I use DOE-2.1E. The system is a PTAC one. The above temperatures are in
degrees C.
Design-cool-t = 25; Zone temperature = 25; Cool-temp-sch gives also 25
C.
Min-supply-t = 13.
OA-FLOW/PER = 10 (SI units)
Fans are scheduled to operate between 7 and 17.
The SS-F report signales that all hours are undercooled.
Hourly reports with Variable-type = U-name of zone AND Variable-list =
(6,16,17,18) indicate the following :
MMDDHH ZONE-8 ZONE-8 ZONE-8 ZONE-8
ZONE LOAD NOT HTG SET CLG SET
TEMP MET POINT POINT
C WATT C C
----( 6) ----(16) ----(17) ----(18)
822 1 34.0 0. -572.8 537.2
822 2 33.9 0. -572.8 537.2
822 3 33.6 0. -572.8 537.2
822 4 33.7 0. -572.8 537.2
822 5 33.5 0. -572.8 537.2
822 6 33.3 0. -572.8 537.2
822 7 33.3 0. -572.8 537.2
822 8 27.3 45404. -572.8 -3.9
822 9 28.5 46529. -572.8 -3.9
82210 27.7 45912. -572.8 -3.9
82211 27.8 45905. -572.8 -3.9
82212 28.4 47505. -572.8 -3.9
82213 27.9 47529. -572.8 -3.9
82214 27.8 46522. -572.8 -3.9
82215 27.7 46117. -572.8 -3.9
82216 27.7 46066. -572.8 -3.9
82217 27.6 45730. -572.8 -3.9
82218 33.8 0. -572.8 537.2
82219 34.1 0. -572.8 537.2
82220 33.6 0. -572.8 537.2
82221 33.4 0. -572.8 537.2
82222 33.5 0. -572.8 537.2
82223 33.6 0. -572.8 537.2
82224 33.7 0. -572.8 537.2
WHAT DOES THAT MEAN ?
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
A non-text attachment was scrubbed...
Name: demba.ndiaye.vcf
Type: text/x-vcard
Size: 632 bytes
Desc: Card for Demba NDIAYE
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20010227/f1555bc6/attachment.vcf>
More information about the Bldg-sim
mailing list