Salma,

  There are (as usual) a number of different ways of having all the 
results from a parametric run put into the same output file. One way is 
to use a Type25 printer as an output device in your simulation and to 
set it to "append" mode instead of "overwrite mode." The mode is 
controlled by a parameter.  The other thing you'll need to do is to make 
sure that the name of the output file is NOT the same as the name of 
your input file, otherwise there will be one output file produced per 
table run. Note that a number of the standard printer output components 
in TRNSYS allow the switch between append and overwrite mode.

kind regards,

  David


On 12/08/2019 07:33, SALMA LAHMAR via TRNSYS-users wrote:
> I have to run a lot of simulations to calculate the building energy 
> consumption depending on the value of different parameters.
> I tried to use trnedit to make a table but I don't know how to have a 
> result of all simulation in one output file like 
> : \Examples\Parametric Runs\SDHW-ParametricRuns in trnsys.
> thanks in advance
> ᐧ
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191210/6a728493/attachment.htm>


More information about the TRNSYS-users mailing list