.
>     http://dspace.mit.edu/handle/1721.1/17617
>     And I see there is also a Type101 in TRNSYS for calling Fulent, so
>     I tried to find more information about it, the only thing I found
>     is a paper from Diego A. Arias
>     http://www.ibpsa.us/pub/simbuild2006/papers/SB06_231_237.pdf. In
>     the paper Multizone is unfortunately not involved. I hope I can
>     get more information from you here.
>     According to  the work of Zhai,  the convective heat transfer from
>     wall surface to air is the key of the coupling process. My
>     Question is, How can I implement the convective heat flux to TRNSYS?
>
>
>     Best regards!
>
>     Yi
>
>
>     ---------- 已转发邮件 ----------
>     From: David BRADLEY <d.bradley at tess-inc.com
>     <mailto:d.bradley at tess-inc.com>>
>     To: E.Nguepi-Donjio at stud.hs-esslingen.de
>     <mailto:E.Nguepi-Donjio at stud.hs-esslingen.de>, "TRNSYS users
>     mailing list at the Solar Energy Lab, UW-Madison"
>     <trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>>
>     Cc:
>     Date: Mon, 25 Nov 2013 11:36:55 -0600
>     Subject: Re: [TRNSYS-users] help
>     Eric,
>       The tutorial that I mentioned last week is exactly what you are
>     asking for. It shows how to connect controller Types and equipment
>     Types to a Type56 building simulation. The tutorial (called
>     "temperature level control from energy rate control") can be
>     downloaded from:
>
>     http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex17.htm
>
>     Regards,
>      David
>
>
>
>
>     On 11/24/2013 04:50, Nguepi Donjio Eric Constant wrote:
>
>         David,
>         Thanks for your answer, it helped me a lot. But what I really
>         wanted to
>         know is:
>         How is the Type 987 and Type 600 tied together with a building
>         project
>         with a controller?
>         please please how me an example.
>
>
>         Kind regards,
>         Eric
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>         Eric,
>
>                I would recommend that you go through the tutorial
>             called "temperature
>             level control from energy rate control" that is available
>             for download
>             from
>             http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex17.htm
>
>                It describes the process of migrating from using Type56
>             to compute
>             heating and cooling loads to using controllers and
>             equipment models to
>             condition the space.
>                Kind regards,
>                David
>
>
>             On 11/21/2013 00:02, Nguepi Donjio Eric Constant wrote:
>
>                 hello users,
>
>                 ich möchte ein Hotelzimmer (Building-Projekt) mit Fan
>                 Coil (Type 987
>                 oder
>                 Type 600) simulieren. Man muss dabei ein richtiger
>                 Regler auswählen,
>                 sonst
>                 macht die Simulation kein Sinn. Ich habe dabei alles
>                 versucht, aber ich
>                 kann das nicht zum laufen bringen. Bitte kann mir
>                 jemand ein Beispiel
>                 schicken? So kann ich sehen wie die Verbindungen
>                 gemacht wurde.
>
>                 Thanks for any help.
>
>                 _______________________________________________
>                 TRNSYS-users mailing list
>                 TRNSYS-users at cae.wisc.edu
>                 <mailto:TRNSYS-users at cae.wisc.edu>
>                 https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>             --
>             ***************************
>             David BRADLEY
>             Principal
>             Thermal Energy Systems Specialists, LLC
>             22 North Carroll Street - suite 370
>             Madison, WI  53703 USA
>
>             P:+1.608.274.2577 <tel:%2B1.608.274.2577>
>             F:+1.608.278.1475 <tel:%2B1.608.278.1475>
>             d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
>
>             http://www.tess-inc.com
>             http://www.trnsys.com
>
>             _______________________________________________
>             TRNSYS-users mailing list
>             TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
>             https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>         _______________________________________________
>         TRNSYS-users mailing list
>         TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
>         https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>     -- 
>     ***************************
>     David BRADLEY
>     Principal
>     Thermal Energy Systems Specialists, LLC
>     22 North Carroll Street - suite 370
>     Madison, WI  53703 USA
>
>     P:+1.608.274.2577 <tel:%2B1.608.274.2577>
>     F:+1.608.278.1475 <tel:%2B1.608.278.1475>
>     d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
>
>     http://www.tess-inc.com
>     http://www.trnsys.com
>
>
>
>     _______________________________________________
>     TRNSYS-users mailing list
>     TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
>     https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com