[Bldg-sim] [EnergyPlus_Support] RE: [Equest-users] White Box Technologies brings simulation weather data to the satellite age

Linda Lawrie linda at fortlawrie.com
Tue Jan 9 04:32:32 PST 2018


Actually, EnergyPlus (and the epw format) uses 
coded flags in the 9 digit "Present Weather 
Codes"  to determine and set Rain/Snow.  Now that 
some stations include precipitation (albeit 
liquid) EnergyPlus sets the rain flag when there 
is adequate precipitation currently.

I believe the updated TMY3 format went away from 
the 9 digit present weather codes, so EnergyPlus 
would rely on the "preciitation" field in the epw file.

It would not be impossible to bring those back to 
the CWEC data; however, probably not as individual flags.

Linda

At 04:44 PM 1/8/2018, Joe Huang via Bldg-sim wrote:
>Content-Type: multipart/alternative;
>  boundary="------------E16429D68ABA1BA04C74DF5C"
>Content-Language: en-US
>
>The rain and snow flags are still available in 
>the raw weather station data, but haven't been 
>included in the processed weather files since 
>the 1990's because  everyone in this hemisphere 
>at least have adopted the TMY2/TMY3 formats, in 
>content  if not the literal file format, 
>developed by NREL, which does not include these 
>two flags. I was also under the impression that 
>none of the simulation programs, such as DOE-2, 
>do not use these two flags anyway.   If these 
>flags are of use, it would make sense to include 
>them, which would not require a change in the 
>DOE-2 *.BINM format, but would require a change to the EnergyPlus *.epw format.
>
>Joe
>
>Joe Huang
>White Box Technologies, Inc.
>346 Rheem Blvd., Suite 205A
>Moraga CA 94556
><mailto:yjhuang at whiteboxtechnologies.com>yjhuang at whiteboxtechnologies.com
>http://weather.whiteboxtechnologies.com for simulation-ready weather data
>(o) (925)388-0265
>(c) (510)928-2683
>"building energy simulations at your fingertips"
>On 1/8/2018 12:15 PM, 'Jones, Christopher' 
><mailto:christopher.r.jones at wsp.com>christopher.r.jones at wsp.com 
>[EnergyPlus_Support] wrote:
>>Â
>>
>>I have a question – what happened to the rain 
>>and snow flags that were in the old CWEC file 
>>but are missing in the latest versions. Many 
>>snow melting systems have a snow/rain sensor in 
>>the slab used to trigger the system on.
>>
>>Â
>>
>>Â
>>
>>Christopher R. Jones, P.Eng.
>>
>>Technical Specialist
>>
>>Sustainability & Energy
>>
>>Â
>>
>>[]
>>
>>
>>T +1 416-644-0252
>>
>>Â
>>
>>2300 Yonge Street, Suite 2300
>>
>>Toronto, ON M4P 1E4 Canada
>>
>><wsp.htm>wsp.com
>>
>>Â
>>
>>Â
>>
>>Please consider the environment before printing...
>>
>>Â
>>
>>Â
>>
>>From: Equest-users 
>>[<mailto:equest-users-bounces at lists.onebuilding.org>mailto:equest-users-bounces at lists.onebuilding.org] 
>>On Behalf Of Joe Huang via Equest-users
>>Sent: Tuesday, January 02, 2018 10:15 PM
>>To: Nicholas Caton 
>><mailto:Nicholas.Caton at schneider-electric.com><Nicholas.Caton at schneider-electric.com>; 
>>BLDG-SIM 
>><mailto:bldg-sim at lists.onebuilding.org><bldg-sim at lists.onebuilding.org>; 
>>EnergyPlus_Support 
>><mailto:EnergyPlus_Support at yahoogroups.com><EnergyPlus_Support at yahoogroups.com>; 
>><mailto:equest-users at onebuilding.org>equest-users at onebuilding.org
>>Cc: Jim Dirkes 
>><mailto:jim at buildingperformanceteam.com><jim at buildingperformanceteam.com>
>>Subject: Re: [Equest-users] White Box 
>>Technologies brings simulation weather data to the satellite age
>>
>>Â
>>
>>Nick,
>>
>>This is an interesting topic that has evolved 
>>in an unexpected way.  Now that NREL has 
>>mastered the technology of satellite-derived 
>>solar radiation, they have regarded weather 
>>station data as an impediment, since there's no 
>>way to get such measured data to match the 
>>5-kilometer grid of the satellite-derived 
>>solar.  Therefore, they have abandoned the 
>>weather station data (which was was used in all 
>>the TMYs to date) and gone instead to 
>>Reanalysis Data from NOAA's MERRA, which is 
>>running a climate forecasting model in 
>>retrospective mode. I don't have time now to 
>>discuss reanalysis, except to say that from 
>>what I've seen the results are decidedly 
>>"iffy".  Almost two years ago, I managed to 
>>get a Work Statement through ASHRAEÂ  for 
>>someone to take a good look at reanalysis data.
>>
>>So, what does this mean for your question? 
>>Â  NREL's National Solar Radiation Data Base 
>>(NSRDB) can now get you the hourly time series 
>>or a TMY for more than a million grid points 
>>over the US, all with satellite-derived solar 
>>radiation but  MERRA results for the other 
>>climate parameters.  I've told NREL several 
>>years ago that for the building simulation 
>>industry it would be much better to merge 
>>the  satellite-derived solar with actual 
>>station data that give good accurate coverage 
>>of urban areas where buildings are located. 
>>NREL's response was that they'd be happy to do 
>>this, but someone has to pay them for the work.
>>
>>In response to your hypothesis below, I think 
>>you're being too disparaging of the previous 
>>modeling efforts while raising too high your 
>>expectations of satellite solar.  It's not 
>>that the previous models failed to account for 
>>local climate conditions, but that they lacked 
>>good data to drive them.  For example, all 
>>models included terms for cloud cover and 
>>clearness, or for the more detailed physical 
>>models arcane parameters like aerosol optical 
>>depth, preciptable moisture, etc.,  but how 
>>available are the input data and how reliable 
>>are they?  The advantages of satellite-derived 
>>solar are that they provide a comprehensive and 
>>objective view of the cloud conditions, which 
>>combined with satellite measurements of the 
>>atmospheric conditions and  improved modeling, 
>>results in  accuracies that previous modeling 
>>efforts can not attain.  As far as discerning 
>>localized effects of smog and dust in urban 
>>areas, that would still depend on whether 
>>there's sufficient monitoring at that spatial 
>>and time scale to detect the differences. 
>>Â  What I mean is that it's one thing to 
>>observe that in general urban locations have 
>>more smog and particulates than rural 
>>locations, but it's something else to quantify 
>>the resultant differences in solar radiation over time and distance.
>>
>>I'd like to take the opportunity here to step 
>>back and comment on the status of weather data 
>>for the building energy community, My 
>>interactions with NREL has brought the 
>>realization that we have been piggy-backing on 
>>the efforts of others outside our community for 
>>our weather data.  I don't intend to pick on 
>>the NREL Solar Program, several of whom I 
>>consider friends and colleagues, but their 
>>target client is the solar power 
>>industry.  Since solar power arrays can be 
>>installed anywhere, preferably in rural 
>>uninhabited locations, it makes sense to go to 
>>satellite-derived solar.  It's also clear that 
>>to serve that industry, NREL would focus its 
>>efforts on getting the best solar values, while 
>>all the other climatic parameters, like 
>>temperature, humidity, wind speed, etc., are 
>>secondary, which may be why getting them from 
>>MERRA is a satisfactory choice.  The focus on 
>>solar is also evident in the weighting used by 
>>NREL to develop the TMYs, with 50% weight 
>>placed on the 2 solar and 50% on the remaining 8 non-solar parameters.
>>
>>For the building energy community, or 
>>priorities are somewhat different. Since 99% of 
>>buildings are located in urban locations, we 
>>should focus much more on climate in urban 
>>areas.  Luckily, that's also where the great 
>>majority of existing weather are located, which 
>>is why I'm resistant to throwing out measured 
>>weather data and replacing them with synthetic 
>>data, no matter how much they've been "seeded" 
>>with real data. As for the weighting of climate 
>>parameters in selecting the typical 
>>months,  why not use building energy 
>>simulations and weight them by the distribution of heating and cooling loads?
>>
>>Joe
>>
>>Joe Huang
>>White Box Technologies, Inc.
>>346 Rheem Blvd., Suite 205A
>>Moraga CA 94556
>><mailto:yjhuang at whiteboxtechnologies.com>yjhuang at whiteboxtechnologies.com
>>http://weather.whiteboxtechnologies.com for simulation-ready weather data
>>(o) (925)388-0265
>>(c) (510)928-2683
>>"building energy simulations at your fingertips"
>>On 1/2/2018 9:30 AM, Nicholas Caton wrote:
>>
>>Hi Joe,
>>
>>Â
>>
>> From your perspective, are NREL or any other 
>> government/professional bodies making 
>> moves/indications to update/refresh the 
>> current TMY3 sets to utilize satellite-derived 
>> solar radiation?  Seems like a no-brainer for 
>> our industry, but is there a 
>> counter-argument?  It seems likely, but has 
>> there been rigorous comparisons of 
>> satellite-derived solar radiation against 
>> measured values and/or our “present-day” 
>> solar models used to derive solar radiation 
>> information for building energy simulation?
>>
>>Â
>>
>>Also, I’m trying to understand and correctly 
>>characterize the impact of this development in 
>>simple terms my brain can follow.  Is it fair to say:
>>
>>Â
>>
>>The solar models used in developing weather 
>>files for building energy simulations to-date 
>>in our industry (including all/most 
>>industry-standard TMY weather sets), because 
>>they have been using solar radiation derived 
>>from (evolving) solar models, have not 
>>accounted for the likes of local climate cloud 
>>cover / smog / dust?  Seattle (~47°N) has 
>>perhaps been seeing as much sunlight through the winter as Paris (~48°N)?
>>
>>Â
>>
>>Does satellite-derived solar radiation address 
>>some or all of these local climate issues 
>>(cloud cover, smog, dust) affecting direct/indirect solar radiation?
>>
>>Â
>>
>>Thanks sincerely for all your teaching Joe,
>>
>>Â
>>
>>~Nick
>>
>>Â
>>
>>[]
>>
>>
>>Nick Caton, P.E., BEMP
>>
>>Â  Senior Energy Engineer
>>Â  Regional Energy Engineering Manager
>>
>>Â  Energy and Sustainability Services
>>Â  Schneider Electric
>>
>>DÂ Â 913.564.6361
>>MÂ Â 785.410.3317
>>FÂ Â 913.564.6380
>>EÂ Â 
>><mailto:nicholas.caton at schneider-electric.com>nicholas.caton at schneider-electric.com
>>
>>15200 Santa Fe Trail Drive
>>Suite 204
>>Lenexa, KS 66219
>>United States
>>
>>[]
>>
>>
>>Â
>>
>>Â
>>
>>From: Equest-users 
>>[<mailto:equest-users-bounces at lists.onebuilding.org>mailto:equest-users-bounces at lists.onebuilding.org] 
>>On Behalf Of Joe Huang via Equest-users
>>Sent: Thursday, December 14, 2017 8:13 PM
>>To: BLDG-SIM 
>><mailto:bldg-sim at lists.onebuilding.org><bldg-sim at lists.onebuilding.org>; 
>>EnergyPlus_Support 
>><mailto:EnergyPlus_Support at yahoogroups.com><EnergyPlus_Support at yahoogroups.com>; 
>><mailto:equest-users at lists.onebuilding.org>equest-users at lists.onebuilding.org
>>Subject: [Equest-users] White Box Technologies 
>>brings simulation weather data to the satellite age
>>
>>Â
>>
>>It is with joy and some trepidation to report 
>>that White Box Technologies (WBT) is updating 
>>all its historical weather files with 
>>satellite-derived solar radiation. Joy because 
>>this overcomes what has been the most 
>>significant question mark with weather files; 
>>trepidation because of the amount of work 
>>needed to carry out and maintain this effort. 
>>To show that this is more than marketing hype, 
>>I need to give a rather long explanation about this development.
>>
>>The bane of weather data over the past three 
>>decades has been the solar radiation (global 
>>horizontal and direct normal) which are not 
>>measured parameters, but derived using various 
>>solar and sky models. All the familiar "typical 
>>year" sets, i.e., TMY, WYEC, IWEC, etc., let 
>>alone the historical weather files, have 
>>modeled solar radiation. Although a lot of
>>work has gone into such models (see M. 
>>Iqbal,"An Introduction to Solar Radiation", 
>>Academic Press, 1983), there remain an almost 
>>intractible problem of the lack of good 
>>measured solar to tune any of these models. For 
>>example, in the ASHRAE IWEC2 weather files, my 
>>team was able to find one or two years' 
>>measured data for less than 50 locations,
>>from which were derived 28 sets of regression 
>>coefficients then used for all 3,012 IWEC2 locations.
>>
>>For the past decade and a half, researchers 
>>around the world have been working to derive 
>>solar radiation from weather satellite imagery, 
>>driven largely by the needs of the solar power 
>>industry for the siting of solar power plants 
>>and getting "bankable" solar estimates for 
>>their arrays. Our little building energy 
>>simulation sector can of course benefit by 
>>hanging on the coattails of the solar power 
>>industry, but the downside has been to be 
>>totally priced out, since the commercial cost 
>>for one year's solar data for one location 
>>(grid cell) typically runs around $1,000.
>>
>>A welcome development over the last five years 
>>is that various government offices or 
>>affiliated consortia are now beginning to also 
>>providing access to satellite-derived solar 
>>radiation at minimal or more acceptable costs 
>>under various conditions. Over the past three 
>>years, WBT has obtained access to such data and 
>>permission for its use in WBT weather files.
>>WBT is now either replacing the solar radiation 
>>on its historical weather files, or using 
>>satellite-derived radiation to develop custom 
>>solar coefficients for each location to extend 
>>the satellite-derived solar to time periods 
>>outside the available time window. With the 
>>exception of polar locations above or below 
>>60/66 degrees, island nations in the Pacific 
>>and Indian Ocean, and a few unfortunate "blind 
>>spots", the entire land mass is being covered 
>>with at least 10 years up to 18 years of hourly solar records.
>>
>>Starting in 2018, WBT historical weather files 
>>in the following areas will all have 
>>satellite-derived solar radiation for the 
>>following time periods: Europe, Africa, South 
>>America east of 66 West, i.e., Brazil and 
>>Uruguay (2004 to date), Australia (1999 to 
>>date), and East Asia (2007 to date, access 
>>pending). WBT historical weather files in the 
>>following areas will have satellite-derived 
>>solar radiation for the indicated time periods 
>>- North America and Central/South American down 
>>to 20 South (1998-2015), South Asia 
>>(2000-2014), with modeled solar radiation from 
>>2016 on that has been individually tuned to the past satellite-derived solar.
>>
>>Another benefit to the satellite-derived solar 
>>is to increases the number of available weather 
>>stations, which in many places has been limited 
>>by the lack of cloud cover data needed to model 
>>the solar radiation.  For reasons that are not 
>>immediately identifiable, several 
>>English-speaking Commonwealth countries has 
>>seen a marked drop in the number of available 
>>stations due to the decreases in the reporting 
>>of cloud cover (see plot, ZAF = South Africa). 
>>For example, the number of stations in the UK 
>>has dropped by almost 2/3s between 2001 and 
>>2017 (174 to 64), but with satellite-derived 
>>solar, it will go back up to over 180, while in 
>>Australia and South Africa the comparable 
>>numbers are from 175 to well over 500, and from 37 to over 100, respectively.
>>[]
>>
>>If interested, customers who have purchased a 
>>historical weather files from WBT over the past 
>>five years can get an updated weather file at 
>>no cost. Lastly, although it will take at least 
>>a month to update all 10,000 2017 files, it's 
>>very quick to do for any specific location or 
>>even 50 or so locations. Therefore, if you have 
>>an urgent request please e-mail me and I will 
>>put that at the beginning of the queue for that day.
>>
>>--
>>Joe Huang
>>White Box Technologies, Inc.
>>346 Rheem Blvd., Suite 205A
>>Moraga CA 94556
>><mailto:yjhuang at whiteboxtechnologies.com>yjhuang at whiteboxtechnologies.com
>>http://weather.whiteboxtechnologies.com for simulation-ready weather data
>>(o) (925)388-0265
>>(c) (510)928-2683
>>"building energy simulations at your fingertips"
>>Â
>>
>>
>>----------
>>
>>
>>NOTICE: This communication and any attachments 
>>("this message") may contain information which 
>>is privileged, confidential, proprietary or 
>>otherwise subject to restricted disclosure 
>>under applicable law. This message is for the 
>>sole use of the intended recipient(s). Any 
>>unauthorized use, disclosure, viewing, copying, 
>>alteration, dissemination or distribution of, 
>>or reliance on, this message is strictly 
>>prohibited. If you have received this message 
>>in error, or you are not an authorized or 
>>intended recipient, please notify the sender 
>>immediately by replying to this message, delete 
>>this message and all copies from your e-mail 
>>system and destroy any printed copies. You are 
>>receiving this communication because you are 
>>listed as a current WSP contact. Should you 
>>have any questions regarding WSP's electronic 
>>communications policy, please consult our 
>>Anti-Spam Commitment at 
>><http://www.wsp.com/casl>www.wsp.com/casl. For 
>>any concern or if you believe you should not be 
>>receiving this message, please forward this 
>>message to 
>><mailto:caslcompliance at wsp.com>caslcompliance at wsp.com 
>>so that we can promptly address your request. 
>>Note that not all messages sent by WSP qualify 
>>as commercial electronic messages.
>>
>>AVIS : Ce message, incluant tout fichier 
>>l'accompagnant (« le message »), peut 
>>contenir des renseignements ou de l'information 
>>privilégiés, confidentiels, propriétaires ou 
>>Ã  divulgation restreinte en vertu de la loi. 
>>Ce message est destiné à l'usage exclusif 
>>du/des destinataire(s) voulu(s). Toute 
>>utilisation non permise, divulgation, lecture, 
>>reproduction, modification, diffusion ou 
>>distribution est interdite. Si vous avez reçu 
>>ce message par erreur, ou que vous n'êtes pas 
>>un destinataire autorisé ou voulu, veuillez en 
>>aviser l'expéditeur immédiatement et 
>>détruire le message et toute copie 
>>électronique ou imprimée. Vous recevez cette 
>>communication car vous faites partie des 
>>contacts de WSP. Si vous avez des questions 
>>concernant la politique de communications 
>>électroniques de WSP, veuillez consulter notre 
>>Engagement anti-pourriel au 
>><http://www.wsp.com/lcap>www.wsp.com/lcap. Pour 
>>toute question ou si vous croyez que vous ne 
>>devriez pas recevoir ce message, prière de le 
>>transférer au 
>><mailto:conformitelcap at wsp.com>conformitelcap at wsp.com 
>>afin que nous puissions rapidement traiter 
>>votre demande. Notez que ce ne sont pas tous 
>>les messages transmis par WSP qui constituent 
>>des messages electroniques commerciaux.
>>
>>
>>
>>-LAEmHhHzdJzBlTWfa4Hgs7pbKl
>>__._,_.___
>>
>>----------
>>Posted by: "Jones, Christopher" 
>><mailto:Christopher.r.Jones at wsp.com><Christopher.r.Jones at wsp.com>
>>
>>----------
>><https://groups.yahoo.com/neo/groups/EnergyPlus_Support/conversations/messages/37879;_ylc=X3oDMTJxajJicWVxBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzM3ODc5BHNlYwNmdHIEc2xrA3JwbHkEc3RpbWUDMTUxNTQ0MjU2MQ--?act=reply&messageNum=37879>Reply 
>>via web post • 
>><mailto:Christopher.r.Jones at wsp.com?subject=RE%3A%20%5BEquest-users%5D%20White%20Box%20Technologies%20brings%20simulation%20weather%20data%20to%20the%20satellite%20age>Reply 
>>to sender • 
>><mailto:EnergyPlus_Support at yahoogroups.com?subject=RE%3A%20%5BEquest-users%5D%20White%20Box%20Technologies%20brings%20simulation%20weather%20data%20to%20the%20satellite%20age>Reply 
>>to group • 
>><https://groups.yahoo.com/neo/groups/EnergyPlus_Support/conversations/newtopic;_ylc=X3oDMTJlMWdkbGppBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA250cGMEc3RpbWUDMTUxNTQ0MjU2MQ-->Start 
>>a New Topic • 
>><https://groups.yahoo.com/neo/groups/EnergyPlus_Support/conversations/topics/37869;_ylc=X3oDMTM2bjlnNGs2BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzM3ODc5BHNlYwNmdHIEc2xrA3Z0cGMEc3RpbWUDMTUxNTQ0MjU2MQR0cGNJZAMzNzg2OQ-->Messages 
>>in this topic (4)
>>
>>----------
>>Check out the automatic photo album with 
>><https://groups.yahoo.com/neo/groups/EnergyPlus_Support/photos/photomatic/788930472;_ylc=X3oDMTE4M3R1OW82BF9TAzk3MzU5NzE0BGNmOQNQSE9UT01BVElDBHNlYwNtZWdhcGhvbmU->2 
>>photo(s) from this topic.
>><https://groups.yahoo.com/neo/groups/EnergyPlus_Support/photos/photomatic/788930472;_ylc=X3oDMTE4M3R1OW82BF9TAzk3MzU5NzE0BGNmOQNQSE9UT01BVElDBHNlYwNtZWdhcGhvbmU->
>>image003.png
>>
>>image003.png
>><https://groups.yahoo.com/neo/groups/EnergyPlus_Support/photos/photomatic/788930472;_ylc=X3oDMTE4M3R1OW82BF9TAzk3MzU5NzE0BGNmOQNQSE9UT01BVElDBHNlYwNtZWdhcGhvbmU-> 
>>
>>
>>----------
>>[]
>>
>>Have you tried the highest rated email app?
>>With 4.5 stars in iTunes, the Yahoo Mail app is 
>>the highest rated email app on the market. What 
>>are you waiting for? Now you can access all 
>>your inboxes (Gmail, Outlook, AOL and more) in 
>>one place. Never delete an email again with 1000GB of free cloud storage.
>>
>>----------
>>EnergyPlus support is found at:
>><http://energyplus.helpserve.com>http://energyplus.helpserve.com 
>>or send a message to 
>><mailto:energyplus-support at gard.com>energyplus-support at gard.com
>>
>>The EnergyPlus web site is found at:
>><http://www.energyplus.net/>http://www.energyplus.net/
>>
>>The group web site is:
>><http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>>Attachments are currently allowed but be 
>>mindful that not everyone has a high speed 
>>connection.  Limit attachments to small files.
>>
>>EnergyPlus Documentation is searchable.  Open 
>>EPlusMainMenu.pdf under the Documentation link 
>>and press the "search" button.
>><https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlbmFlcm9tBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTUxNTQ0MjU2MQ-->Visit 
>>Your Group
>>    * 
>> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmZjN2YmRvBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE1MTU0NDI1NjE->New 
>> Members 1
>><https://groups.yahoo.com/neo;_ylc=X3oDMTJkYzZoN2MxBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNTE1NDQyNTYx>
>>Yahoo! Groups
>>
>>• 
>><https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy 
>>• 
>><mailto:EnergyPlus_Support-unsubscribe at yahoogroups.com?subject=Unsubscribe>Unsubscribe 
>>• <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
>>
>>.
>>
>>__,_._,___
>
>
>
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send  a 
>blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180109/d51893e6/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 308766a.png
Type: image/png
Size: 25844 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180109/d51893e6/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 3087689.png
Type: image/png
Size: 255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180109/d51893e6/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 3087698.png
Type: image/png
Size: 8477 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180109/d51893e6/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 30876a8.png
Type: image/png
Size: 12088 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180109/d51893e6/attachment-0003.png>


More information about the Bldg-sim mailing list