[Bldg-sim] Apartment/hotel DOE-2.1E systems.
Varkie Thomas
Varkie.Thomas at som.com
Wed Aug 28 06:41:40 PDT 2002
Thanks for your helpful response..
At the moment we analyze buildings during the schematic phase of the
project to compare envelope, systems & plant alternatives. So we don't
go into the details that you describe but we might have to in the future
to show compliance with energy conservation codes before submitting
construction documents. We model hotels the way architects design it
during the schematic phase with modifications to eliminate the details
but keeping the design intent intact. This means the different space
types (meeting rooms, gymnasiums, indoor swimming pools, laudry,
restaurants, lobbies, etc.) and area configurations requiring different
design criteria and systems requirements are maintained. There is no
problem using DOE2.1E for hotels since the rooms are served by FCUs or
induction units with heating and cooling coils. In the case of FCUs the
outdoor air is supplied to the corridor and transferred to the room.
There is only one exhaust system in a hotel for the bathroom which can
be modelled in DOE2.1E. So DOE2.1E can handle hotels. In the case of
high rise apartment buildings there can be 3 exhaust systems (bathroom,
kitchen & dryer) with different air quantities and operating schedules.
At the moment we have to treat the exhaust systems as one system and use
the weighted average values of the operating profile fractions.
We also have a solution for dealing with the other issues that I raised.
They were (1) varying the outdoor air based on occupancy (using CO2
sensors) independently of the supply air in a VAV system and (2)
under-floor air distribution versus ceiling air distribution. I was
interested in finding out how others handled these situations. DOE2.1E
also does not allow duplicate systems using the LIKE/EXCEPT keywords.
This is awkward when dealing with floor by floor airhanding units in a
high-rise buildings with two or more units per floor and served by one
or more separate outdoor air handling units
Thanks again for your response.
Varkie
-----Original Message-----
From: Aulbach, John [mailto:JAulbach at semprasolutions.com]
Sent: Tuesday, August 27, 2002 3:15 PM
To: Bldg-sim at gard.com
Subject: [Bldg-sim] Apartment/hotel DOE-2.1E systems.
Always glad to help a fellow Chicagoan. Even though I now live in
California.
Back in the days I did energy modeling for Hilton Hotels, I would always
divide the hotel Guest Tower up into several levels of occupancy. Since
only one side of a typical hotel room faces the external
(solar/transmission) and hotels rooms usually have drapes closed, I
didn't worry too much about outdoor fenestration or transmission
conditions versus the effect of internal load and, of course, outside
air on the room.
I then divided the hotel guest rooms up into three or four (as many as
six) occupied levels, as hotel occupancies are roller coasters of
conventions, holiday periods, and every else in between. I made a group
of guest rooms fully occupied, and a group partially occupied, and a
third group lightly occupied (assuming a three way division).
I then chose the FOUR PIPE INDUCTION system for my HVAC. This system
allows for Primary AND Secondary heating and cooling coils. The Primary
coils would temper the outside airflow, and the secondary would attack
the combination of the primary tempered and the induced room air. The
Induction ratio became the ratio of all fan coil airflow (say 500 guest
room x 200 CFM/fan coil) to the total outside air.
This is direct ventilation of the guest rooms and/or the corridor are
pulled into the guest room and further treated by the fan coils. And
exhaust air is permitted in this SYSTEM-TYPE.
High rise apartment living areas can be handled in the same way.
I thank Bruce Birdsall, one of the original DOE-2 developers at Lawrence
Berkeley Labs for teaching me this trick.
John R. Aulbach, PE, CEM
Project Engineer
Sempra Energy Solutions
555 West Fifth Street
Mail Location 27F3
Los Angeles, CA 90013
Tel: (213) 244-8551 Beeper (888) 520-1051
"Sempra Energy Solutions is not the same company as SDG&E/ SoCalGas, the
Utilities. Sempra Energy Solutions is not regulated by the California
Public Utilities Commission, and you do not have to buy Sempra Energy
Solutions products or services to continue to receive quality regulated
service from the Utilities."
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20020828/ea63c5ad/attachment-0002.htm>
More information about the Bldg-sim
mailing list