[TRNSYS-users] How to control a circulating pump via OR logic?

Angel Carrera angel.carrera at aiguasol.coop
Fri Jul 31 02:44:19 PDT 2015


Hi,

for this you can use an equation block. Connect the individual control
signals as inputs and on the out puts you generate an equation as

Control=min(1,signal1+signal2)

or

Control=OR(signal1,signal2)

or any other arithmetic/logic combination that meets your requirements.
Then you use this variable as your input control signal by connecting it to
the desired components, hope it helps

Angel

2015-07-31 9:02 GMT+02:00 Theeraphat Sri-on <m5640225 at g.sut.ac.th>:

> >> I need to active circulating pump when a heat pump active and when
> cooling tower active, but a heat pump and cooling tower not  active at same
> time.
>
> >> I need to use a logic OR to control, how can I create a control model
> in TRNSYS for this requirement?, or any ones has another idea please tell
> me.
>
> >>Thanks you for your help.
>
> --
> Best regards,
> ----------
> *Mr.Theeraphat Sri-on*
> *Graduate Student*
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
>


-- 
*Àngel Carrera*


*Consultor SeniorÀrea tècnica*

Sistemes Avançats d'Energia Solar Tèrmica SCCL
C/ Roger de Llúria, 29 3r 2a 08009 Barcelona
Mòbil: (+34) 663 27 66 80
Tel: (+34) 93 342 47 55
Fax: (+34) 93 342 47 56

angel.carrera at aiguasol.coop
http://www.aiguasol.coop
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150731/4ad03d4a/attachment.htm>


More information about the TRNSYS-users mailing list