Salma,

   If your building is physically attached to neighboring buildings then 
you'd want to define those adjoining walls as BOUNDARY walls. In 
TRNBuild, you can then specify what the boundary condition on the other 
side of those adjoining walls is. Your options are to assume that the 
temperature on the other side of those walls is identical to the 
temperature in your building, or you can assume a constant or a 
scheduled temperature profile.

kind regards,

  David