[TRNSYS-users] Hot water absorption chiller

David BRADLEY d.bradley at tess-inc.com
Fri Jan 9 13:50:11 PST 2015


Farah,
   In order to get the simulation to run you can put in the same COP and 
capacity data twice into the file, once with a 1.0 part load ratio and 
again with a lower part load ratio. I want to stress, though, that while 
that will make the simulation run, you aren't going to get meaningful 
results out of your simulation unless you can find some part load data. 
Otherwise the chiller is going to run at its full load capacity and COP 
no matter what the inlet conditions to it are.
Best,
  David


On 1/9/2015 13:12, Farah KOJOK wrote:
>
> Dear Sir,
>
> I want to simulate a small hot water absorption chiller (Rotartica 
> Type) on TRNSYS. The data (COP and Cooling capacity) of this chiller 
> are only available for design fraction at full load.
>
> However, when I tried to simulate the solar chiller using an external 
> file that I created, I get an error: I must have 2 design fraction 
> minimum in the external file.
>
> Does anyone have an idea about this?
>
> Thank for your help.
>
> Best regards
>
> Farah KOJOK
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150109/e1693567/attachment-0002.htm>


More information about the TRNSYS-users mailing list