[TRNSYS-users] us of Coldbridges
Pauline GELIN
p.gelin at katene.fr
Tue Oct 1 23:40:08 PDT 2013
Hello,
Thank you for your answer.
As I wrote, there is only one wall of 1m² and with a coefficient of 1W/m²K and the coldbridge.
The boundary condition for the wall is 20°C and the inside temperature is 19°C.
The coldbridge is linked to a orientation with no radiation and a outdoor temperature and tsky of 20°C.
The static loss output (QUA) well gives me 2 W but for me the QSENS output doesn’t give me that but a result of 6 W. How can you explain that?
As I wrote before it seems to have a factor of 5 when I change resistance values or lengths of coldbridge.
Moreover, if I change the coldbridge as a wall with also a orientation with no radiation and a fixed outdoor temperature, I have also approximately the same factor between the result I expect and what I have for QSENS output.
Thank you in advance if you have an idea.
Best regards,
Pauline GELIN
Ingénieur Conception environnementale
[cid:image001.jpg at 01CEBF4B.00309780]
[cid:image002.jpg at 01CEBF4B.00309780]
10 avenue des canuts
69120 VAULX EN VELIN
T : 04.37.45.33.33
Ligne directe : 04.37.45.33.47
www.katene.coop
www.quadriplus-groupe.com<http://www.quadriplus-groupe.com>
www.woopa.coop<http://www.woopa.coop>
De : trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] De la part de Avesani Stefano
Envoyé : lundi 30 septembre 2013 11:20
À : TRNSYS users mailing list at the Solar Energy Lab, UW-Madison; David BRADLEY
Objet : Re: [TRNSYS-users] us of Coldbridges
Hi Pauline,
We are deeping the issue of thermal bridges in TRNSYS trying to find the best way of simulating this. What I am trying to simulate is a very simple zone with just one thermal bridge as transmitting external surface. Actually the QSENS calculated is coherent with the whole zone energy balance (of which the CBR “surface” is just one component and the other surfaces contribute to the energy balance even if they are set with BC identical). The heat flux lost through the CBR is then coherent with the formula q[W] = psi*l*deltaT.
What kind of zone have you used? Other surfaces? Which BC?
Looking forward to finding a good answer!
kind regards
Stefano
EURAC research
Institute for Renewable Energy
Via Luis-Zuegg 11, I-39100 Bolzano
t +39 0471 055 654
f +39 0471 055 699
stefano.avesani at eurac.edu<mailto:stefano.avesani at eurac.edu>
www.eurac.edu<http://www.eurac.edu/>
EURAC research
Legal Seat
Viale Druso 1, I-39100 Bolzano
This transmission is intended only for the use of the addressee and may contain confidential or legally privileged information.
If you receive this transmission by error, please notify the author immediately by mail and delete all copies of this transmission and any attachments.
Any use or dissemination of this communication is strictly prohibited by the "Privacy-Code", D.Lgs. 196/2003 and may lead to penal prosecution and liability for damages.
P Think before you print
From: trnsys-users-bounces at cae.wisc.edu<mailto:trnsys-users-bounces at cae.wisc.edu> [mailto:trnsys-users-bounces at cae.wisc.edu] On Behalf Of Pauline GELIN
Sent: Thursday, 19 September, 2013 13:35
To: David BRADLEY; trnsys-users (trnsys-users at cae.wisc.edu<mailto:trnsys-users at cae.wisc.edu>)
Subject: [TRNSYS-users] us of Coldbridges
Hi,
Sorry to multiply the questions but I I try to consolidate our simulations of buildings and another question remains about how the values of resistance and length for a coldbridge are used.
When I want to simulate a very simple building zone (one wall of 1m² with a U equals to 1W/m²K and one coldbridge of 1m with a U equals to 1W/mK) , with no weather data, a constant outside temperature of 19° and a constant inside temperature of 20°C, the QUA output (meaning static losses transmission) is well given as 2 W but the QSENS outputs isn’t (it seems to be equal to 6 W).
When I change lengths or resistance values, it always seems to have a factor of 5 between the input value of coldbridge and the output value of QSENS.
Could someone explain this to me?
Thank you very much for your help.
Best regards,
Pauline GELIN
Ingénieur Conception environnementale
[cid:image003.jpg at 01CEBF4B.00309780]
[cid:image004.jpg at 01CEBF4B.00309780]
10 avenue des canuts
69120 VAULX EN VELIN
T : 04.37.45.33.33
Ligne directe : 04.37.45.33.47
www.katene.coop
www.quadriplus-groupe.com<http://www.quadriplus-groupe.com>
www.woopa.coop<http://www.woopa.coop>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20131002/e315106f/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1718 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20131002/e315106f/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1058 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20131002/e315106f/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1925 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20131002/e315106f/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1089 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20131002/e315106f/attachment-0007.jpg>
More information about the TRNSYS-users
mailing list