[BLDG-SIM] DOE-2 Modelling Capabilities
Fred Winkelmann
fcw at pegasus.lbl.gov
Wed Jul 28 09:22:32 PDT 1999
Steve:
The answers follow.
Fred Winkelmann
>Hi All,
>I'm interested in DOE-2's modelling capabilities. Can the 2.1E engine
>handle
> a. Walls that lean in or out (non-vertical)? YES
> b. Curved walls? NOT DIRECTLY; CURVED WALLS HAVE TO BE DECOMPOSED INTO A
SET OF RECTANGULAR WALLS WHOSE AZIMUTHS AND TILTS FOLLOW THE CURVE
OF THE ORIGINAL WALL. THE TOTAL AREA OF THESE RECTANGLES
SHOULD ADD UP TO THE SAME AREA AS THE ORIGINAL CURVED WALL.
> c. Windows that lean in or out (non-vertical) with fixed shading
devices? YES