[TRNSYS-users] Type 107 external data file

David BRADLEY d.bradley at tess-inc.com
Mon May 11 09:41:17 PDT 2015


Anton,
   In order to create a new data file you'll need to have manufacturer's 
data for the machine that you want to model. Manufacturer's data usually 
includes some information that shows how the machine's cooling capacity 
changes as a function of the inlet conditions. Often they give values of 
full-load capacity for a number of inlet water temperatures in a table. 
The fraction of rated capacity is obtained by dividing the capacity at a 
given set of inlet conditions by the capacity at the machine's rated 
inlet conditions. The same principal is true for the design energy 
input. In the case of Type107 the design energy input is the amount of 
energy that is extracted from the hot water stream at the machine's 
rated condition.
kind regards,
  David


On 5/10/2015 4:25 AM, Anton Åhlund wrote:
> Hi!
>
> I'm doing a master thesis in solar cooling and I have problem with the 
> type 107 external data file. I want to use other temperature spans 
> then the ones in the example data file.
>
> I can't figure out how to calculate the <Fraction of rated capacity> 
> and <design energy input>, which changes depending on the different 
> temps. of the fluid flows (inlet hot water temp, chilled water 
> setpoint and cooling water temp). I have looked carefully in the 
> mathematical description pdf but can figure it out. Does anyone know 
> how to calculate this?
>
> Kind regards,
> Anton Åhlund
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150511/a8c773b0/attachment.htm>


More information about the TRNSYS-users mailing list