[BLDG-SIM] Moisture flux in internal walls
    habaza11 at cs.com 
    habaza11 at cs.com
       
    Mon Feb  4 06:29:16 PST 2002
    
    
  
Sirs;
When an internal wall is shared between two zones. I assume that the external layer of this wall will be the internal layer of the same wall in the other zone that shares the same wall, and visa versa.
Thus the moisture flux of the external surface of this wall should be equal to the moisture flux of the internal surface of the same wall from the other zone. If this assumption is correct, why the moisture flux of the internal surface of this wall does not equal the moisture flux of the external surface of the same wall from the other side in E-plus.
Attached please find the input file for more details.
Second; when moisture flux is negative does this mean absorption or desorption?.
Thank you.
======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
!-Generator IDFEditor 1.02
!-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically.
!-      Use '!' comments if they need to be retained when using the IDFEditor.
!-   ===========  ALL OBJECTS IN CLASS: RUNPERIOD ===========
RunPeriod,
    1,                       !- Begin Month
    1,                       !- Begin Day Of Month
    12,                      !- End Month
    30;                      !- End Day Of Month
!-   ===========  ALL OBJECTS IN CLASS: GROUNDTEMPERATURES ===========
GROUNDTEMPERATURES,
    12.2222233,              !- Jan {C}
    12.7777786,              !- Feb {C}
    14.4444447,              !- Mar {C}
    16.6666679,              !- Apr {C}
    19.4444447,              !- May {C}
    23.333334,               !- Jun {C}
    22.2222233,              !- Jul {C}
    20,                      !- Aug {C}
    17.7777786,              !- Sep {C}
    16.6666679,              !- Oct {C}
    14.4444447,              !- Nov {C}
    12.7777786;              !- Dec {C}
!-   ===========  ALL OBJECTS IN CLASS: BUILDING ===========
BUILDING,
!                                                                                                                                                            Building Name
    Beliveau House,          !- Building Name
!                                                                                                                                                            Building Azimuth
    0,                       !- North Axis {deg}
!                                                                                                                                                            Building Terrain
    Suburbs,                 !- Terrain
!                                                                                                                                                            Loads Convergence Tolerance
    0.039999999,             !- Loads Convergence Tolerance Value
!                                                                                                                                                            Temperature Convergence Tolerance
    0.4,                     !- Temperature Convergence Tolerance Value
!                                                                                                                                                            Solar Distribution
    FullInteriorAndExterior; !- Solar Distribution
!-   ===========  ALL OBJECTS IN CLASS: TIMESTEP IN HOUR ===========
TIMESTEP IN HOUR,
    6;                       !- Time Step in Hour
!-   ===========  ALL OBJECTS IN CLASS: INSIDE CONVECTION ALGORITHM ===========
INSIDE CONVECTION ALGORITHM,
!                                                                                                                                                            Inside Convection Algorithm
    Detailed;                !- InsideConvectionValue
!-   ===========  ALL OBJECTS IN CLASS: OUTSIDE CONVECTION ALGORITHM ===========
OUTSIDE CONVECTION ALGORITHM,
!                                                                                                                                                            Outside Convection Algorithm
    Detailed;                !- OutsideConvectionValue
!-   ===========  ALL OBJECTS IN CLASS: SKY RADIANCE DISTRIBUTION ===========
SKY RADIANCE DISTRIBUTION,
    1;                       !- SkyRadianceValue
!-   ===========  ALL OBJECTS IN CLASS: SOLUTION ALGORITHM ===========
SOLUTION ALGORITHM,
!                                                                                                                                                            Solution Algorithm
    MTF;                     !- SolutionAlgo
!-   ===========  ALL OBJECTS IN CLASS: DEBUG OUTPUT ===========
DEBUG OUTPUT,
    0;                       !- YesNo
!-   ===========  ALL OBJECTS IN CLASS: ZONE VOLUME CAPACITANCE MULTIPLIER ===========
ZONE VOLUME CAPACITANCE MULTIPLIER,
    1;                       !- Capacitance Multiplier
!-   ===========  ALL OBJECTS IN CLASS: MATERIAL:REGULAR ===========
MATERIAL:REGULAR,
    A1 - 1 IN STUCCO,        !- Name
    Smooth,                  !- Roughness
    0.025389841,             !- Thickness {m}
    0.6918309,               !- Conductivity {W/m-K}
    1858.142,                !- Density {kg/m3}
    836.8,                   !- Specific Heat {J/kg-K}
    0.9,                     !- Absorptance:Thermal
    0.92,                    !- Absorptance:Solar
    0.92;                    !- Absorptance:Visible
MATERIAL:REGULAR,
    C4 - 4 IN COMMON BRICK,  !- Name
    Rough,                   !- Roughness
    0.1014984,               !- Thickness {m}
    0.7264224,               !- Conductivity {W/m-K}
    1922.216,                !- Density {kg/m3}
    836.8,                   !- Specific Heat {J/kg-K}
    0.9,                     !- Absorptance:Thermal
    0.76,                    !- Absorptance:Solar
    0.76;                    !- Absorptance:Visible
MATERIAL:REGULAR,
    E1 - 3 / 4 IN PLASTER OR GYP BOARD,
                             !- Name
    Smooth,                  !- Roughness
    0.01905,                 !- Thickness {m}
    0.7264224,               !- Conductivity {W/m-K}
    1601.846,                !- Density {kg/m3}
    836.8,                   !- Specific Heat {J/kg-K}
    0.9,                     !- Absorptance:Thermal
    0.92,                    !- Absorptance:Solar
    0.92;                    !- Absorptance:Visible
MATERIAL:REGULAR,
    8 IN Concrete Block,     !- Name
    Smooth,                  !- Roughness
    0.2033016,               !- Thickness {m}
    1.113,                   !- Conductivity {W/m-K}
    849,                     !- Density {kg/m3}
    921.1,                   !- Specific Heat {J/kg-K}
    0.9,                     !- Absorptance:Thermal
    0.82,                    !- Absorptance:Solar
    0.82;                    !- Absorptance:Visible
MATERIAL:REGULAR,
    DIRT 12 IN,              !- Name
    Rough,                   !- Roughness
    0.3048,                  !- Thickness {m}
    0.1729577,               !- Conductivity {W/m-K}
    1041.2,                  !- Density {kg/m3}
    836.8,                   !- Specific Heat {J/kg-K}
    0.9,                     !- Absorptance:Thermal
    0.7,                     !- Absorptance:Solar
    0.7;                     !- Absorptance:Visible
MATERIAL:REGULAR,
    C10 - 8 IN HW CONCRETE,  !- Name
    MediumRough,             !- Roughness
    0.2033016,               !- Thickness {m}
    1.729577,                !- Conductivity {W/m-K}
    2242.585,                !- Density {kg/m3}
    836.8,                   !- Specific Heat {J/kg-K}
    0.9,                     !- Absorptance:Thermal
    0.65,                    !- Absorptance:Solar
    0.65;                    !- Absorptance:Visible
MATERIAL:REGULAR,
    E2 - 1 / 2 IN SLAG OR STONE,
                             !- Name
    Rough,                   !- Roughness
    0.012710161,             !- Thickness {m}
    1.435549,                !- Conductivity {W/m-K}
    881.0155,                !- Density {kg/m3}
    1673.6,                  !- Specific Heat {J/kg-K}
    0.9,                     !- Absorptance:Thermal
    0.55,                    !- Absorptance:Solar
    0.55;                    !- Absorptance:Visible
MATERIAL:REGULAR,
    E3 - 3 / 8 IN FELT AND MEMBRANE,
                             !- Name
    Rough,                   !- Roughness
    0.0095402403,            !- Thickness {m}
    0.1902535,               !- Conductivity {W/m-K}
    1121.292,                !- Density {kg/m3}
    1673.6,                  !- Specific Heat {J/kg-K}
    0.9,                     !- Absorptance:Thermal
    0.75,                    !- Absorptance:Solar
    0.75;                    !- Absorptance:Visible
MATERIAL:REGULAR,
    B5 - 1 IN DENSE INSULATION,
                             !- Name
    VeryRough,               !- Roughness
    0.025389841,             !- Thickness {m}
    0.04323943,              !- Conductivity {W/m-K}
    91.30524,                !- Density {kg/m3}
    836.8,                   !- Specific Heat {J/kg-K}
    0.9,                     !- Absorptance:Thermal
    0.5,                     !- Absorptance:Solar
    0.5;                     !- Absorptance:Visible
MATERIAL:REGULAR,
    C12 - 2 IN HW CONCRETE,  !- Name
    MediumRough,             !- Roughness
    0.050901599,             !- Thickness {m}
    1.729577,                !- Conductivity {W/m-K}
    2242.585,                !- Density {kg/m3}
    836.8,                   !- Specific Heat {J/kg-K}
    0.9,                     !- Absorptance:Thermal
    0.65,                    !- Absorptance:Solar
    0.65;                    !- Absorptance:Visible
!-   ===========  ALL OBJECTS IN CLASS: MATERIAL:WINDOWGLASS ===========
MATERIAL:WINDOWGLASS,
!                                                                                                                                                                  Material name
    WIN-LAY-GLASS-LIGHT,     !- Name
!                                                                                                                                                                  Optical data type {SpectralAverage or Spectral}
    SpectralAverage,         !- Optical Data Type
!                                                                                                                                                                  Name of spectral data set when Optical Data Type = Spectral
    ,                        !- Name of Window Glass Spectral Data Set
!                                                                                                                                                                  Thickness {m}
    0.003,                   !- Thickness {m}
!                                                                                                                                                                  Solar transmittance at normal incidence
    0.9,                     !- Solar Transmittance at Normal Incidence
!                                                                                                                                                                  Solar reflectance at normal incidence: front side
    0.031,                   !- Solar Reflectance at Normal Incidence: Front Side
!                                                                                                                                                                  Solar reflectance at normal incidence: back side
    0.031,                   !- Solar Reflectance at Normal Incidence: Back Side
!                                                                                                                                                                  Visible transmittance at normal incidence
    0.9,                     !- Visible Transmittance at Normal Incidence
!                                                                                                                                                                  Visible reflectance at normal incidence: front side
    0.05,                    !- Visible Reflectance at Normal Incidence: Front Side
!                                                                                                                                                                  Visible reflectance at normal incidence: back side
    0.05,                    !- Visible Reflectance at Normal Incidence: Back Side
!                                                                                                                                                                  IR transmittance at normal incidence
    0,                       !- IR Transmittance at Normal Incidence
!                                                                                                                                                                  IR emissivity: front side
    0.84,                    !- IR Hemispherical Emissivity: Front Side
!                                                                                                                                                                  IR emissivity: back side
    0.84,                    !- IR Hemispherical Emissivity: Back Side
!                                                                                                                                                                  Conductivity {W/m-K}
    0.9;                     !- Conductivity {W/m-K}
MATERIAL:WINDOWGLASS,
    WIN-dark glass,          !- Name
    SpectralAverage,         !- Optical Data Type
    ,                        !- Name of Window Glass Spectral Data Set
    0.006,                   !- Thickness {m}
    0.6,                     !- Solar Transmittance at Normal Incidence
    0.1,                     !- Solar Reflectance at Normal Incidence: Front Side
    0.1,                     !- Solar Reflectance at Normal Incidence: Back Side
    0.6,                     !- Visible Transmittance at Normal Incidence
    0.1,                     !- Visible Reflectance at Normal Incidence: Front Side
    0.1,                     !- Visible Reflectance at Normal Incidence: Back Side
    0,                       !- IR Transmittance at Normal Incidence
    0.3,                     !- IR Hemispherical Emissivity: Front Side
    0.6,                     !- IR Hemispherical Emissivity: Back Side
    0.9;                     !- Conductivity {W/m-K}
!-   ===========  ALL OBJECTS IN CLASS: MATERIAL:WINDOWGAS ===========
MATERIAL:WINDOWGAS,
    gaz layer,               !- Name
    Air,                     !- Gas Type
    0.02,                    !- Thickness {m}
    1,                       !- Density {kg/m3}
    0.1,                     !- Density Temperature Derivative {kg/m3-K}
    1,                       !- Conductivity {W/m-K}
    1,                       !- Conductivity Temperature Derivative {W/m-K2}
    1,                       !- Viscosity {kg/m-s}
    1,                       !- Viscosity Temperature Derivative {kg/m-s-K}
    1,                       !- Prandtl Number
    0;                       !- Prandtl Number Temperature Derivative {1/K}
!-   ===========  ALL OBJECTS IN CLASS: MATERIAL:WINDOWSHADE ===========
MATERIAL:WINDOWSHADE,
    winshadematerial,        !- Name
    0.05,                    !- Solar transmittance
    0.3,                     !- Solar Reflectance
    0.05,                    !- Visible transmittance
    0.3,                     !- Visible reflectance
    0.9,                     !- Thermal hemispherical emissivity
    0.05,                    !- Thermal transmittance
    0.001,                   !- Thickness {m}
    1;                       !- Conductivity {W/m-K}
!-   ===========  ALL OBJECTS IN CLASS: MATERIALPROPERTY:MOISTURE:MTF ===========
MATERIALPROPERTY:MOISTURE:MTF,
    A1 - 1 IN STUCCO,        !- Name
    0.00000100766,           !- Vapor Diffusivity {m2/s}
    0.5,                     !- Porosity {m3/m3}
    0.0004655,               !- Thermal-Gradient Coeff for Moisture Capacity {kg/kg-K}
    0.41951504;              !- Isothermal moisture capacity {m3/kg}
MATERIALPROPERTY:MOISTURE:MTF,
    C4 - 4 IN COMMON BRICK,  !- Name
    0.00000487362,           !- Vapor Diffusivity {m2/s}
    0.5,                     !- Porosity {m3/m3}
    0.00013022,              !- Thermal-Gradient Coeff for Moisture Capacity {kg/kg-K}
    0.13165985;              !- Isothermal moisture capacity {m3/kg}
MATERIALPROPERTY:MOISTURE:MTF,
    E1 - 3 / 4 IN PLASTER OR GYP BOARD,
                             !- Name
    0.00000526351,           !- Vapor Diffusivity {m2/s}
    0.7,                     !- Porosity {m3/m3}
    0.0008794,               !- Thermal-Gradient Coeff for Moisture Capacity {kg/kg-K}
    1.1602;                  !- Isothermal moisture capacity {m3/kg}
MATERIALPROPERTY:MOISTURE:MTF,
    8 IN Concrete Block,     !- Name
    0.0000056234,            !- Vapor Diffusivity {m2/s}
    0.5,                     !- Porosity {m3/m3}
    0.00057034,              !- Thermal-Gradient Coeff for Moisture Capacity {kg/kg-K}
    0.58603225;              !- Isothermal moisture capacity {m3/kg}
MATERIALPROPERTY:MOISTURE:MTF,
    DIRT 12 IN,              !- Name
    0.000015051,             !- Vapor Diffusivity {m2/s}
    0.8,                     !- Porosity {m3/m3}
    0.00089686,              !- Thermal-Gradient Coeff for Moisture Capacity {kg/kg-K}
    0.94256147;              !- Isothermal moisture capacity {m3/kg}
MATERIALPROPERTY:MOISTURE:MTF,
    C10 - 8 IN HW CONCRETE,  !- Name
    0.00000232898,           !- Vapor Diffusivity {m2/s}
    0.5,                     !- Porosity {m3/m3}
    0.00050548,              !- Thermal-Gradient Coeff for Moisture Capacity {kg/kg-K}
    0.52702561;              !- Isothermal moisture capacity {m3/kg}
MATERIALPROPERTY:MOISTURE:MTF,
    E2 - 1 / 2 IN SLAG OR STONE,
                             !- Name
    0.000010051,             !- Vapor Diffusivity {m2/s}
    0.765,                   !- Porosity {m3/m3}
    0.00064801,              !- Thermal-Gradient Coeff for Moisture Capacity {kg/kg-K}
    0.64827268;              !- Isothermal moisture capacity {m3/kg}
MATERIALPROPERTY:MOISTURE:MTF,
    E3 - 3 / 8 IN FELT AND MEMBRANE,
                             !- Name
    0.000000024419,          !- Vapor Diffusivity {m2/s}
    0,                       !- Porosity {m3/m3}
    0,                       !- Thermal-Gradient Coeff for Moisture Capacity {kg/kg-K}
    0;                       !- Isothermal moisture capacity {m3/kg}
MATERIALPROPERTY:MOISTURE:MTF,
    B5 - 1 IN DENSE INSULATION,
                             !- Name
    0.00000078477,           !- Vapor Diffusivity {m2/s}
    0.9,                     !- Porosity {m3/m3}
    0.0007671,               !- Thermal-Gradient Coeff for Moisture Capacity {kg/kg-K}
    0.84124418;              !- Isothermal moisture capacity {m3/kg}
MATERIALPROPERTY:MOISTURE:MTF,
    C12 - 2 IN HW CONCRETE,  !- Name
    0.00000232898,           !- Vapor Diffusivity {m2/s}
    0.5,                     !- Porosity {m3/m3}
    0.00050548,              !- Thermal-Gradient Coeff for Moisture Capacity {kg/kg-K}
    0.52702561;              !- Isothermal moisture capacity {m3/kg}
!-   ===========  ALL OBJECTS IN CLASS: MATERIALPROPERTY:MOISTURE:EMPD ===========
MATERIALPROPERTY:MOISTURE:EMPD,
    E1 - 3 / 4 IN PLASTER OR GYP BOARD,
                             !- Name
!                EMPD Value
    0.004,                   !- EMPD value {m}
!                Constant to define equilibrium equation {dimensionless}
    0.072549,                !- "a", coefficient to define equilibrium equation {dimensionless}
!                Constant to define equilibrium equation {dimensionless}
    0.397173,                !- "b", coefficient to define equilibrium equation {dimensionless}
!                Constant to define equilibrium equation {dimensionless}
    0.007774,                !- "c", coefficient to define equilibrium equation {dimensionless}
!                Constant to define equilibrium equation {dimensionless}
    11.7057;                 !- "d", coefficient to define equilibrium equation {dimensionless}
MATERIALPROPERTY:MOISTURE:EMPD,
    C10 - 8 IN HW CONCRETE,  !- Name
!                EMPD Value
    0.004,                   !- EMPD value {m}
!                Constant to define equilibrium equation {dimensionless}
    0.018062,                !- "a", coefficient to define equilibrium equation {dimensionless}
!                Constant to define equilibrium equation {dimensionless}
    0.451879,                !- "b", coefficient to define equilibrium equation {dimensionless}
!                Constant to define equilibrium equation {dimensionless}
    0.026178,                !- "c", coefficient to define equilibrium equation {dimensionless}
!                Constant to define equilibrium equation {dimensionless}
    10.8356;                 !- "d", coefficient to define equilibrium equation {dimensionless}
MATERIALPROPERTY:MOISTURE:EMPD,
    C12 - 2 IN HW CONCRETE,  !- Name
!                EMPD Value
    0.004,                   !- EMPD value {m}
!                Constant to define equilibrium equation {dimensionless}
    0.018062,                !- "a", coefficient to define equilibrium equation {dimensionless}
!                Constant to define equilibrium equation {dimensionless}
    0.451879,                !- "b", coefficient to define equilibrium equation {dimensionless}
!                Constant to define equilibrium equation {dimensionless}
    0.026178,                !- "c", coefficient to define equilibrium equation {dimensionless}
!                Constant to define equilibrium equation {dimensionless}
    10.8356;                 !- "d", coefficient to define equilibrium equation {dimensionless}
MATERIALPROPERTY:MOISTURE:EMPD,
    E3 - 3 / 8 IN FELT AND MEMBRANE,
                             !- Name
    0.004,                   !- EMPD value {m}
    0.018062,                !- "a", coefficient to define equilibrium equation {dimensionless}
    0.451879,                !- "b", coefficient to define equilibrium equation {dimensionless}
    0.026178,                !- "c", coefficient to define equilibrium equation {dimensionless}
    10.8356;                 !- "d", coefficient to define equilibrium equation {dimensionless}
MATERIALPROPERTY:MOISTURE:EMPD,
    C4 - 4 IN COMMON BRICK,  !- Name
    0.004,                   !- EMPD value {m}
    0.018062,                !- "a", coefficient to define equilibrium equation {dimensionless}
    0.451879,                !- "b", coefficient to define equilibrium equation {dimensionless}
    0.026178,                !- "c", coefficient to define equilibrium equation {dimensionless}
    10.8356;                 !- "d", coefficient to define equilibrium equation {dimensionless}
!-   ===========  ALL OBJECTS IN CLASS: CONSTRUCTION ===========
CONSTRUCTION,
!                                                                                                                                                                  Material layer names follow:
    EXTWALL80,               !- Name
    A1 - 1 IN STUCCO,        !- Outside Layer
    B5 - 1 IN DENSE INSULATION,
                             !- Layer #2
    E1 - 3 / 4 IN PLASTER OR GYP BOARD,
                             !- Layer #3
    E1 - 3 / 4 IN PLASTER OR GYP BOARD;
                             !- Layer #4
CONSTRUCTION,
!                                                                                                                                                                  Material layer names follow:
    PARTITION06,             !- Name
    E1 - 3 / 4 IN PLASTER OR GYP BOARD,
                             !- Outside Layer
    C4 - 4 IN COMMON BRICK,  !- Layer #2
    E1 - 3 / 4 IN PLASTER OR GYP BOARD;
                             !- Layer #3
CONSTRUCTION,
!                                                                                                                                                                  Material layer names follow:
    FLOOR SLAB 8 IN,         !- Name
    DIRT 12 IN,              !- Outside Layer
    C10 - 8 IN HW CONCRETE;  !- Layer #2
CONSTRUCTION,
!                                                                                                                                                                  Material layer names follow:
    ROOF34,                  !- Name
    E2 - 1 / 2 IN SLAG OR STONE,
                             !- Outside Layer
    E3 - 3 / 8 IN FELT AND MEMBRANE,
                             !- Layer #2
    B5 - 1 IN DENSE INSULATION,
                             !- Layer #3
    E1 - 3 / 4 IN PLASTER OR GYP BOARD;
                             !- Layer #4
CONSTRUCTION,
    WIN-CON-LIGHT,           !- Name
    WIN-dark glass,          !- Outside Layer
    gaz layer,               !- Layer #2
    WIN-dark glass;          !- Layer #3
CONSTRUCTION,
    EXTWALL80-earth,         !- Name
    DIRT 12 IN,              !- Outside Layer
    C4 - 4 IN COMMON BRICK,  !- Layer #2
    E3 - 3 / 8 IN FELT AND MEMBRANE;
                             !- Layer #3
CONSTRUCTION,
    winshadeconst,           !- Name
    winshadematerial,        !- Outside Layer
    WIN-dark glass,          !- Layer #2
    gaz layer,               !- Layer #3
    WIN-dark glass;          !- Layer #4
CONSTRUCTION,
    floor mass,              !- Name
    C4 - 4 IN COMMON BRICK;  !- Outside Layer
!-   ===========  ALL OBJECTS IN CLASS: ZONE ===========
ZONE,
!                                                                                                                                                            Zone Name
    RESISTIVE ZONE,          !- Zone Name
!                                                                                                                                                            Zone North Axis (relative to Building)
    0,                       !- Relative North (to building) {deg}
!                                                                                                                                                            Zone X Origin {m}
    0,                       !- X Origin {m}
!                                                                                                                                                            Zone Y Origin {m}
    0,                       !- Y Origin {m}
!                                                                                                                                                            Zone Z Origin {m}
    0,                       !- Z Origin {m}
!                                                                                                                                                            Zone Type
    1,                       !- Type
!                                                                                                                                                            Zone Multiplier
    1,                       !- Multiplier
!                                                                                                                                                            Zone Ceiling Height {m}
    -100,                    !- Ceiling Height {m}
!                                                                                                                                                            Zone Volume {m**3}
    0;                       !- Volume {m3}
ZONE,
!                                                                                                                                                            Zone Name
    EAST ZONE,               !- Zone Name
!                                                                                                                                                            Zone North Axis (relative to Building)
    0,                       !- Relative North (to building) {deg}
!                                                                                                                                                            Zone X Origin {m}
    6.096,                   !- X Origin {m}
!                                                                                                                                                            Zone Y Origin {m}
    0,                       !- Y Origin {m}
!                                                                                                                                                            Zone Z Origin {m}
    0,                       !- Z Origin {m}
!                                                                                                                                                            Zone Type
    1,                       !- Type
!                                                                                                                                                            Zone Multiplier
    1,                       !- Multiplier
!                                                                                                                                                            Zone Ceiling Height {m}
    -100,                    !- Ceiling Height {m}
!                                                                                                                                                            Zone Volume {m**3}
    0;                       !- Volume {m3}
ZONE,
!                                                                                                                                                            Zone Name
    NORTH ZONE,              !- Zone Name
!                                                                                                                                                            Zone North Axis (relative to Building)
    0,                       !- Relative North (to building) {deg}
!                                                                                                                                                            Zone X Origin {m}
    0,                       !- X Origin {m}
!                                                                                                                                                            Zone Y Origin {m}
    6.096,                   !- Y Origin {m}
!                                                                                                                                                            Zone Z Origin {m}
    0,                       !- Z Origin {m}
!                                                                                                                                                            Zone Type
    1,                       !- Type
!                                                                                                                                                            Zone Multiplier
    1,                       !- Multiplier
!                                                                                                                                                            Zone Ceiling Height {m}
    -100,                    !- Ceiling Height {m}
!                                                                                                                                                            Zone Volume {m**3}
    0;                       !- Volume {m3}
!-   ===========  ALL OBJECTS IN CLASS: SURFACEGEOMETRY ===========
SurfaceGeometry,
!                                                                                                                                                            BLAST Translator units, UpperLeftCorner, Counter Clock-Wise, World Coordinate System
!                                                                                                                                                            Note original Building and Zone Origins are retained
    UpperLeftCorner,         !- SurfaceStartingPosition
    CounterClockWise,        !- VertexEntry
    WorldCoordinateSystem;   !- SurfaceGeometryKey
!-   ===========  ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER ===========
Surface:HeatTransfer,
    Zn001:Wall001,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    EXTWALL80,               !- Construction Name of the Surface
    RESISTIVE ZONE,          !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    0,                       !- Vertex 1 X-coordinate {m}
    0,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    0,                       !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    10,                      !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    10,                      !- Vertex 4 X-coordinate {m}
    0,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn001:Wall002,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    EXTWALL80,               !- Construction Name of the Surface
    RESISTIVE ZONE,          !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    0,                       !- Vertex 1 X-coordinate {m}
    8,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    0,                       !- Vertex 2 X-coordinate {m}
    8,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    0,                       !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    0,                       !- Vertex 4 X-coordinate {m}
    0,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn001:Wall003,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    PARTITION06,             !- Construction Name of the Surface
    RESISTIVE ZONE,          !- InsideFaceEnvironment
    OtherZone,               !- OutsideFaceEnvironment
    Zn003:Wall004,           !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    10,                      !- Vertex 1 X-coordinate {m}
    8,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    10,                      !- Vertex 2 X-coordinate {m}
    8,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    0,                       !- Vertex 3 X-coordinate {m}
    8,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    0,                       !- Vertex 4 X-coordinate {m}
    8,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn001:Wall004,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    PARTITION06,             !- Construction Name of the Surface
    RESISTIVE ZONE,          !- InsideFaceEnvironment
    OtherZone,               !- OutsideFaceEnvironment
    Zn002:Wall004,           !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    10,                      !- Vertex 1 X-coordinate {m}
    0,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    10,                      !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    10,                      !- Vertex 3 X-coordinate {m}
    8,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    10,                      !- Vertex 4 X-coordinate {m}
    8,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn001:Flr001,            !- User Supplied Surface Name
    Floor,                   !- Surface Type
    FLOOR SLAB 8 IN,         !- Construction Name of the Surface
    RESISTIVE ZONE,          !- InsideFaceEnvironment
    OtherZone,               !- OutsideFaceEnvironment
    Zn001:Flr001,            !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    1,                       !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    0,                       !- Vertex 1 X-coordinate {m}
    0,                       !- Vertex 1 Y-coordinate {m}
    0,                       !- Vertex 1 Z-coordinate {m}
    0,                       !- Vertex 2 X-coordinate {m}
    8,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    10,                      !- Vertex 3 X-coordinate {m}
    8,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    10,                      !- Vertex 4 X-coordinate {m}
    0,                       !- Vertex 4 Y-coordinate {m}
    0;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn001:Roof001,           !- User Supplied Surface Name
    Roof,                    !- Surface Type
    ROOF34,                  !- Construction Name of the Surface
    RESISTIVE ZONE,          !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0,                       !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    0,                       !- Vertex 1 X-coordinate {m}
    8,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    0,                       !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    6,                       !- Vertex 2 Z-coordinate {m}
    10,                      !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    6,                       !- Vertex 3 Z-coordinate {m}
    10,                      !- Vertex 4 X-coordinate {m}
    8,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn002:Wall001,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    EXTWALL80,               !- Construction Name of the Surface
    EAST ZONE,               !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    20,                      !- Vertex 1 X-coordinate {m}
    8,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    20,                      !- Vertex 2 X-coordinate {m}
    8,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    17,                      !- Vertex 3 X-coordinate {m}
    8,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    17,                      !- Vertex 4 X-coordinate {m}
    8,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn002:Wall002,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    EXTWALL80,               !- Construction Name of the Surface
    EAST ZONE,               !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    10,                      !- Vertex 1 X-coordinate {m}
    0,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    10,                      !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    20,                      !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    20,                      !- Vertex 4 X-coordinate {m}
    0,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn002:Wall003,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    EXTWALL80,               !- Construction Name of the Surface
    EAST ZONE,               !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    20,                      !- Vertex 1 X-coordinate {m}
    0,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    20,                      !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    20,                      !- Vertex 3 X-coordinate {m}
    8,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    20,                      !- Vertex 4 X-coordinate {m}
    8,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn002:Wall004,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    PARTITION06,             !- Construction Name of the Surface
    EAST ZONE,               !- InsideFaceEnvironment
    OtherZone,               !- OutsideFaceEnvironment
    Zn001:Wall004,           !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    10,                      !- Vertex 1 X-coordinate {m}
    8,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    10,                      !- Vertex 2 X-coordinate {m}
    8,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    10,                      !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    10,                      !- Vertex 4 X-coordinate {m}
    0,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn002:Wall005,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    PARTITION06,             !- Construction Name of the Surface
    EAST ZONE,               !- InsideFaceEnvironment
    OtherZone,               !- OutsideFaceEnvironment
    Zn003:Wall005,           !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    17,                      !- Vertex 1 X-coordinate {m}
    8,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    17,                      !- Vertex 2 X-coordinate {m}
    8,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    10,                      !- Vertex 3 X-coordinate {m}
    8,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    10,                      !- Vertex 4 X-coordinate {m}
    8,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn002:Flr001,            !- User Supplied Surface Name
    Floor,                   !- Surface Type
    FLOOR SLAB 8 IN,         !- Construction Name of the Surface
    EAST ZONE,               !- InsideFaceEnvironment
    OtherZone,               !- OutsideFaceEnvironment
    Zn002:Flr001,            !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    1,                       !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    10,                      !- Vertex 1 X-coordinate {m}
    0,                       !- Vertex 1 Y-coordinate {m}
    0,                       !- Vertex 1 Z-coordinate {m}
    10,                      !- Vertex 2 X-coordinate {m}
    8,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    20,                      !- Vertex 3 X-coordinate {m}
    8,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    20,                      !- Vertex 4 X-coordinate {m}
    0,                       !- Vertex 4 Y-coordinate {m}
    0;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn002:Roof001,           !- User Supplied Surface Name
    Roof,                    !- Surface Type
    ROOF34,                  !- Construction Name of the Surface
    EAST ZONE,               !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0,                       !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    10,                      !- Vertex 1 X-coordinate {m}
    8,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    10,                      !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    6,                       !- Vertex 2 Z-coordinate {m}
    20,                      !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    6,                       !- Vertex 3 Z-coordinate {m}
    20,                      !- Vertex 4 X-coordinate {m}
    8,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn003:Wall001,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    EXTWALL80,               !- Construction Name of the Surface
    NORTH ZONE,              !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    0,                       !- Vertex 1 X-coordinate {m}
    14,                      !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    0,                       !- Vertex 2 X-coordinate {m}
    14,                      !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    0,                       !- Vertex 3 X-coordinate {m}
    8,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    0,                       !- Vertex 4 X-coordinate {m}
    8,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn003:Wall002,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    EXTWALL80,               !- Construction Name of the Surface
    NORTH ZONE,              !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    17,                      !- Vertex 1 X-coordinate {m}
    14,                      !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    17,                      !- Vertex 2 X-coordinate {m}
    14,                      !- Vertex 2 Y-coordinate {m}
    3,                       !- Vertex 2 Z-coordinate {m}
    0,                       !- Vertex 3 X-coordinate {m}
    14,                      !- Vertex 3 Y-coordinate {m}
    3,                       !- Vertex 3 Z-coordinate {m}
    0,                       !- Vertex 4 X-coordinate {m}
    14,                      !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn003:Wall003,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    EXTWALL80,               !- Construction Name of the Surface
    NORTH ZONE,              !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    17,                      !- Vertex 1 X-coordinate {m}
    8,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    17,                      !- Vertex 2 X-coordinate {m}
    8,                       !- Vertex 2 Y-coordinate {m}
    3,                       !- Vertex 2 Z-coordinate {m}
    17,                      !- Vertex 3 X-coordinate {m}
    14,                      !- Vertex 3 Y-coordinate {m}
    3,                       !- Vertex 3 Z-coordinate {m}
    17,                      !- Vertex 4 X-coordinate {m}
    14,                      !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn003:Wall004,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    PARTITION06,             !- Construction Name of the Surface
    NORTH ZONE,              !- InsideFaceEnvironment
    OtherZone,               !- OutsideFaceEnvironment
    Zn001:Wall003,           !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    0,                       !- Vertex 1 X-coordinate {m}
    8,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    0,                       !- Vertex 2 X-coordinate {m}
    8,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    10,                      !- Vertex 3 X-coordinate {m}
    8,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    10,                      !- Vertex 4 X-coordinate {m}
    8,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn003:Wall005,           !- User Supplied Surface Name
    Wall,                    !- Surface Type
    PARTITION06,             !- Construction Name of the Surface
    NORTH ZONE,              !- InsideFaceEnvironment
    OtherZone,               !- OutsideFaceEnvironment
    Zn002:Wall005,           !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    10,                      !- Vertex 1 X-coordinate {m}
    8,                       !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    10,                      !- Vertex 2 X-coordinate {m}
    8,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    17,                      !- Vertex 3 X-coordinate {m}
    8,                       !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    17,                      !- Vertex 4 X-coordinate {m}
    8,                       !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn003:Flr001,            !- User Supplied Surface Name
    Floor,                   !- Surface Type
    FLOOR SLAB 8 IN,         !- Construction Name of the Surface
    NORTH ZONE,              !- InsideFaceEnvironment
    OtherZone,               !- OutsideFaceEnvironment
    Zn003:Flr001,            !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    1,                       !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    0,                       !- Vertex 1 X-coordinate {m}
    8,                       !- Vertex 1 Y-coordinate {m}
    0,                       !- Vertex 1 Z-coordinate {m}
    0,                       !- Vertex 2 X-coordinate {m}
    14,                      !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    17,                      !- Vertex 3 X-coordinate {m}
    14,                      !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    17,                      !- Vertex 4 X-coordinate {m}
    8,                       !- Vertex 4 Y-coordinate {m}
    0;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn003:Roof001,           !- User Supplied Surface Name
    Roof,                    !- Surface Type
    ROOF34,                  !- Construction Name of the Surface
    NORTH ZONE,              !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0,                       !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    0,                       !- Vertex 1 X-coordinate {m}
    14,                      !- Vertex 1 Y-coordinate {m}
    6,                       !- Vertex 1 Z-coordinate {m}
    0,                       !- Vertex 2 X-coordinate {m}
    8,                       !- Vertex 2 Y-coordinate {m}
    6,                       !- Vertex 2 Z-coordinate {m}
    17,                      !- Vertex 3 X-coordinate {m}
    8,                       !- Vertex 3 Y-coordinate {m}
    6,                       !- Vertex 3 Z-coordinate {m}
    17,                      !- Vertex 4 X-coordinate {m}
    14,                      !- Vertex 4 Y-coordinate {m}
    6;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn003:Wall003a,          !- User Supplied Surface Name
    Wall,                    !- Surface Type
    EXTWALL80-earth,         !- Construction Name of the Surface
    NORTH ZONE,              !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    17,                      !- Vertex 1 X-coordinate {m}
    8,                       !- Vertex 1 Y-coordinate {m}
    3,                       !- Vertex 1 Z-coordinate {m}
    17,                      !- Vertex 2 X-coordinate {m}
    8,                       !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    17,                      !- Vertex 3 X-coordinate {m}
    14,                      !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    17,                      !- Vertex 4 X-coordinate {m}
    14,                      !- Vertex 4 Y-coordinate {m}
    3;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Zn003:Wall002a,          !- User Supplied Surface Name
    Wall,                    !- Surface Type
    EXTWALL80-earth,         !- Construction Name of the Surface
    NORTH ZONE,              !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    17,                      !- Vertex 1 X-coordinate {m}
    14,                      !- Vertex 1 Y-coordinate {m}
    3,                       !- Vertex 1 Z-coordinate {m}
    17,                      !- Vertex 2 X-coordinate {m}
    14,                      !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    0,                       !- Vertex 3 X-coordinate {m}
    14,                      !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    0,                       !- Vertex 4 X-coordinate {m}
    14,                      !- Vertex 4 Y-coordinate {m}
    3;                       !- Vertex 4 Z-coordinate {m}
!-   ===========  ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER:SUB ===========
Surface:HeatTransfer:Sub,
    Zn001:Wall001:Win001,    !- User Supplied Surface Name
    WINDOW,                  !- Surface Type
    WIN-CON-LIGHT,           !- Construction Name of the Surface
    Zn001:Wall001,           !- Base Surface Name
    ,                        !- OutsideFaceEnvironment Object
    0.5,                     !- View Factor to Ground
    winshadecontrol,         !- Name of shading control (windows only)
    ,                        !- WindowFrameAndDivider Name
    1,                       !- Multiplier
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    0.548,                   !- Vertex 1 X-coordinate {m}
    0,                       !- Vertex 1 Y-coordinate {m}
    4.5,                     !- Vertex 1 Z-coordinate {m}
    0.548,                   !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    0.5,                     !- Vertex 2 Z-coordinate {m}
    6.548,                   !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    0.5,                     !- Vertex 3 Z-coordinate {m}
    6.548,                   !- Vertex 4 X-coordinate {m}
    0,                       !- Vertex 4 Y-coordinate {m}
    4.5;                     !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer:Sub,
    Zn002:Wall002:Win001,    !- User Supplied Surface Name
    Window,                  !- Surface Type
    WIN-CON-LIGHT,           !- Construction Name of the Surface
    Zn002:Wall002,           !- Base Surface Name
    ,                        !- OutsideFaceEnvironment Object
    0.5,                     !- View Factor to Ground
    winshadecontrol,         !- Name of shading control (windows only)
    ,                        !- WindowFrameAndDivider Name
    1,                       !- Multiplier
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    10.548,                  !- Vertex 1 X-coordinate {m}
    0,                       !- Vertex 1 Y-coordinate {m}
    4.5,                     !- Vertex 1 Z-coordinate {m}
    10.548,                  !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    0.5,                     !- Vertex 2 Z-coordinate {m}
    16.548,                  !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    0.5,                     !- Vertex 3 Z-coordinate {m}
    16.548,                  !- Vertex 4 X-coordinate {m}
    0,                       !- Vertex 4 Y-coordinate {m}
    4.5;                     !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer:Sub,
    Zn003:Wall002:Win001,    !- User Supplied Surface Name
    Window,                  !- Surface Type
    WIN-CON-LIGHT,           !- Construction Name of the Surface
    Zn003:Wall002,           !- Base Surface Name
    ,                        !- OutsideFaceEnvironment Object
    0.5,                     !- View Factor to Ground
    winshadecontrol,         !- Name of shading control (windows only)
    ,                        !- WindowFrameAndDivider Name
    1,                       !- Multiplier
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    10.548,                  !- Vertex 1 X-coordinate {m}
    14,                      !- Vertex 1 Y-coordinate {m}
    5,                       !- Vertex 1 Z-coordinate {m}
    10.548,                  !- Vertex 2 X-coordinate {m}
    14,                      !- Vertex 2 Y-coordinate {m}
    3.5,                     !- Vertex 2 Z-coordinate {m}
    5.548,                   !- Vertex 3 X-coordinate {m}
    14,                      !- Vertex 3 Y-coordinate {m}
    3.5,                     !- Vertex 3 Z-coordinate {m}
    5.548,                   !- Vertex 4 X-coordinate {m}
    14,                      !- Vertex 4 Y-coordinate {m}
    5;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer:Sub,
    Zn002:Wall003:Win001,    !- User Supplied Surface Name
    Window,                  !- Surface Type
    WIN-CON-LIGHT,           !- Construction Name of the Surface
    Zn002:Wall003,           !- Base Surface Name
    ,                        !- OutsideFaceEnvironment Object
    0.5,                     !- View Factor to Ground
    winshadecontrol,         !- Name of shading control (windows only)
    ,                        !- WindowFrameAndDivider Name
    1,                       !- Multiplier
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    20,                      !- Vertex 1 X-coordinate {m}
    1,                       !- Vertex 1 Y-coordinate {m}
    4,                       !- Vertex 1 Z-coordinate {m}
    20,                      !- Vertex 2 X-coordinate {m}
    1,                       !- Vertex 2 Y-coordinate {m}
    1,                       !- Vertex 2 Z-coordinate {m}
    20,                      !- Vertex 3 X-coordinate {m}
    3,                       !- Vertex 3 Y-coordinate {m}
    1,                       !- Vertex 3 Z-coordinate {m}
    20,                      !- Vertex 4 X-coordinate {m}
    3,                       !- Vertex 4 Y-coordinate {m}
    4;                       !- Vertex 4 Z-coordinate {m}
!-   ===========  ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER:INTERNALMASS ===========
Surface:HeatTransfer:InternalMass,
    mass floor,              !- User Supplied Surface Name
    floor mass,              !- Construction Name of the Surface
    RESISTIVE ZONE,          !- Interior Environment
    900;                     !- Surface area {m2}
Surface:HeatTransfer:InternalMass,
    mass floorz2,            !- User Supplied Surface Name
    floor mass,              !- Construction Name of the Surface
    EAST ZONE,               !- Interior Environment
    900;                     !- Surface area {m2}
Surface:HeatTransfer:InternalMass,
    mass floorznorth,        !- User Supplied Surface Name
    floor mass,              !- Construction Name of the Surface
    NORTH ZONE,              !- Interior Environment
    900;                     !- Surface area {m2}
!-   ===========  ALL OBJECTS IN CLASS: SURFACE:SHADING:ATTACHED ===========
Surface:Shading:Attached,
    Zn001:Wall001:Shade001,  !- User Supplied Surface Name
    Zn001:Wall001,           !- Base Surface Name
    ,                        !- TransSchedShadowSurf
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    0.5,                     !- Vertex 1 X-coordinate {m}
    -1.1,                    !- Vertex 1 Y-coordinate {m}
    3,                       !- Vertex 1 Z-coordinate {m}
    0.5,                     !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    3,                       !- Vertex 2 Z-coordinate {m}
    10,                      !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    3,                       !- Vertex 3 Z-coordinate {m}
    10,                      !- Vertex 4 X-coordinate {m}
    -1.1,                    !- Vertex 4 Y-coordinate {m}
    3;                       !- Vertex 4 Z-coordinate {m}
Surface:Shading:Attached,
    Zn001:Wall001:Shade002,  !- User Supplied Surface Name
    Zn001:Wall001,           !- Base Surface Name
    ,                        !- TransSchedShadowSurf
    4,                       !- Number of Surface Vertice Groups -- Number of (X,Y,Z) groups in this surface
    10.5,                    !- Vertex 1 X-coordinate {m}
    -1.1,                    !- Vertex 1 Y-coordinate {m}
    3,                       !- Vertex 1 Z-coordinate {m}
    10.5,                    !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    3,                       !- Vertex 2 Z-coordinate {m}
    19.5,                    !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    3,                       !- Vertex 3 Z-coordinate {m}
    19.5,                    !- Vertex 4 X-coordinate {m}
    -1.1,                    !- Vertex 4 Y-coordinate {m}
    3;                       !- Vertex 4 Z-coordinate {m}
!-   ===========  ALL OBJECTS IN CLASS: WINDOWSHADINGCONTROL ===========
WINDOWSHADINGCONTROL,
    winshadecontrol,         !- User Supplied Shading Control Name
    ExteriorNonInsulatingShade,
                             !- Control type
    winshadeconst,           !- Name of construction with shading
    OutsideAirTemp,          !- Trigger
    Cooling Setpoints,       !- Schedule name
    15;                      !- SetPoint {W/m2, W or deg C}
!-   ===========  ALL OBJECTS IN CLASS: SCHEDULETYPE ===========
ScheduleType,
!                                                                                                                                                            Not limited
    Any Number;              !- ScheduleType Name
ScheduleType,
    Fraction,                !- ScheduleType Name
    0.0 : 1.0 ,              !- range
    CONTINUOUS;              !- Numeric Type
ScheduleType,
    Temperature,             !- ScheduleType Name
    -60:200,                 !- range
    CONTINUOUS;              !- Numeric Type
ScheduleType,
    Control Type,            !- ScheduleType Name
    0:4,                     !- range
    DISCRETE;                !- Numeric Type
ScheduleType,
    On/Off,                  !- ScheduleType Name
    0:1,                     !- range
    DISCRETE;                !- Numeric Type
!-   ===========  ALL OBJECTS IN CLASS: DAYSCHEDULE ===========
DAYSCHEDULE,
    ActLevDay,               !- Name
    Any Number,              !- ScheduleType
    131.8,                   !- Hour 1
    131.8,                   !- Hour 2
    131.8,                   !- Hour 3
    131.8,                   !- Hour 4
    131.8,                   !- Hour 5
    131.8,                   !- Hour 6
    131.8,                   !- Hour 7
    131.8,                   !- Hour 8
    131.8,                   !- Hour 9
    131.8,                   !- Hour 10
    131.8,                   !- Hour 11
    131.8,                   !- Hour 12
    131.8,                   !- Hour 13
    131.8,                   !- Hour 14
    131.8,                   !- Hour 15
    131.8,                   !- Hour 16
    131.8,                   !- Hour 17
    131.8,                   !- Hour 18
    131.8,                   !- Hour 19
    131.8,                   !- Hour 20
    131.8,                   !- Hour 21
    131.8,                   !- Hour 22
    131.8,                   !- Hour 23
    131.8;                   !- Hour 24
DAYSCHEDULE,
    WorkEffDay,              !- Name
    Any Number,              !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0,                       !- Hour 6
    0,                       !- Hour 7
    0,                       !- Hour 8
    0,                       !- Hour 9
    0,                       !- Hour 10
    0,                       !- Hour 11
    0,                       !- Hour 12
    0,                       !- Hour 13
    0,                       !- Hour 14
    0,                       !- Hour 15
    0,                       !- Hour 16
    0,                       !- Hour 17
    0,                       !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24
DAYSCHEDULE,
    CloInsDay,               !- Name
    Any Number,              !- ScheduleType
    1,                       !- Hour 1
    1,                       !- Hour 2
    1,                       !- Hour 3
    1,                       !- Hour 4
    1,                       !- Hour 5
    1,                       !- Hour 6
    1,                       !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    1,                       !- Hour 18
    1,                       !- Hour 19
    1,                       !- Hour 20
    1,                       !- Hour 21
    1,                       !- Hour 22
    1,                       !- Hour 23
    1;                       !- Hour 24
DAYSCHEDULE,
    AirVelDay,               !- Name
    Any Number,              !- ScheduleType
    0.137,                   !- Hour 1
    0.137,                   !- Hour 2
    0.137,                   !- Hour 3
    0.137,                   !- Hour 4
    0.137,                   !- Hour 5
    0.137,                   !- Hour 6
    0.137,                   !- Hour 7
    0.137,                   !- Hour 8
    0.137,                   !- Hour 9
    0.137,                   !- Hour 10
    0.137,                   !- Hour 11
    0.137,                   !- Hour 12
    0.137,                   !- Hour 13
    0.137,                   !- Hour 14
    0.137,                   !- Hour 15
    0.137,                   !- Hour 16
    0.137,                   !- Hour 17
    0.137,                   !- Hour 18
    0.137,                   !- Hour 19
    0.137,                   !- Hour 20
    0.137,                   !- Hour 21
    0.137,                   !- Hour 22
    0.137,                   !- Hour 23
    0.137;                   !- Hour 24
DAYSCHEDULE,
    BLDG Day   1,            !- Name
    Any Number,              !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0,                       !- Hour 6
    0.1,                     !- Hour 7
    0.5,                     !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    0.5,                     !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    0.5,                     !- Hour 17
    0.1,                     !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24
DAYSCHEDULE,
    BLDG Day   2,            !- Name
    Any Number,              !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0,                       !- Hour 6
    0,                       !- Hour 7
    0,                       !- Hour 8
    0,                       !- Hour 9
    0,                       !- Hour 10
    0,                       !- Hour 11
    0,                       !- Hour 12
    0,                       !- Hour 13
    0,                       !- Hour 14
    0,                       !- Hour 15
    0,                       !- Hour 16
    0,                       !- Hour 17
    0,                       !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24
DAYSCHEDULE,
    BLDG Day   5,            !- Name
    Any Number,              !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0,                       !- Hour 6
    0,                       !- Hour 7
    0,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    1,                       !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24
DAYSCHEDULE,
    BLDG Day   6,            !- Name
    Any Number,              !- ScheduleType
    0.05,                    !- Hour 1
    0.05,                    !- Hour 2
    0.05,                    !- Hour 3
    0.05,                    !- Hour 4
    0.05,                    !- Hour 5
    0.05,                    !- Hour 6
    0.2,                     !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    0.5,                     !- Hour 18
    0.05,                    !- Hour 19
    0.05,                    !- Hour 20
    0.05,                    !- Hour 21
    0.05,                    !- Hour 22
    0.05,                    !- Hour 23
    0.05;                    !- Hour 24
DAYSCHEDULE,
    BLDG Day   7,            !- Name
    Any Number,              !- ScheduleType
    0.05,                    !- Hour 1
    0.05,                    !- Hour 2
    0.05,                    !- Hour 3
    0.05,                    !- Hour 4
    0.05,                    !- Hour 5
    0.05,                    !- Hour 6
    0.05,                    !- Hour 7
    0.05,                    !- Hour 8
    0.05,                    !- Hour 9
    0.05,                    !- Hour 10
    0.05,                    !- Hour 11
    0.05,                    !- Hour 12
    0.05,                    !- Hour 13
    0.05,                    !- Hour 14
    0.05,                    !- Hour 15
    0.05,                    !- Hour 16
    0.05,                    !- Hour 17
    0.05,                    !- Hour 18
    0.05,                    !- Hour 19
    0.05,                    !- Hour 20
    0.05,                    !- Hour 21
    0.05,                    !- Hour 22
    0.05,                    !- Hour 23
    0.05;                    !- Hour 24
DAYSCHEDULE,
    SYS Day   1,             !- Name
    Any Number,              !- ScheduleType
    1,                       !- Hour 1
    1,                       !- Hour 2
    1,                       !- Hour 3
    1,                       !- Hour 4
    1,                       !- Hour 5
    1,                       !- Hour 6
    1,                       !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    1,                       !- Hour 18
    1,                       !- Hour 19
    1,                       !- Hour 20
    1,                       !- Hour 21
    1,                       !- Hour 22
    1,                       !- Hour 23
    1;                       !- Hour 24
DAYSCHEDULE,
    SYS Day   2,             !- Name
    Any Number,              !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0,                       !- Hour 6
    0,                       !- Hour 7
    0,                       !- Hour 8
    0,                       !- Hour 9
    0,                       !- Hour 10
    0,                       !- Hour 11
    0,                       !- Hour 12
    0,                       !- Hour 13
    0,                       !- Hour 14
    0,                       !- Hour 15
    0,                       !- Hour 16
    0,                       !- Hour 17
    0,                       !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24
DAYSCHEDULE,
    SYS Day   3,             !- Name
    Any Number,              !- ScheduleType
    0.05,                    !- Hour 1
    0.05,                    !- Hour 2
    0.05,                    !- Hour 3
    0.05,                    !- Hour 4
    0.05,                    !- Hour 5
    0.05,                    !- Hour 6
    0.05,                    !- Hour 7
    0.05,                    !- Hour 8
    0.05,                    !- Hour 9
    0.05,                    !- Hour 10
    0.05,                    !- Hour 11
    0.05,                    !- Hour 12
    0.05,                    !- Hour 13
    0.05,                    !- Hour 14
    0.05,                    !- Hour 15
    0.05,                    !- Hour 16
    0.05,                    !- Hour 17
    0.05,                    !- Hour 18
    0.05,                    !- Hour 19
    0.05,                    !- Hour 20
    0.05,                    !- Hour 21
    0.05,                    !- Hour 22
    0.05,                    !- Hour 23
    0.05;                    !- Hour 24
DAYSCHEDULE,
    SYS Day   4,             !- Name
    Any Number,              !- ScheduleType
    0.15,                    !- Hour 1
    0.15,                    !- Hour 2
    0.15,                    !- Hour 3
    0.15,                    !- Hour 4
    0.15,                    !- Hour 5
    0.15,                    !- Hour 6
    0.15,                    !- Hour 7
    0.15,                    !- Hour 8
    0.15,                    !- Hour 9
    0.15,                    !- Hour 10
    0.15,                    !- Hour 11
    0.15,                    !- Hour 12
    0.15,                    !- Hour 13
    0.15,                    !- Hour 14
    0.15,                    !- Hour 15
    0.15,                    !- Hour 16
    0.15,                    !- Hour 17
    0.15,                    !- Hour 18
    0.15,                    !- Hour 19
    0.15,                    !- Hour 20
    0.15,                    !- Hour 21
    0.15,                    !- Hour 22
    0.15,                    !- Hour 23
    0.15;                    !- Hour 24
DAYSCHEDULE,
    SYS Day   5,             !- Name
    Any Number,              !- ScheduleType
    0.5,                     !- Hour 1
    0.5,                     !- Hour 2
    0.5,                     !- Hour 3
    0.5,                     !- Hour 4
    0.5,                     !- Hour 5
    0.5,                     !- Hour 6
    0.5,                     !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    0.5,                     !- Hour 18
    0.5,                     !- Hour 19
    0.5,                     !- Hour 20
    0.5,                     !- Hour 21
    0.5,                     !- Hour 22
    0.5,                     !- Hour 23
    0.5;                     !- Hour 24
DAYSCHEDULE,
    SYS Day   6,             !- Name
    Any Number,              !- ScheduleType
    0.5,                     !- Hour 1
    0.5,                     !- Hour 2
    0.5,                     !- Hour 3
    0.5,                     !- Hour 4
    0.5,                     !- Hour 5
    0.5,                     !- Hour 6
    0.5,                     !- Hour 7
    0.6,                     !- Hour 8
    0.6,                     !- Hour 9
    0.6,                     !- Hour 10
    0.6,                     !- Hour 11
    0.6,                     !- Hour 12
    0.6,                     !- Hour 13
    0.6,                     !- Hour 14
    0.6,                     !- Hour 15
    0.6,                     !- Hour 16
    0.6,                     !- Hour 17
    0.5,                     !- Hour 18
    0.5,                     !- Hour 19
    0.5,                     !- Hour 20
    0.5,                     !- Hour 21
    0.5,                     !- Hour 22
    0.5,                     !- Hour 23
    0.5;                     !- Hour 24
DAYSCHEDULE,
    PLT Day   1,             !- Name
    Any Number,              !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0,                       !- Hour 6
    0.1,                     !- Hour 7
    0.5,                     !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    0.5,                     !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    0.5,                     !- Hour 17
    0.1,                     !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24
DAYSCHEDULE,
    PLT Day   2,             !- Name
    Any Number,              !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0,                       !- Hour 6
    0,                       !- Hour 7
    0,                       !- Hour 8
    0,                       !- Hour 9
    0,                       !- Hour 10
    0,                       !- Hour 11
    0,                       !- Hour 12
    0,                       !- Hour 13
    0,                       !- Hour 14
    0,                       !- Hour 15
    0,                       !- Hour 16
    0,                       !- Hour 17
    0,                       !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24
DAYSCHEDULE,
    DayAllON,                !- Name
    on/off,                  !- ScheduleType
    1,                       !- Hour 1
    1,                       !- Hour 2
    1,                       !- Hour 3
    1,                       !- Hour 4
    1,                       !- Hour 5
    1,                       !- Hour 6
    1,                       !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    1,                       !- Hour 18
    1,                       !- Hour 19
    1,                       !- Hour 20
    1,                       !- Hour 21
    1,                       !- Hour 22
    1,                       !- Hour 23
    1;                       !- Hour 24
DAYSCHEDULE,
    DayAllOFF,               !- Name
    on/off,                  !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0,                       !- Hour 6
    0,                       !- Hour 7
    0,                       !- Hour 8
    0,                       !- Hour 9
    0,                       !- Hour 10
    0,                       !- Hour 11
    0,                       !- Hour 12
    0,                       !- Hour 13
    0,                       !- Hour 14
    0,                       !- Hour 15
    0,                       !- Hour 16
    0,                       !- Hour 17
    0,                       !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24
DAYSCHEDULE,
    TransDayOn,              !- Name
    Fraction,                !- ScheduleType
    1,                       !- Hour 1
    1,                       !- Hour 2
    1,                       !- Hour 3
    1,                       !- Hour 4
    1,                       !- Hour 5
    1,                       !- Hour 6
    1,                       !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    1,                       !- Hour 18
    1,                       !- Hour 19
    1,                       !- Hour 20
    1,                       !- Hour 21
    1,                       !- Hour 22
    1,                       !- Hour 23
    1;                       !- Hour 24
DAYSCHEDULE,
    TransDayOff,             !- Name
    Fraction,                !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0,                       !- Hour 6
    0,                       !- Hour 7
    0,                       !- Hour 8
    0,                       !- Hour 9
    0,                       !- Hour 10
    0,                       !- Hour 11
    0,                       !- Hour 12
    0,                       !- Hour 13
    0,                       !- Hour 14
    0,                       !- Hour 15
    0,                       !- Hour 16
    0,                       !- Hour 17
    0,                       !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24
DAYSCHEDULE,
!                                                                                                                                                           ****************************************************************
!                                                                                                                                                            Schedules
    Day On Peak,             !- Name
    Fraction,                !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0,                       !- Hour 6
    0,                       !- Hour 7
    0,                       !- Hour 8
    0,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    1,                       !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24
DAYSCHEDULE,
    Day Off Peak,            !- Name
    Fraction,                !- ScheduleType
    1,                       !- Hour 1
    1,                       !- Hour 2
    1,                       !- Hour 3
    1,                       !- Hour 4
    1,                       !- Hour 5
    1,                       !- Hour 6
    1,                       !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    0,                       !- Hour 10
    0,                       !- Hour 11
    0,                       !- Hour 12
    0,                       !- Hour 13
    0,                       !- Hour 14
    0,                       !- Hour 15
    0,                       !- Hour 16
    0,                       !- Hour 17
    0,                       !- Hour 18
    1,                       !- Hour 19
    1,                       !- Hour 20
    1,                       !- Hour 21
    1,                       !- Hour 22
    1,                       !- Hour 23
    1;                       !- Hour 24
DAYSCHEDULE,
    DayON,                   !- Name
    Fraction,                !- ScheduleType
    1,                       !- Hour 1
    1,                       !- Hour 2
    1,                       !- Hour 3
    1,                       !- Hour 4
    1,                       !- Hour 5
    1,                       !- Hour 6
    1,                       !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    1,                       !- Hour 18
    1,                       !- Hour 19
    1,                       !- Hour 20
    1,                       !- Hour 21
    1,                       !- Hour 22
    1,                       !- Hour 23
    1;                       !- Hour 24
DAYSCHEDULE,
    Summer Supply Air Temp Day Sch,
                             !- Name
    Temperature,             !- ScheduleType
    13,                      !- Hour 1
    13,                      !- Hour 2
    13,                      !- Hour 3
    13,                      !- Hour 4
    13,                      !- Hour 5
    13,                      !- Hour 6
    13,                      !- Hour 7
    13,                      !- Hour 8
    13,                      !- Hour 9
    13,                      !- Hour 10
    13,                      !- Hour 11
    13,                      !- Hour 12
    13,                      !- Hour 13
    13,                      !- Hour 14
    13,                      !- Hour 15
    13,                      !- Hour 16
    13,                      !- Hour 17
    13,                      !- Hour 18
    13,                      !- Hour 19
    13,                      !- Hour 20
    13,                      !- Hour 21
    13,                      !- Hour 22
    13,                      !- Hour 23
    13;                      !- Hour 24
DAYSCHEDULE,
    Winter Supply Air Temp Day Sch,
                             !- Name
    Temperature,             !- ScheduleType
    16,                      !- Hour 1
    16,                      !- Hour 2
    16,                      !- Hour 3
    16,                      !- Hour 4
    16,                      !- Hour 5
    16,                      !- Hour 6
    16,                      !- Hour 7
    16,                      !- Hour 8
    16,                      !- Hour 9
    16,                      !- Hour 10
    16,                      !- Hour 11
    16,                      !- Hour 12
    16,                      !- Hour 13
    16,                      !- Hour 14
    16,                      !- Hour 15
    16,                      !- Hour 16
    16,                      !- Hour 17
    16,                      !- Hour 18
    16,                      !- Hour 19
    16,                      !- Hour 20
    16,                      !- Hour 21
    16,                      !- Hour 22
    16,                      !- Hour 23
    16;                      !- Hour 24
DAYSCHEDULE,
    Chilled Water Loop Daily,!- Name
    Temperature,             !- ScheduleType
    6.67,                    !- Hour 1
    6.67,                    !- Hour 2
    6.67,                    !- Hour 3
    6.67,                    !- Hour 4
    6.67,                    !- Hour 5
    6.67,                    !- Hour 6
    6.67,                    !- Hour 7
    6.67,                    !- Hour 8
    6.67,                    !- Hour 9
    6.67,                    !- Hour 10
    6.67,                    !- Hour 11
    6.67,                    !- Hour 12
    6.67,                    !- Hour 13
    6.67,                    !- Hour 14
    6.67,                    !- Hour 15
    6.67,                    !- Hour 16
    6.67,                    !- Hour 17
    6.67,                    !- Hour 18
    6.67,                    !- Hour 19
    6.67,                    !- Hour 20
    6.67,                    !- Hour 21
    6.67,                    !- Hour 22
    6.67,                    !- Hour 23
    6.67;                    !- Hour 24
DAYSCHEDULE,
    Hot Water Loop Daily,    !- Name
    Temperature,             !- ScheduleType
    60,                      !- Hour 1
    60,                      !- Hour 2
    60,                      !- Hour 3
    60,                      !- Hour 4
    60,                      !- Hour 5
    60,                      !- Hour 6
    60,                      !- Hour 7
    60,                      !- Hour 8
    60,                      !- Hour 9
    60,                      !- Hour 10
    60,                      !- Hour 11
    60,                      !- Hour 12
    60,                      !- Hour 13
    60,                      !- Hour 14
    60,                      !- Hour 15
    60,                      !- Hour 16
    60,                      !- Hour 17
    60,                      !- Hour 18
    60,                      !- Hour 19
    60,                      !- Hour 20
    60,                      !- Hour 21
    60,                      !- Hour 22
    60,                      !- Hour 23
    60;                      !- Hour 24
DAYSCHEDULE,
    SystemOperatingDaySched, !- Name
    Fraction,                !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    1,                       !- Hour 6
    1,                       !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    1,                       !- Hour 18
    1,                       !- Hour 19
    1,                       !- Hour 20
    1,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24
DAYSCHEDULE,
    SystemOffDaySched,       !- Name
    Fraction,                !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0,                       !- Hour 6
    0,                       !- Hour 7
    0,                       !- Hour 8
    0,                       !- Hour 9
    0,                       !- Hour 10
    0,                       !- Hour 11
    0,                       !- Hour 12
    0,                       !- Hour 13
    0,                       !- Hour 14
    0,                       !- Hour 15
    0,                       !- Hour 16
    0,                       !- Hour 17
    0,                       !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24
DAYSCHEDULE,
    SystemOnDaySched,        !- Name
    Fraction,                !- ScheduleType
    1,                       !- Hour 1
    1,                       !- Hour 2
    1,                       !- Hour 3
    1,                       !- Hour 4
    1,                       !- Hour 5
    1,                       !- Hour 6
    1,                       !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    1,                       !- Hour 18
    1,                       !- Hour 19
    1,                       !- Hour 20
    1,                       !- Hour 21
    1,                       !- Hour 22
    1,                       !- Hour 23
    1;                       !- Hour 24
DAYSCHEDULE,
    Summer Zone Temp Lo Day Sch,
                             !- Name
    Temperature,             !- ScheduleType
    15,                      !- Hour 1
    15,                      !- Hour 2
    15,                      !- Hour 3
    15,                      !- Hour 4
    15,                      !- Hour 5
    15,                      !- Hour 6
    15,                      !- Hour 7
    20,                      !- Hour 8
    20,                      !- Hour 9
    20,                      !- Hour 10
    20,                      !- Hour 11
    20,                      !- Hour 12
    20,                      !- Hour 13
    20,                      !- Hour 14
    20,                      !- Hour 15
    20,                      !- Hour 16
    20,                      !- Hour 17
    20,                      !- Hour 18
    20,                      !- Hour 19
    20,                      !- Hour 20
    20,                      !- Hour 21
    20,                      !- Hour 22
    20,                      !- Hour 23
    15;                      !- Hour 24
DAYSCHEDULE,
    Winter Zone Temp Lo Day Sch,
                             !- Name
    Temperature,             !- ScheduleType
    15,                      !- Hour 1
    15,                      !- Hour 2
    15,                      !- Hour 3
    15,                      !- Hour 4
    15,                      !- Hour 5
    20,                      !- Hour 6
    20,                      !- Hour 7
    20,                      !- Hour 8
    20,                      !- Hour 9
    20,                      !- Hour 10
    20,                      !- Hour 11
    20,                      !- Hour 12
    20,                      !- Hour 13
    20,                      !- Hour 14
    20,                      !- Hour 15
    20,                      !- Hour 16
    20,                      !- Hour 17
    20,                      !- Hour 18
    20,                      !- Hour 19
    20,                      !- Hour 20
    20,                      !- Hour 21
    20,                      !- Hour 22
    15,                      !- Hour 23
    15;                      !- Hour 24
DAYSCHEDULE,
    Summer Zone Temp Hi Day Sch,
                             !- Name
    Temperature,             !- ScheduleType
    25,                      !- Hour 1
    25,                      !- Hour 2
    25,                      !- Hour 3
    25,                      !- Hour 4
    25,                      !- Hour 5
    25,                      !- Hour 6
    25,                      !- Hour 7
    25,                      !- Hour 8
    25,                      !- Hour 9
    25,                      !- Hour 10
    25,                      !- Hour 11
    25,                      !- Hour 12
    25,                      !- Hour 13
    25,                      !- Hour 14
    25,                      !- Hour 15
    25,                      !- Hour 16
    25,                      !- Hour 17
    25,                      !- Hour 18
    25,                      !- Hour 19
    25,                      !- Hour 20
    25,                      !- Hour 21
    25,                      !- Hour 22
    25,                      !- Hour 23
    25;                      !- Hour 24
DAYSCHEDULE,
    Winter Zone Temp Hi Day Sch,
                             !- Name
    Temperature,             !- ScheduleType
    50,                      !- Hour 1
    50,                      !- Hour 2
    50,                      !- Hour 3
    50,                      !- Hour 4
    50,                      !- Hour 5
    50,                      !- Hour 6
    50,                      !- Hour 7
    50,                      !- Hour 8
    50,                      !- Hour 9
    50,                      !- Hour 10
    50,                      !- Hour 11
    50,                      !- Hour 12
    50,                      !- Hour 13
    50,                      !- Hour 14
    50,                      !- Hour 15
    50,                      !- Hour 16
    50,                      !- Hour 17
    50,                      !- Hour 18
    50,                      !- Hour 19
    50,                      !- Hour 20
    50,                      !- Hour 21
    50,                      !- Hour 22
    50,                      !- Hour 23
    50;                      !- Hour 24
DAYSCHEDULE,
    Summer Control Type Day Sch,
                             !- Name
    Control Type,            !- ScheduleType
    2,                       !- Hour 1
    2,                       !- Hour 2
    2,                       !- Hour 3
    2,                       !- Hour 4
    2,                       !- Hour 5
    2,                       !- Hour 6
    2,                       !- Hour 7
    2,                       !- Hour 8
    2,                       !- Hour 9
    2,                       !- Hour 10
    2,                       !- Hour 11
    2,                       !- Hour 12
    2,                       !- Hour 13
    2,                       !- Hour 14
    2,                       !- Hour 15
    2,                       !- Hour 16
    2,                       !- Hour 17
    2,                       !- Hour 18
    2,                       !- Hour 19
    2,                       !- Hour 20
    2,                       !- Hour 21
    2,                       !- Hour 22
    2,                       !- Hour 23
    2;                       !- Hour 24
DAYSCHEDULE,
    Winter Control Type Day Sch,
                             !- Name
    Control Type,            !- ScheduleType
    1,                       !- Hour 1
    1,                       !- Hour 2
    1,                       !- Hour 3
    1,                       !- Hour 4
    1,                       !- Hour 5
    1,                       !- Hour 6
    1,                       !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    1,                       !- Hour 18
    1,                       !- Hour 19
    1,                       !- Hour 20
    1,                       !- Hour 21
    1,                       !- Hour 22
    1,                       !- Hour 23
    1;                       !- Hour 24
DAYSCHEDULE,
    lightday,                !- Name
    Any Number,              !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0.5,                     !- Hour 6
    0.5,                     !- Hour 7
    0,                       !- Hour 8
    0,                       !- Hour 9
    0,                       !- Hour 10
    0,                       !- Hour 11
    0,                       !- Hour 12
    0,                       !- Hour 13
    0,                       !- Hour 14
    0,                       !- Hour 15
    0,                       !- Hour 16
    0,                       !- Hour 17
    0.1,                     !- Hour 18
    0.3,                     !- Hour 19
    0.4,                     !- Hour 20
    1,                       !- Hour 21
    1,                       !- Hour 22
    1,                       !- Hour 23
    0.5;                     !- Hour 24
DAYSCHEDULE,
    nightventilday,          !- Name
    Control Type,            !- ScheduleType
    1,                       !- Hour 1
    1,                       !- Hour 2
    1,                       !- Hour 3
    1,                       !- Hour 4
    1,                       !- Hour 5
    1,                       !- Hour 6
    1,                       !- Hour 7
    0,                       !- Hour 8
    0,                       !- Hour 9
    0,                       !- Hour 10
    0,                       !- Hour 11
    0,                       !- Hour 12
    0,                       !- Hour 13
    0,                       !- Hour 14
    0,                       !- Hour 15
    0,                       !- Hour 16
    0,                       !- Hour 17
    0,                       !- Hour 18
    0,                       !- Hour 19
    1,                       !- Hour 20
    1,                       !- Hour 21
    1,                       !- Hour 22
    1,                       !- Hour 23
    1;                       !- Hour 24
DAYSCHEDULE,
    nightventildayh,         !- Name
    Control Type,            !- ScheduleType
    0,                       !- Hour 1
    0,                       !- Hour 2
    1,                       !- Hour 3
    1,                       !- Hour 4
    1,                       !- Hour 5
    1,                       !- Hour 6
    1,                       !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    0,                       !- Hour 11
    0,                       !- Hour 12
    0,                       !- Hour 13
    0,                       !- Hour 14
    0,                       !- Hour 15
    0,                       !- Hour 16
    0,                       !- Hour 17
    0,                       !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24
!-   ===========  ALL OBJECTS IN CLASS: WEEKSCHEDULE ===========
WEEKSCHEDULE,
    ActLevWeek,              !- Name
    ActLevDay,               !- Sunday DAYSCHEDULE Name
    ActLevDay,               !- Monday DAYSCHEDULE Name
    ActLevDay,               !- Tuesday DAYSCHEDULE Name
    ActLevDay,               !- Wednesday DAYSCHEDULE Name
    ActLevDay,               !- Thursday DAYSCHEDULE Name
    ActLevDay,               !- Friday DAYSCHEDULE Name
    ActLevDay,               !- Saturday DAYSCHEDULE Name
    ActLevDay,               !- Holiday DAYSCHEDULE Name
    ActLevDay,               !- SummerDesignDay DAYSCHEDULE Name
    ActLevDay,               !- WinterDesignDay DAYSCHEDULE Name
    ActLevDay,               !- CustomDay1 DAYSCHEDULE Name
    ActLevDay;               !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    WorkEffWeek,             !- Name
    WorkEffDay,              !- Sunday DAYSCHEDULE Name
    WorkEffDay,              !- Monday DAYSCHEDULE Name
    WorkEffDay,              !- Tuesday DAYSCHEDULE Name
    WorkEffDay,              !- Wednesday DAYSCHEDULE Name
    WorkEffDay,              !- Thursday DAYSCHEDULE Name
    WorkEffDay,              !- Friday DAYSCHEDULE Name
    WorkEffDay,              !- Saturday DAYSCHEDULE Name
    WorkEffDay,              !- Holiday DAYSCHEDULE Name
    WorkEffDay,              !- SummerDesignDay DAYSCHEDULE Name
    WorkEffDay,              !- WinterDesignDay DAYSCHEDULE Name
    WorkEffDay,              !- CustomDay1 DAYSCHEDULE Name
    WorkEffDay;              !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    CloInsWeek,              !- Name
    CloInsDay,               !- Sunday DAYSCHEDULE Name
    CloInsDay,               !- Monday DAYSCHEDULE Name
    CloInsDay,               !- Tuesday DAYSCHEDULE Name
    CloInsDay,               !- Wednesday DAYSCHEDULE Name
    CloInsDay,               !- Thursday DAYSCHEDULE Name
    CloInsDay,               !- Friday DAYSCHEDULE Name
    CloInsDay,               !- Saturday DAYSCHEDULE Name
    CloInsDay,               !- Holiday DAYSCHEDULE Name
    CloInsDay,               !- SummerDesignDay DAYSCHEDULE Name
    CloInsDay,               !- WinterDesignDay DAYSCHEDULE Name
    CloInsDay,               !- CustomDay1 DAYSCHEDULE Name
    CloInsDay;               !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    AirVelWeek,              !- Name
    AirVelDay,               !- Sunday DAYSCHEDULE Name
    AirVelDay,               !- Monday DAYSCHEDULE Name
    AirVelDay,               !- Tuesday DAYSCHEDULE Name
    AirVelDay,               !- Wednesday DAYSCHEDULE Name
    AirVelDay,               !- Thursday DAYSCHEDULE Name
    AirVelDay,               !- Friday DAYSCHEDULE Name
    AirVelDay,               !- Saturday DAYSCHEDULE Name
    AirVelDay,               !- Holiday DAYSCHEDULE Name
    AirVelDay,               !- SummerDesignDay DAYSCHEDULE Name
    AirVelDay,               !- WinterDesignDay DAYSCHEDULE Name
    AirVelDay,               !- CustomDay1 DAYSCHEDULE Name
    AirVelDay;               !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    OFFICE OCCUPANCY,        !- Name
    BLDG Day   2,            !- Sunday DAYSCHEDULE Name
    BLDG Day   1,            !- Monday DAYSCHEDULE Name
    BLDG Day   1,            !- Tuesday DAYSCHEDULE Name
    BLDG Day   1,            !- Wednesday DAYSCHEDULE Name
    BLDG Day   1,            !- Thursday DAYSCHEDULE Name
    BLDG Day   1,            !- Friday DAYSCHEDULE Name
    BLDG Day   2,            !- Saturday DAYSCHEDULE Name
    BLDG Day   2,            !- Holiday DAYSCHEDULE Name
    BLDG Day   2,            !- SummerDesignDay DAYSCHEDULE Name
    BLDG Day   2,            !- WinterDesignDay DAYSCHEDULE Name
    BLDG Day   2,            !- CustomDay1 DAYSCHEDULE Name
    BLDG Day   2;            !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    INTERMITTENT,            !- Name
    BLDG Day   2,            !- Sunday DAYSCHEDULE Name
    BLDG Day   5,            !- Monday DAYSCHEDULE Name
    BLDG Day   5,            !- Tuesday DAYSCHEDULE Name
    BLDG Day   5,            !- Wednesday DAYSCHEDULE Name
    BLDG Day   5,            !- Thursday DAYSCHEDULE Name
    BLDG Day   5,            !- Friday DAYSCHEDULE Name
    BLDG Day   2,            !- Saturday DAYSCHEDULE Name
    BLDG Day   2,            !- Holiday DAYSCHEDULE Name
    BLDG Day   2,            !- SummerDesignDay DAYSCHEDULE Name
    BLDG Day   2,            !- WinterDesignDay DAYSCHEDULE Name
    BLDG Day   2,            !- CustomDay1 DAYSCHEDULE Name
    BLDG Day   2;            !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    OFFICE LIGHTING,         !- Name
    BLDG Day   7,            !- Sunday DAYSCHEDULE Name
    BLDG Day   6,            !- Monday DAYSCHEDULE Name
    BLDG Day   6,            !- Tuesday DAYSCHEDULE Name
    BLDG Day   6,            !- Wednesday DAYSCHEDULE Name
    BLDG Day   6,            !- Thursday DAYSCHEDULE Name
    BLDG Day   6,            !- Friday DAYSCHEDULE Name
    BLDG Day   7,            !- Saturday DAYSCHEDULE Name
    BLDG Day   7,            !- Holiday DAYSCHEDULE Name
    BLDG Day   7,            !- SummerDesignDay DAYSCHEDULE Name
    BLDG Day   7,            !- WinterDesignDay DAYSCHEDULE Name
    BLDG Day   7,            !- CustomDay1 DAYSCHEDULE Name
    BLDG Day   7;            !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    SYS-ON,                  !- Name
    SYS Day   1,             !- Sunday DAYSCHEDULE Name
    SYS Day   1,             !- Monday DAYSCHEDULE Name
    SYS Day   1,             !- Tuesday DAYSCHEDULE Name
    SYS Day   1,             !- Wednesday DAYSCHEDULE Name
    SYS Day   1,             !- Thursday DAYSCHEDULE Name
    SYS Day   1,             !- Friday DAYSCHEDULE Name
    SYS Day   1,             !- Saturday DAYSCHEDULE Name
    SYS Day   1,             !- Holiday DAYSCHEDULE Name
    SYS Day   1,             !- SummerDesignDay DAYSCHEDULE Name
    SYS Day   1,             !- WinterDesignDay DAYSCHEDULE Name
    SYS Day   1,             !- CustomDay1 DAYSCHEDULE Name
    SYS Day   1;             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    SYS-OFF,                 !- Name
    SYS Day   2,             !- Sunday DAYSCHEDULE Name
    SYS Day   2,             !- Monday DAYSCHEDULE Name
    SYS Day   2,             !- Tuesday DAYSCHEDULE Name
    SYS Day   2,             !- Wednesday DAYSCHEDULE Name
    SYS Day   2,             !- Thursday DAYSCHEDULE Name
    SYS Day   2,             !- Friday DAYSCHEDULE Name
    SYS Day   2,             !- Saturday DAYSCHEDULE Name
    SYS Day   2,             !- Holiday DAYSCHEDULE Name
    SYS Day   2,             !- SummerDesignDay DAYSCHEDULE Name
    SYS Day   2,             !- WinterDesignDay DAYSCHEDULE Name
    SYS Day   2,             !- CustomDay1 DAYSCHEDULE Name
    SYS Day   2;             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    SYS-MINIMUM OUTSIDE AIR, !- Name
    SYS Day   3,             !- Sunday DAYSCHEDULE Name
    SYS Day   4,             !- Monday DAYSCHEDULE Name
    SYS Day   4,             !- Tuesday DAYSCHEDULE Name
    SYS Day   4,             !- Wednesday DAYSCHEDULE Name
    SYS Day   4,             !- Thursday DAYSCHEDULE Name
    SYS Day   4,             !- Friday DAYSCHEDULE Name
    SYS Day   3,             !- Saturday DAYSCHEDULE Name
    SYS Day   3,             !- Holiday DAYSCHEDULE Name
    SYS Day   3,             !- SummerDesignDay DAYSCHEDULE Name
    SYS Day   3,             !- WinterDesignDay DAYSCHEDULE Name
    SYS Day   3,             !- CustomDay1 DAYSCHEDULE Name
    SYS Day   3;             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    SYS-HOSPITAL EQUIPMENT,  !- Name
    SYS Day   6,             !- Sunday DAYSCHEDULE Name
    SYS Day   5,             !- Monday DAYSCHEDULE Name
    SYS Day   5,             !- Tuesday DAYSCHEDULE Name
    SYS Day   5,             !- Wednesday DAYSCHEDULE Name
    SYS Day   5,             !- Thursday DAYSCHEDULE Name
    SYS Day   5,             !- Friday DAYSCHEDULE Name
    SYS Day   6,             !- Saturday DAYSCHEDULE Name
    SYS Day   6,             !- Holiday DAYSCHEDULE Name
    SYS Day   6,             !- SummerDesignDay DAYSCHEDULE Name
    SYS Day   6,             !- WinterDesignDay DAYSCHEDULE Name
    SYS Day   6,             !- CustomDay1 DAYSCHEDULE Name
    SYS Day   6;             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    PLT-OFFICE OCCUPANCY,    !- Name
    PLT Day   2,             !- Sunday DAYSCHEDULE Name
    PLT Day   1,             !- Monday DAYSCHEDULE Name
    PLT Day   1,             !- Tuesday DAYSCHEDULE Name
    PLT Day   1,             !- Wednesday DAYSCHEDULE Name
    PLT Day   1,             !- Thursday DAYSCHEDULE Name
    PLT Day   1,             !- Friday DAYSCHEDULE Name
    PLT Day   2,             !- Saturday DAYSCHEDULE Name
    PLT Day   2,             !- Holiday DAYSCHEDULE Name
    PLT Day   2,             !- SummerDesignDay DAYSCHEDULE Name
    PLT Day   2,             !- WinterDesignDay DAYSCHEDULE Name
    PLT Day   2,             !- CustomDay1 DAYSCHEDULE Name
    PLT Day   2;             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    WeekAllON,               !- Name
    DayAllON,                !- Sunday DAYSCHEDULE Name
    DayAllON,                !- Monday DAYSCHEDULE Name
    DayAllON,                !- Tuesday DAYSCHEDULE Name
    DayAllON,                !- Wednesday DAYSCHEDULE Name
    DayAllON,                !- Thursday DAYSCHEDULE Name
    DayAllON,                !- Friday DAYSCHEDULE Name
    DayAllON,                !- Saturday DAYSCHEDULE Name
    DayAllON,                !- Holiday DAYSCHEDULE Name
    DayAllON,                !- SummerDesignDay DAYSCHEDULE Name
    DayAllON,                !- WinterDesignDay DAYSCHEDULE Name
    DayAllON,                !- CustomDay1 DAYSCHEDULE Name
    DayAllON;                !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    WeekAllOFF,              !- Name
    DayAllOFF,               !- Sunday DAYSCHEDULE Name
    DayAllOFF,               !- Monday DAYSCHEDULE Name
    DayAllOFF,               !- Tuesday DAYSCHEDULE Name
    DayAllOFF,               !- Wednesday DAYSCHEDULE Name
    DayAllOFF,               !- Thursday DAYSCHEDULE Name
    DayAllOFF,               !- Friday DAYSCHEDULE Name
    DayAllOFF,               !- Saturday DAYSCHEDULE Name
    DayAllOFF,               !- Holiday DAYSCHEDULE Name
    DayAllOFF,               !- SummerDesignDay DAYSCHEDULE Name
    DayAllOFF,               !- WinterDesignDay DAYSCHEDULE Name
    DayAllOFF,               !- CustomDay1 DAYSCHEDULE Name
    DayAllOFF;               !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    TransWeekOn,             !- Name
    TransDayOn,              !- Sunday DAYSCHEDULE Name
    TransDayOn,              !- Monday DAYSCHEDULE Name
    TransDayOn,              !- Tuesday DAYSCHEDULE Name
    TransDayOn,              !- Wednesday DAYSCHEDULE Name
    TransDayOn,              !- Thursday DAYSCHEDULE Name
    TransDayOn,              !- Friday DAYSCHEDULE Name
    TransDayOn,              !- Saturday DAYSCHEDULE Name
    TransDayOn,              !- Holiday DAYSCHEDULE Name
    TransDayOn,              !- SummerDesignDay DAYSCHEDULE Name
    TransDayOn,              !- WinterDesignDay DAYSCHEDULE Name
    TransDayOn,              !- CustomDay1 DAYSCHEDULE Name
    TransDayOn;              !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    TransWeekOff,            !- Name
    TransDayOff,             !- Sunday DAYSCHEDULE Name
    TransDayOff,             !- Monday DAYSCHEDULE Name
    TransDayOff,             !- Tuesday DAYSCHEDULE Name
    TransDayOff,             !- Wednesday DAYSCHEDULE Name
    TransDayOff,             !- Thursday DAYSCHEDULE Name
    TransDayOff,             !- Friday DAYSCHEDULE Name
    TransDayOff,             !- Saturday DAYSCHEDULE Name
    TransDayOff,             !- Holiday DAYSCHEDULE Name
    TransDayOff,             !- SummerDesignDay DAYSCHEDULE Name
    TransDayOff,             !- WinterDesignDay DAYSCHEDULE Name
    TransDayOff,             !- CustomDay1 DAYSCHEDULE Name
    TransDayOff;             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Week on Peak,            !- Name
    Day On Peak,             !- Sunday DAYSCHEDULE Name
    Day On Peak,             !- Monday DAYSCHEDULE Name
    Day On Peak,             !- Tuesday DAYSCHEDULE Name
    Day On Peak,             !- Wednesday DAYSCHEDULE Name
    Day On Peak,             !- Thursday DAYSCHEDULE Name
    Day On Peak,             !- Friday DAYSCHEDULE Name
    Day On Peak,             !- Saturday DAYSCHEDULE Name
    Day On Peak,             !- Holiday DAYSCHEDULE Name
    Day On Peak,             !- SummerDesignDay DAYSCHEDULE Name
    Day On Peak,             !- WinterDesignDay DAYSCHEDULE Name
    Day On Peak,             !- CustomDay1 DAYSCHEDULE Name
    Day On Peak;             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Week Off Peak,           !- Name
    Day Off Peak,            !- Sunday DAYSCHEDULE Name
    Day Off Peak,            !- Monday DAYSCHEDULE Name
    Day Off Peak,            !- Tuesday DAYSCHEDULE Name
    Day Off Peak,            !- Wednesday DAYSCHEDULE Name
    Day Off Peak,            !- Thursday DAYSCHEDULE Name
    Day Off Peak,            !- Friday DAYSCHEDULE Name
    Day Off Peak,            !- Saturday DAYSCHEDULE Name
    Day Off Peak,            !- Holiday DAYSCHEDULE Name
    Day Off Peak,            !- SummerDesignDay DAYSCHEDULE Name
    Day Off Peak,            !- WinterDesignDay DAYSCHEDULE Name
    Day Off Peak,            !- CustomDay1 DAYSCHEDULE Name
    Day Off Peak;            !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    WeekON,                  !- Name
    DayON,                   !- Sunday DAYSCHEDULE Name
    DayON,                   !- Monday DAYSCHEDULE Name
    DayON,                   !- Tuesday DAYSCHEDULE Name
    DayON,                   !- Wednesday DAYSCHEDULE Name
    DayON,                   !- Thursday DAYSCHEDULE Name
    DayON,                   !- Friday DAYSCHEDULE Name
    DayON,                   !- Saturday DAYSCHEDULE Name
    DayON,                   !- Holiday DAYSCHEDULE Name
    DayON,                   !- SummerDesignDay DAYSCHEDULE Name
    DayON,                   !- WinterDesignDay DAYSCHEDULE Name
    DayON,                   !- CustomDay1 DAYSCHEDULE Name
    DayON;                   !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Summer Supply Air Temp Week Sch,
                             !- Name
    Summer Supply Air Temp Day Sch,
                             !- Sunday DAYSCHEDULE Name
    Summer Supply Air Temp Day Sch,
                             !- Monday DAYSCHEDULE Name
    Summer Supply Air Temp Day Sch,
                             !- Tuesday DAYSCHEDULE Name
    Summer Supply Air Temp Day Sch,
                             !- Wednesday DAYSCHEDULE Name
    Summer Supply Air Temp Day Sch,
                             !- Thursday DAYSCHEDULE Name
    Summer Supply Air Temp Day Sch,
                             !- Friday DAYSCHEDULE Name
    Summer Supply Air Temp Day Sch,
                             !- Saturday DAYSCHEDULE Name
    Summer Supply Air Temp Day Sch,
                             !- Holiday DAYSCHEDULE Name
    Summer Supply Air Temp Day Sch,
                             !- SummerDesignDay DAYSCHEDULE Name
    Summer Supply Air Temp Day Sch,
                             !- WinterDesignDay DAYSCHEDULE Name
    Summer Supply Air Temp Day Sch,
                             !- CustomDay1 DAYSCHEDULE Name
    Summer Supply Air Temp Day Sch;
                             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Winter Supply Air Temp Week Sch,
                             !- Name
    Winter Supply Air Temp Day Sch,
                             !- Sunday DAYSCHEDULE Name
    Winter Supply Air Temp Day Sch,
                             !- Monday DAYSCHEDULE Name
    Winter Supply Air Temp Day Sch,
                             !- Tuesday DAYSCHEDULE Name
    Winter Supply Air Temp Day Sch,
                             !- Wednesday DAYSCHEDULE Name
    Winter Supply Air Temp Day Sch,
                             !- Thursday DAYSCHEDULE Name
    Winter Supply Air Temp Day Sch,
                             !- Friday DAYSCHEDULE Name
    Winter Supply Air Temp Day Sch,
                             !- Saturday DAYSCHEDULE Name
    Winter Supply Air Temp Day Sch,
                             !- Holiday DAYSCHEDULE Name
    Winter Supply Air Temp Day Sch,
                             !- SummerDesignDay DAYSCHEDULE Name
    Winter Supply Air Temp Day Sch,
                             !- WinterDesignDay DAYSCHEDULE Name
    Winter Supply Air Temp Day Sch,
                             !- CustomDay1 DAYSCHEDULE Name
    Winter Supply Air Temp Day Sch;
                             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Chilled Water Loop Weekly,
                             !- Name
    Chilled Water Loop Daily,!- Sunday DAYSCHEDULE Name
    Chilled Water Loop Daily,!- Monday DAYSCHEDULE Name
    Chilled Water Loop Daily,!- Tuesday DAYSCHEDULE Name
    Chilled Water Loop Daily,!- Wednesday DAYSCHEDULE Name
    Chilled Water Loop Daily,!- Thursday DAYSCHEDULE Name
    Chilled Water Loop Daily,!- Friday DAYSCHEDULE Name
    Chilled Water Loop Daily,!- Saturday DAYSCHEDULE Name
    Chilled Water Loop Daily,!- Holiday DAYSCHEDULE Name
    Chilled Water Loop Daily,!- SummerDesignDay DAYSCHEDULE Name
    Chilled Water Loop Daily,!- WinterDesignDay DAYSCHEDULE Name
    Chilled Water Loop Daily,!- CustomDay1 DAYSCHEDULE Name
    Chilled Water Loop Daily;!- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Hot Water Loop Weekly,   !- Name
    Hot Water Loop Daily,    !- Sunday DAYSCHEDULE Name
    Hot Water Loop Daily,    !- Monday DAYSCHEDULE Name
    Hot Water Loop Daily,    !- Tuesday DAYSCHEDULE Name
    Hot Water Loop Daily,    !- Wednesday DAYSCHEDULE Name
    Hot Water Loop Daily,    !- Thursday DAYSCHEDULE Name
    Hot Water Loop Daily,    !- Friday DAYSCHEDULE Name
    Hot Water Loop Daily,    !- Saturday DAYSCHEDULE Name
    Hot Water Loop Daily,    !- Holiday DAYSCHEDULE Name
    Hot Water Loop Daily,    !- SummerDesignDay DAYSCHEDULE Name
    Hot Water Loop Daily,    !- WinterDesignDay DAYSCHEDULE Name
    Hot Water Loop Daily,    !- CustomDay1 DAYSCHEDULE Name
    Hot Water Loop Daily;    !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    FanAndCoilWinterWeekSched,
                             !- Name
    SystemOnDaySched,        !- Sunday DAYSCHEDULE Name
    SystemOnDaySched,        !- Monday DAYSCHEDULE Name
    SystemOnDaySched,        !- Tuesday DAYSCHEDULE Name
    SystemOnDaySched,        !- Wednesday DAYSCHEDULE Name
    SystemOnDaySched,        !- Thursday DAYSCHEDULE Name
    SystemOnDaySched,        !- Friday DAYSCHEDULE Name
    SystemOnDaySched,        !- Saturday DAYSCHEDULE Name
    SystemOnDaySched,        !- Holiday DAYSCHEDULE Name
    SystemOnDaySched,        !- SummerDesignDay DAYSCHEDULE Name
    SystemOnDaySched,        !- WinterDesignDay DAYSCHEDULE Name
    SystemOnDaySched,        !- CustomDay1 DAYSCHEDULE Name
    SystemOnDaySched;        !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    FanAndCoilSummerWeekSched,
                             !- Name
    SystemOffDaySched,       !- Sunday DAYSCHEDULE Name
    SystemOperatingDaySched, !- Monday DAYSCHEDULE Name
    SystemOperatingDaySched, !- Tuesday DAYSCHEDULE Name
    SystemOperatingDaySched, !- Wednesday DAYSCHEDULE Name
    SystemOperatingDaySched, !- Thursday DAYSCHEDULE Name
    SystemOperatingDaySched, !- Friday DAYSCHEDULE Name
    SystemOffDaySched,       !- Saturday DAYSCHEDULE Name
    SystemOffDaySched,       !- Holiday DAYSCHEDULE Name
    SystemOffDaySched,       !- SummerDesignDay DAYSCHEDULE Name
    SystemOffDaySched,       !- WinterDesignDay DAYSCHEDULE Name
    SystemOffDaySched,       !- CustomDay1 DAYSCHEDULE Name
    SystemOffDaySched;       !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    FanAndCoilAllOffWeekSched,
                             !- Name
    SystemOffDaySched,       !- Sunday DAYSCHEDULE Name
    SystemOffDaySched,       !- Monday DAYSCHEDULE Name
    SystemOffDaySched,       !- Tuesday DAYSCHEDULE Name
    SystemOffDaySched,       !- Wednesday DAYSCHEDULE Name
    SystemOffDaySched,       !- Thursday DAYSCHEDULE Name
    SystemOffDaySched,       !- Friday DAYSCHEDULE Name
    SystemOffDaySched,       !- Saturday DAYSCHEDULE Name
    SystemOffDaySched,       !- Holiday DAYSCHEDULE Name
    SystemOffDaySched,       !- SummerDesignDay DAYSCHEDULE Name
    SystemOffDaySched,       !- WinterDesignDay DAYSCHEDULE Name
    SystemOffDaySched,       !- CustomDay1 DAYSCHEDULE Name
    SystemOffDaySched;       !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Summer Zone Temp Lo Week Sch,
                             !- Name
    Summer Zone Temp Lo Day Sch,
                             !- Sunday DAYSCHEDULE Name
    Summer Zone Temp Lo Day Sch,
                             !- Monday DAYSCHEDULE Name
    Summer Zone Temp Lo Day Sch,
                             !- Tuesday DAYSCHEDULE Name
    Summer Zone Temp Lo Day Sch,
                             !- Wednesday DAYSCHEDULE Name
    Summer Zone Temp Lo Day Sch,
                             !- Thursday DAYSCHEDULE Name
    Summer Zone Temp Lo Day Sch,
                             !- Friday DAYSCHEDULE Name
    Summer Zone Temp Lo Day Sch,
                             !- Saturday DAYSCHEDULE Name
    Summer Zone Temp Lo Day Sch,
                             !- Holiday DAYSCHEDULE Name
    Summer Zone Temp Lo Day Sch,
                             !- SummerDesignDay DAYSCHEDULE Name
    Summer Zone Temp Lo Day Sch,
                             !- WinterDesignDay DAYSCHEDULE Name
    Summer Zone Temp Lo Day Sch,
                             !- CustomDay1 DAYSCHEDULE Name
    Summer Zone Temp Lo Day Sch;
                             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Winter Zone Temp Lo Week Sch,
                             !- Name
    Winter Zone Temp Lo Day Sch,
                             !- Sunday DAYSCHEDULE Name
    Winter Zone Temp Lo Day Sch,
                             !- Monday DAYSCHEDULE Name
    Winter Zone Temp Lo Day Sch,
                             !- Tuesday DAYSCHEDULE Name
    Winter Zone Temp Lo Day Sch,
                             !- Wednesday DAYSCHEDULE Name
    Winter Zone Temp Lo Day Sch,
                             !- Thursday DAYSCHEDULE Name
    Winter Zone Temp Lo Day Sch,
                             !- Friday DAYSCHEDULE Name
    Winter Zone Temp Lo Day Sch,
                             !- Saturday DAYSCHEDULE Name
    Winter Zone Temp Lo Day Sch,
                             !- Holiday DAYSCHEDULE Name
    Winter Zone Temp Lo Day Sch,
                             !- SummerDesignDay DAYSCHEDULE Name
    Winter Zone Temp Lo Day Sch,
                             !- WinterDesignDay DAYSCHEDULE Name
    Winter Zone Temp Lo Day Sch,
                             !- CustomDay1 DAYSCHEDULE Name
    Winter Zone Temp Lo Day Sch;
                             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Summer Zone Temp Hi Week Sch,
                             !- Name
    Summer Zone Temp Hi Day Sch,
                             !- Sunday DAYSCHEDULE Name
    Summer Zone Temp Hi Day Sch,
                             !- Monday DAYSCHEDULE Name
    Summer Zone Temp Hi Day Sch,
                             !- Tuesday DAYSCHEDULE Name
    Summer Zone Temp Hi Day Sch,
                             !- Wednesday DAYSCHEDULE Name
    Summer Zone Temp Hi Day Sch,
                             !- Thursday DAYSCHEDULE Name
    Summer Zone Temp Hi Day Sch,
                             !- Friday DAYSCHEDULE Name
    Summer Zone Temp Hi Day Sch,
                             !- Saturday DAYSCHEDULE Name
    Summer Zone Temp Hi Day Sch,
                             !- Holiday DAYSCHEDULE Name
    Summer Zone Temp Hi Day Sch,
                             !- SummerDesignDay DAYSCHEDULE Name
    Summer Zone Temp Hi Day Sch,
                             !- WinterDesignDay DAYSCHEDULE Name
    Summer Zone Temp Hi Day Sch,
                             !- CustomDay1 DAYSCHEDULE Name
    Summer Zone Temp Hi Day Sch;
                             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Winter Zone Temp Hi Week Sch,
                             !- Name
    Winter Zone Temp Hi Day Sch,
                             !- Sunday DAYSCHEDULE Name
    Winter Zone Temp Hi Day Sch,
                             !- Monday DAYSCHEDULE Name
    Winter Zone Temp Hi Day Sch,
                             !- Tuesday DAYSCHEDULE Name
    Winter Zone Temp Hi Day Sch,
                             !- Wednesday DAYSCHEDULE Name
    Winter Zone Temp Hi Day Sch,
                             !- Thursday DAYSCHEDULE Name
    Winter Zone Temp Hi Day Sch,
                             !- Friday DAYSCHEDULE Name
    Winter Zone Temp Hi Day Sch,
                             !- Saturday DAYSCHEDULE Name
    Winter Zone Temp Hi Day Sch,
                             !- Holiday DAYSCHEDULE Name
    Winter Zone Temp Hi Day Sch,
                             !- SummerDesignDay DAYSCHEDULE Name
    Winter Zone Temp Hi Day Sch,
                             !- WinterDesignDay DAYSCHEDULE Name
    Winter Zone Temp Hi Day Sch,
                             !- CustomDay1 DAYSCHEDULE Name
    Winter Zone Temp Hi Day Sch;
                             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Summer Control Type Week Sch,
                             !- Name
    Summer Control Type Day Sch,
                             !- Sunday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Monday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Tuesday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Wednesday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Thursday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Friday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Saturday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Holiday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- SummerDesignDay DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- WinterDesignDay DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- CustomDay1 DAYSCHEDULE Name
    Summer Control Type Day Sch;
                             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Winter Control Type Week Sch,
                             !- Name
    Winter Control Type Day Sch,
                             !- Sunday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Monday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Tuesday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Wednesday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Thursday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Friday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Saturday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Holiday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- SummerDesignDay DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- WinterDesignDay DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- CustomDay1 DAYSCHEDULE Name
    Winter Control Type Day Sch;
                             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    nighttimeventweek,       !- Name
    nightventilday,          !- Sunday DAYSCHEDULE Name
    nightventilday,          !- Monday DAYSCHEDULE Name
    nightventilday,          !- Tuesday DAYSCHEDULE Name
    nightventilday,          !- Wednesday DAYSCHEDULE Name
    nightventilday,          !- Thursday DAYSCHEDULE Name
    nightventilday,          !- Friday DAYSCHEDULE Name
    nightventilday,          !- Saturday DAYSCHEDULE Name
    nightventilday,          !- Holiday DAYSCHEDULE Name
    nightventilday,          !- SummerDesignDay DAYSCHEDULE Name
    nightventilday,          !- WinterDesignDay DAYSCHEDULE Name
    nightventilday,          !- CustomDay1 DAYSCHEDULE Name
    nightventilday;          !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    lightweekschedual,       !- Name
    lightday,                !- Sunday DAYSCHEDULE Name
    lightday,                !- Monday DAYSCHEDULE Name
    lightday,                !- Tuesday DAYSCHEDULE Name
    lightday,                !- Wednesday DAYSCHEDULE Name
    lightday,                !- Thursday DAYSCHEDULE Name
    lightday,                !- Friday DAYSCHEDULE Name
    lightday,                !- Saturday DAYSCHEDULE Name
    lightday,                !- Holiday DAYSCHEDULE Name
    lightday,                !- SummerDesignDay DAYSCHEDULE Name
    lightday,                !- WinterDesignDay DAYSCHEDULE Name
    lightday,                !- CustomDay1 DAYSCHEDULE Name
    lightday;                !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    nighttimeventweekh,      !- Name
    nightventildayh,         !- Sunday DAYSCHEDULE Name
    nightventildayh,         !- Monday DAYSCHEDULE Name
    nightventildayh,         !- Tuesday DAYSCHEDULE Name
    nightventildayh,         !- Wednesday DAYSCHEDULE Name
    nightventildayh,         !- Thursday DAYSCHEDULE Name
    nightventildayh,         !- Friday DAYSCHEDULE Name
    nightventildayh,         !- Saturday DAYSCHEDULE Name
    nightventildayh,         !- Holiday DAYSCHEDULE Name
    nightventildayh,         !- SummerDesignDay DAYSCHEDULE Name
    nightventildayh,         !- WinterDesignDay DAYSCHEDULE Name
    nightventildayh,         !- CustomDay1 DAYSCHEDULE Name
    nightventildayh;         !- CustomDay2 DAYSCHEDULE Name
!-   ===========  ALL OBJECTS IN CLASS: SCHEDULE ===========
SCHEDULE,
    Activity Sch,            !- Name
    Any Number,              !- ScheduleType
    ActLevWeek,              !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    Work Eff Sch,            !- Name
    Any Number,              !- ScheduleType
    WorkEffWeek,             !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    Clothing Sch,            !- Name
    Any Number,              !- ScheduleType
    CloInsWeek,              !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    Air Velo Sch,            !- Name
    Any Number,              !- ScheduleType
    AirVelWeek,              !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    BLDG Sch   1,            !- Name
    Any Number,              !- ScheduleType
    OFFICE OCCUPANCY,        !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    BLDG Sch   2,            !- Name
    Any Number,              !- ScheduleType
    INTERMITTENT,            !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    BLDG Sch   3,            !- Name
    Any Number,              !- ScheduleType
    OFFICE LIGHTING,         !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    ReportSch,               !- Name
    on/off,                  !- ScheduleType
    WeekAllON,               !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    5,                       !- End Month 1
    5,                       !- End Day 1
    WeekAllON,               !- Name of WEEKSCHEDULE 2
    5,                       !- Start Month 2
    6,                       !- Start Day 2
    5,                       !- End Month 2
    8,                       !- End Day 2
    WeekAllON,               !- Name of WEEKSCHEDULE 3
    5,                       !- Start Month 3
    9,                       !- Start Day 3
    12,                      !- End Month 3
    31;                      !- End Day 3
SCHEDULE,
    TransOn,                 !- Name
    Fraction,                !- ScheduleType
    TransWeekOn,             !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    On Peak,                 !- Name
    Fraction,                !- ScheduleType
    Week On Peak,            !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    Off Peak,                !- Name
    Fraction,                !- ScheduleType
    Week Off Peak,           !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    ON,                      !- Name
    Fraction,                !- ScheduleType
    WeekON,                  !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    Seasonal Reset Supply Air Temp Sch,
                             !- Name
    Temperature,             !- ScheduleType
    Winter Supply Air Temp Week Sch,
                             !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    3,                       !- End Month 1
    31,                      !- End Day 1
    Summer Supply Air Temp Week Sch,
                             !- Name of WEEKSCHEDULE 2
    4,                       !- Start Month 2
    1,                       !- Start Day 2
    9,                       !- End Month 2
    30,                      !- End Day 2
    Winter Supply Air Temp Week Sch,
                             !- Name of WEEKSCHEDULE 3
    10,                      !- Start Month 3
    1,                       !- Start Day 3
    12,                      !- End Month 3
    31;                      !- End Day 3
SCHEDULE,
    CW Loop Temp Schedule,   !- Name
    Temperature,             !- ScheduleType
    Chilled Water Loop Weekly,
                             !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    HW Loop Temp Schedule,   !- Name
    Temperature,             !- ScheduleType
    Hot Water Loop Weekly,   !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    FanAndCoilAvailSched,    !- Name
    Fraction,                !- ScheduleType
    FanAndCoilWinterWeekSched,
                             !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    3,                       !- End Month 1
    31,                      !- End Day 1
    FanAndCoilSummerWeekSched,
                             !- Name of WEEKSCHEDULE 2
    4,                       !- Start Month 2
    1,                       !- Start Day 2
    9,                       !- End Month 2
    30,                      !- End Day 2
    FanAndCoilWinterWeekSched,
                             !- Name of WEEKSCHEDULE 3
    10,                      !- Start Month 3
    1,                       !- Start Day 3
    12,                      !- End Month 3
    31;                      !- End Day 3
SCHEDULE,
    CoolingCoilAvailSched,   !- Name
    Fraction,                !- ScheduleType
    FanAndCoilAllOffWeekSched,
                             !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    3,                       !- End Month 1
    31,                      !- End Day 1
    FanAndCoilSummerWeekSched,
                             !- Name of WEEKSCHEDULE 2
    4,                       !- Start Month 2
    1,                       !- Start Day 2
    9,                       !- End Month 2
    30,                      !- End Day 2
    FanAndCoilAllOffWeekSched,
                             !- Name of WEEKSCHEDULE 3
    10,                      !- Start Month 3
    1,                       !- Start Day 3
    12,                      !- End Month 3
    31;                      !- End Day 3
SCHEDULE,
    Heating Setpoints,       !- Name
    Temperature,             !- ScheduleType
    Winter Zone Temp Lo Week Sch,
                             !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    3,                       !- End Month 1
    31,                      !- End Day 1
    Summer Zone Temp Lo Week Sch,
                             !- Name of WEEKSCHEDULE 2
    4,                       !- Start Month 2
    1,                       !- Start Day 2
    9,                       !- End Month 2
    30,                      !- End Day 2
    Winter Zone Temp Lo Week Sch,
                             !- Name of WEEKSCHEDULE 3
    10,                      !- Start Month 3
    1,                       !- Start Day 3
    12,                      !- End Month 3
    31;                      !- End Day 3
SCHEDULE,
    Cooling Setpoints,       !- Name
    Temperature,             !- ScheduleType
    Winter Zone Temp Hi Week Sch,
                             !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    3,                       !- End Month 1
    31,                      !- End Day 1
    Summer Zone Temp Hi Week Sch,
                             !- Name of WEEKSCHEDULE 2
    4,                       !- Start Month 2
    1,                       !- Start Day 2
    9,                       !- End Month 2
    30,                      !- End Day 2
    Winter Zone Temp Hi Week Sch,
                             !- Name of WEEKSCHEDULE 3
    10,                      !- Start Month 3
    1,                       !- Start Day 3
    12,                      !- End Month 3
    31;                      !- End Day 3
SCHEDULE,
    Zone Control Type Sched, !- Name
    Control Type,            !- ScheduleType
    Winter Control Type Week Sch,
                             !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    3,                       !- End Month 1
    31,                      !- End Day 1
    Summer Control Type Week Sch,
                             !- Name of WEEKSCHEDULE 2
    4,                       !- Start Month 2
    1,                       !- Start Day 2
    9,                       !- End Month 2
    30,                      !- End Day 2
    Winter Control Type Week Sch,
                             !- Name of WEEKSCHEDULE 3
    10,                      !- Start Month 3
    1,                       !- Start Day 3
    12,                      !- End Month 3
    31;                      !- End Day 3
SCHEDULE,
    FanSched1,               !- Name
    ON/OFF,                  !- ScheduleType
    SYS-HOSPITAL EQUIPMENT,  !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    ReheatSched1,            !- Name
    ON/OFF,                  !- ScheduleType
    SYS-ON,                  !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    12,                      !- End Month 1
    31;                      !- End Day 1
SCHEDULE,
    nightventilation,        !- Name
    ON/OFF,                  !- ScheduleType
    nighttimeventweek,       !- Name of WEEKSCHEDULE 1
    6,                       !- Start Month 1
    1,                       !- Start Day 1
    10,                      !- End Month 1
    31,                      !- End Day 1
    WeekAllOFF,              !- Name of WEEKSCHEDULE 2
    1,                       !- Start Month 2
    1,                       !- Start Day 2
    5,                       !- End Month 2
    31,                      !- End Day 2
    WeekAllOFF,              !- Name of WEEKSCHEDULE 3
    11,                      !- Start Month 3
    1,                       !- Start Day 3
    12,                      !- End Month 3
    31;                      !- End Day 3
SCHEDULE,
    nightventilationh,       !- Name
    ON/OFF,                  !- ScheduleType
    nighttimeventweekh,      !- Name of WEEKSCHEDULE 1
    6,                       !- Start Month 1
    1,                       !- Start Day 1
    10,                      !- End Month 1
    31,                      !- End Day 1
    WeekAllOFF,              !- Name of WEEKSCHEDULE 2
    1,                       !- Start Month 2
    1,                       !- Start Day 2
    5,                       !- End Month 2
    31,                      !- End Day 2
    WeekAllOFF,              !- Name of WEEKSCHEDULE 3
    11,                      !- Start Month 3
    1,                       !- Start Day 3
    12,                      !- End Month 3
    31;                      !- End Day 3
!-   ===========  ALL OBJECTS IN CLASS: PEOPLE ===========
PEOPLE,
!                                                                                                                                                            Int Gain Type and Zone
    RESISTIVE ZONE,          !- Zone Name
!                                                                                                                                                            "Maximum" Number of People
    0,                       !- Number of People
!                                                                                                                                                            Occupancy Schedule
    ON,                      !- Number of People SCHEDULE Name (real--fraction)
!                                                                                                                                                            Fraction Radiant
    0.3,                     !- Fraction Radiant
!                                                                                                                                                            Activity Level Schedule Name
    Activity Sch,            !- Activity level SCHEDULE Name (units W/person, real)
!                                                                                                                                                            Take default name for people (Zone Name)
    ,                        !- PEOPLE Group Name
!                                                                                                                                                            MRT calculation type
    zoneaveraged,            !- MRT Calculation Type
!                                                                                                                                                            Surface name
    ,                        !- Surface Name
!                                                                                                                                                            Work Efficiency Schedule Name
    Work Eff Sch,            !- Work Efficiency SCHEDULE Name (0.0-1.0,real)
!                                                                                                                                                            Clothing Insulation Schedule
    Clothing Sch,            !- Clothing Insulation SCHEDULE Name (real)
!                                                                                                                                                            Air Velocity Schedule
    Air Velo Sch,            !- Air Velocity SCHEDULE Name (units m/s, real)
!                                                                                                                                                            Calculate Thermal Comfort Using Fanger Model
    FANGER      ,            !- Thermal Comfort Report Type
!                                                                                                                                                            Calculate Thermal Comfort Using Pierce Model
    PIERCE      ,            !- Thermal Comfort Report Type
!                                                                                                                                                            Calculate Thermal Comfort Using KSU Model
    KSU         ;            !- Thermal Comfort Report Type
PEOPLE,
!                                                                                                                                                            Int Gain Type and Zone
    EAST ZONE,               !- Zone Name
!                                                                                                                                                            "Maximum" Number of People
    0,                       !- Number of People
!                                                                                                                                                            Occupancy Schedule
    ON,                      !- Number of People SCHEDULE Name (real--fraction)
!                                                                                                                                                            Fraction Radiant
    0.3,                     !- Fraction Radiant
!                                                                                                                                                            Activity Level Schedule Name
    Activity Sch,            !- Activity level SCHEDULE Name (units W/person, real)
!                                                                                                                                                            Take default name for people (Zone Name)
    ,                        !- PEOPLE Group Name
!                                                                                                                                                            MRT calculation type
    zoneaveraged,            !- MRT Calculation Type
!                                                                                                                                                            Surface name
    ,                        !- Surface Name
!                                                                                                                                                            Work Efficiency Schedule Name
    Work Eff Sch,            !- Work Efficiency SCHEDULE Name (0.0-1.0,real)
!                                                                                                                                                            Clothing Insulation Schedule
    Clothing Sch,            !- Clothing Insulation SCHEDULE Name (real)
!                                                                                                                                                            Air Velocity Schedule
    Air Velo Sch,            !- Air Velocity SCHEDULE Name (units m/s, real)
!                                                                                                                                                            Calculate Thermal Comfort Using Fanger Model
    FANGER      ,            !- Thermal Comfort Report Type
!                                                                                                                                                            Calculate Thermal Comfort Using KSU Model
    KSU         ;            !- Thermal Comfort Report Type
PEOPLE,
!                                                                                                                                                            Int Gain Type and Zone
    NORTH ZONE,              !- Zone Name
!                                                                                                                                                            "Maximum" Number of People
    0,                       !- Number of People
!                                                                                                                                                            Occupancy Schedule
    ON,                      !- Number of People SCHEDULE Name (real--fraction)
!                                                                                                                                                            Fraction Radiant
    0.3,                     !- Fraction Radiant
!                                                                                                                                                            Activity Level Schedule Name
    Activity Sch,            !- Activity level SCHEDULE Name (units W/person, real)
!                                                                                                                                                            Take default name for people (Zone Name)
    ,                        !- PEOPLE Group Name
!                                                                                                                                                            MRT calculation type
    zoneaveraged,            !- MRT Calculation Type
!                                                                                                                                                            Surface name
    ,                        !- Surface Name
!                                                                                                                                                            Work Efficiency Schedule Name
    Work Eff Sch,            !- Work Efficiency SCHEDULE Name (0.0-1.0,real)
!                                                                                                                                                            Clothing Insulation Schedule
    Clothing Sch,            !- Clothing Insulation SCHEDULE Name (real)
!                                                                                                                                                            Air Velocity Schedule
    Air Velo Sch,            !- Air Velocity SCHEDULE Name (units m/s, real)
!                                                                                                                                                            Calculate Thermal Comfort Using Fanger Model
    FANGER      ;            !- Thermal Comfort Report Type
!-   ===========  ALL OBJECTS IN CLASS: LIGHTS ===========
LIGHTS,
!                                                                                                                                                            Int Gain Type, Zone, and Schedule
    EAST ZONE,               !- Zone Name
    BLDG Sch   1,            !- SCHEDULE Name
!                                                                                                                                                            Design Level {w}
    150,                     !- Design Level {W}
!                                                                                                                                                            Return Air Fraction
    0,                       !- Return Air Fraction
!                                                                                                                                                            Fraction Radiant
    0.2,                     !- Fraction Radiant
!                                                                                                                                                            Fraction Visible
    0.2,                     !- Fraction Visible
!                                                                                                                                                            Fraction Replaceable
    0;                       !- Fraction Replaceable
LIGHTS,
!                                                                                                                                                            Int Gain Type, Zone, and Schedule
    EAST ZONE,               !- Zone Name
    BLDG Sch   1,            !- SCHEDULE Name
!                                                                                                                                                            Design Level {w}
    150,                     !- Design Level {W}
!                                                                                                                                                            Return Air Fraction
    0,                       !- Return Air Fraction
!                                                                                                                                                            Fraction Radiant
    0.2,                     !- Fraction Radiant
!                                                                                                                                                            Fraction Visible
    0.2,                     !- Fraction Visible
!                                                                                                                                                            Fraction Replaceable
    0;                       !- Fraction Replaceable
LIGHTS,
    NORTH ZONE,              !- Zone Name
    BLDG Sch   1,            !- SCHEDULE Name
    150,                     !- Design Level {W}
    0,                       !- Return Air Fraction
    0.2,                     !- Fraction Radiant
    0.2,                     !- Fraction Visible
    0;                       !- Fraction Replaceable
!-   ===========  ALL OBJECTS IN CLASS: ELECTRIC EQUIPMENT ===========
ELECTRIC EQUIPMENT,
!                                                                                                                                                            Int Gain Type, Zone, and Schedule
    RESISTIVE ZONE,          !- Zone Name
    ON,                      !- SCHEDULE Name
!                                                                                                                                                            Design Level {w}
    1,                       !- Design Level {W}
!                                                                                                                                                            Fraction Latent
    0.8,                     !- Fraction Latent
!                                                                                                                                                            Fraction Radiant
    0.1,                     !- Fraction Radiant
!                                                                                                                                                            Fraction Lost
    0;                       !- Fraction Lost
ELECTRIC EQUIPMENT,
!                                                                                                                                                            Int Gain Type, Zone, and Schedule
    EAST ZONE,               !- Zone Name
    ON,                      !- SCHEDULE Name
!                                                                                                                                                            Design Level {w}
    1,                       !- Design Level {W}
!                                                                                                                                                            Fraction Latent
    0.8,                     !- Fraction Latent
!                                                                                                                                                            Fraction Radiant
    0.1,                     !- Fraction Radiant
!                                                                                                                                                            Fraction Lost
    0;                       !- Fraction Lost
ELECTRIC EQUIPMENT,
!                                                                                                                                                            Int Gain Type, Zone, and Schedule
    NORTH ZONE,              !- Zone Name
    ON,                      !- SCHEDULE Name
!                                                                                                                                                            Design Level {w}
    1,                       !- Design Level {W}
!                                                                                                                                                            Fraction Latent
    0.8,                     !- Fraction Latent
!                                                                                                                                                            Fraction Radiant
    0.1,                     !- Fraction Radiant
!                                                                                                                                                            Fraction Lost
    0;                       !- Fraction Lost
!-   ===========  ALL OBJECTS IN CLASS: INFILTRATION ===========
INFILTRATION,
    RESISTIVE ZONE,          !- Zone Name
    Work Eff Sch,            !- SCHEDULE Name
    1.866,                   !- Design Volume Flow Rate {m3/s}
    0.606,                   !- Constant Term Coefficient
    0.0363599,               !- Temperature Term Coefficient
    0.1177716,               !- Velocity Term Coefficient
    0;                       !- Velocity Squared Term Coefficient
INFILTRATION,
    EAST ZONE,               !- Zone Name
    Work Eff Sch,            !- SCHEDULE Name
    1.86666,                 !- Design Volume Flow Rate {m3/s}
    0.606,                   !- Constant Term Coefficient
    0.0363599,               !- Temperature Term Coefficient
    0.1177716,               !- Velocity Term Coefficient
    0;                       !- Velocity Squared Term Coefficient
INFILTRATION,
    NORTH ZONE,              !- Zone Name
    Work Eff Sch,            !- SCHEDULE Name
    1.86666,                 !- Design Volume Flow Rate {m3/s}
    0.606,                   !- Constant Term Coefficient
    0.0363599,               !- Temperature Term Coefficient
    0.1177716,               !- Velocity Term Coefficient
    0;                       !- Velocity Squared Term Coefficient
!-   ===========  ALL OBJECTS IN CLASS: NODE LIST ===========
NODE LIST,
    OutsideAirInletNodes,    !- Node List Name
    Outside Air Inlet Node,  !- Node_ID_1
    Outside Air Inlet Node 2;!- Node_ID_2
NODE LIST,
    Zone1Inlets,             !- Node List Name
    Zone 1 Reheat Air Outlet Node;
                             !- Node_ID_1
NODE LIST,
    Zone2Inlets,             !- Node List Name
    Zone 2 Reheat Air Outlet Node;
                             !- Node_ID_1
NODE LIST,
    Zone3Inlets,             !- Node List Name
    Zone 3 Reheat Air Outlet Node;
                             !- Node_ID_1
NODE LIST,
    Supply Air Temp Nodes,   !- Node List Name
!                                                                                                            Set Point Node
    Air Loop Outlet Node;    !- Node_ID_1
NODE LIST,
    Mixed Air Nodes,         !- Node List Name
    Mixed Air Node;          !- Node_ID_1
!-   ===========  ALL OBJECTS IN CLASS: BRANCH LIST ===========
BRANCH LIST,
    Air Loop Branches,       !- Branch List Name
    Air Loop Main Branch;    !- Branch Name 1
BRANCH LIST,
    Cooling Supply Side Branches,
                             !- Branch List Name
    CW Pump Branch,          !- Branch Name 1
    Little Chiller Branch,   !- Branch Name 2
    Big Chiller Branch,      !- Branch Name 3
    Purchased Cooling Branch,!- Branch Name 4
    Supply Bypass Branch,    !- Branch Name 5
    Cooling Supply Outlet;   !- Branch Name 6
BRANCH LIST,
    Cooling Demand Side Branches,
                             !- Branch List Name
    Cooling Demand Inlet,    !- Branch Name 1
    Cooling Coil Branch,     !- Branch Name 2
    Demand Bypass Branch,    !- Branch Name 3
    Cooling Demand Outlet;   !- Branch Name 4
BRANCH LIST,
    Condenser Supply Side Branches,
                             !- Branch List Name
    Condenser Supply Inlet Branch,
                             !- Branch Name 1
    Condenser Supply Tower Branch,
                             !- Branch Name 2
    Condenser Supply Bypass Branch,
                             !- Branch Name 3
    Condenser Supply Outlet Branch;
                             !- Branch Name 4
BRANCH LIST,
    Condenser Demand Side Branches,
                             !- Branch List Name
    Condenser Demand Inlet Branch,
                             !- Branch Name 1
    Little Chiller Condenser Branch,
                             !- Branch Name 2
    Big Chiller Condenser Branch,
                             !- Branch Name 3
    Condenser Demand Bypass Branch,
                             !- Branch Name 4
    Condenser Demand Outlet Branch;
                             !- Branch Name 5
BRANCH LIST,
    Heating Supply Side Branches,
                             !- Branch List Name
    Heating Supply Inlet Branch,
                             !- Branch Name 1
    Heating Purchased Hot Water Branch,
                             !- Branch Name 2
    Heating Supply Bypass Branch,
                             !- Branch Name 3
    Heating Supply Outlet Branch;
                             !- Branch Name 4
BRANCH LIST,
    Heating Demand Side Branches,
                             !- Branch List Name
    Reheat Inlet Branch,     !- Branch Name 1
    Zone 1 Reheat Branch,    !- Branch Name 2
    Zone 2 Reheat Branch,    !- Branch Name 3
    Zone 3 Reheat Branch,    !- Branch Name 4
    Reheat Bypass Branch,    !- Branch Name 5
    Reheat Outlet Branch;    !- Branch Name 6
!-   ===========  ALL OBJECTS IN CLASS: CONNECTOR LIST ===========
CONNECTOR LIST,
    Cooling Supply Side Connectors,
                             !- Connector List Name
    SPLITTER,                !- Type of Connector 1
    CW Loop Splitter,        !- Name of Connector 1
    MIXER,                   !- Type of Connector 2
    CW Loop Mixer;           !- Name of Connector 2
CONNECTOR LIST,
    Cooling Demand Side Connectors,
                             !- Connector List Name
    SPLITTER,                !- Type of Connector 1
    CW Demand Splitter,      !- Name of Connector 1
    MIXER,                   !- Type of Connector 2
    CW Demand Mixer;         !- Name of Connector 2
CONNECTOR LIST,
    Condenser Supply Side Connectors,
                             !- Connector List Name
    SPLITTER,                !- Type of Connector 1
    Condenser Supply Splitter,
                             !- Name of Connector 1
    MIXER,                   !- Type of Connector 2
    Condenser Supply Mixer;  !- Name of Connector 2
CONNECTOR LIST,
    Condenser Demand Side Connectors,
                             !- Connector List Name
    SPLITTER,                !- Type of Connector 1
    Condenser Demand Splitter,
                             !- Name of Connector 1
    MIXER,                   !- Type of Connector 2
    Condenser Demand Mixer;  !- Name of Connector 2
CONNECTOR LIST,
    Heating Supply Side Connectors,
                             !- Connector List Name
    SPLITTER,                !- Type of Connector 1
    Heating Supply Splitter, !- Name of Connector 1
    MIXER,                   !- Type of Connector 2
    Heating Supply Mixer;    !- Name of Connector 2
CONNECTOR LIST,
    Heating Demand Side Connectors,
                             !- Connector List Name
    SPLITTER,                !- Type of Connector 1
    Reheat Splitter,         !- Name of Connector 1
    MIXER,                   !- Type of Connector 2
    Reheat Mixer;            !- Name of Connector 2
!-   ===========  ALL OBJECTS IN CLASS: BRANCH ===========
BRANCH,
!                                                                                                                BRANCH, Air Loop Main Branch,
!                                                                                                                      1.3,
!                                                                                                                      OUTSIDE AIR SYSTEM, OA Sys 1,
!                                                                                                                      Air Loop Inlet Node, Mixed Air Node,PASSIVE,
!                                                                                                                      FAN:SIMPLE:ConstVolume, Supply Fan 1,
!                                                                                                                      Mixed Air Node, Cooling Coil Air Inlet Node, ACTIVE,
!                                                                                                                      COIL:Water:DetailedFlatCooling, Detailed Cooling Coil,
!                                                                                                                      Cooling Coil Air Inlet Node, Air Loop Outlet Node, PASSIVE;
! 
!                                                                                                               FAN:SIMPLE:ConstVolume,
!                                                                                                                 Supply Fan 1,  !Fan Name
!                                                                                                                 FanAndCoilAvailSched,        !Fan Schedule
!                                                                                                                 0.7,           !Fan Efficiency
!                                                                                                                 600.0,         !Delta Pressure [N/M^2]
!                                                                                                                 1.3,           !Max Vol Flow Rate  [m^3/Sec]
!                                                                                                                 0.9,           !motor efficiency
!                                                                                                                 1.0,           !motor in air stream fraction
!                                                                                                                 Mixed Air Node,
!                                                                                                                 Cooling Coil Air Inlet Node;          !Inlet Node, Outlet Node
    Air Loop Main Branch,    !- Branch Name
    6,                       !- Maximum Branch Flow Rate {m3/s}
    OUTSIDE AIR SYSTEM,      !- Comp1 Type
    OA Sys 1,                !- Comp1 Name
    Air Loop Inlet Node,     !- Comp1 Inlet Node Name
    Mixed Air Node,          !- Comp1 Outlet Node Name
    PASSIVE,                 !- Comp1 Branch Control Type
    FAN:SIMPLE:ConstVolume,  !- Comp2 Type
    Supply Fan 1,            !- Comp2 Name
    Mixed Air Node,          !- Comp2 Inlet Node Name
    Cooling Coil Air Inlet Node 1,
                             !- Comp2 Outlet Node Name
    ACTIVE,                  !- Comp2 Branch Control Type
    EvapCooler:InDirect:CelDekPad,
                             !- Comp3 Type
    evaporative 1,           !- Comp3 Name
    Cooling Coil Air Inlet Node 1,
                             !- Comp3 Inlet Node Name
    Cooling Coil Air Inlet Node,
                             !- Comp3 Outlet Node Name
    ACTIVE,                  !- Comp3 Branch Control Type
    COIL:Water:DetailedFlatCooling,
                             !- Comp4 Type
    Detailed Cooling Coil,   !- Comp4 Name
    Cooling Coil Air Inlet Node,
                             !- Comp4 Inlet Node Name
    Air Loop Outlet Node,    !- Comp4 Outlet Node Name
    PASSIVE;                 !- Comp4 Branch Control Type
BRANCH,
    Cooling Demand Inlet,    !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Demand Side Inlet Pipe,  !- Comp1 Name
    CW Demand Inlet Node,    !- Comp1 Inlet Node Name
    CW Demand Entrance Pipe Outlet Node,
                             !- Comp1 Outlet Node Name
!                                                                                                           inlet to loop
    PASSIVE;                 !- Comp1 Branch Control Type
BRANCH,
    Cooling Coil Branch,     !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    COIL:Water:DetailedFlatCooling,
                             !- Comp1 Type
    Detailed Cooling Coil,   !- Comp1 Name
    Cooling Coil Water Inlet Node,
                             !- Comp1 Inlet Node Name
    Cooling Coil Water Outlet Node,
                             !- Comp1 Outlet Node Name
    Active;                  !- Comp1 Branch Control Type
BRANCH,
    Demand Bypass Branch,    !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Demand Side Bypass,      !- Comp1 Name
    CW Demand Bypass Inlet Node,
                             !- Comp1 Inlet Node Name
    CW Demand Bypass Outlet Node,
                             !- Comp1 Outlet Node Name
!                                                                                                           inlet to loop
    BYPASS;                  !- Comp1 Branch Control Type
BRANCH,
    Cooling Demand Outlet,   !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    CW Demand Side Outlet Pipe,
                             !- Comp1 Name
    CW Demand Exit Pipe Inlet Node,
                             !- Comp1 Inlet Node Name
    CW Demand Outlet Node,   !- Comp1 Outlet Node Name
!                                                                                                           outlet to loop
    PASSIVE;                 !- Comp1 Branch Control Type
BRANCH,
    Cooling Supply Outlet,   !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Supply Side Outlet Pipe, !- Comp1 Name
    Supply Side Exit Pipe Inlet Node,
                             !- Comp1 Inlet Node Name
    CW Supply Outlet Node,   !- Comp1 Outlet Node Name
!                                                                                                           Bypass
    PASSIVE;                 !- Comp1 Branch Control Type
BRANCH,
    CW Pump Branch,          !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PUMP:VARIABLE SPEED,     !- Comp1 Type
    Circ Pump,               !- Comp1 Name
    CW Supply Inlet Node,    !- Comp1 Inlet Node Name
    CW Pump Outlet Node,     !- Comp1 Outlet Node Name
    Active;                  !- Comp1 Branch Control Type
BRANCH,
    Little Chiller Branch,   !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    CHILLER:CONST COP,       !- Comp1 Type
    Little Chiller,          !- Comp1 Name
    Little Chiller Inlet Node,
                             !- Comp1 Inlet Node Name
    Little Chiller Outlet Node,
                             !- Comp1 Outlet Node Name
    Active;                  !- Comp1 Branch Control Type
BRANCH,
    Big Chiller Branch,      !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    CHILLER:BLAST,           !- Comp1 Type
    Big Chiller,             !- Comp1 Name
    Big Chiller Inlet Node,  !- Comp1 Inlet Node Name
    Big Chiller Outlet Node, !- Comp1 Outlet Node Name
    Active;                  !- Comp1 Branch Control Type
BRANCH,
    Purchased Cooling Branch,!- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PURCHASED:CHILLED WATER, !- Comp1 Type
    Purchased Cooling,       !- Comp1 Name
    Purchased Cooling Inlet Node,
                             !- Comp1 Inlet Node Name
    Purchased Cooling Outlet Node,
                             !- Comp1 Outlet Node Name
    Active;                  !- Comp1 Branch Control Type
BRANCH,
    Supply Bypass Branch,    !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Supply Side Bypass,      !- Comp1 Name
    CW Supply Bypass Inlet Node,
                             !- Comp1 Inlet Node Name
    CW Supply Bypass Outlet Node,
                             !- Comp1 Outlet Node Name
!                                                                                                           inlet to loop
    BYPASS;                  !- Comp1 Branch Control Type
BRANCH,
    Condenser Supply Inlet Branch,
                             !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PUMP:VARIABLE SPEED,     !- Comp1 Type
    Cond Circ Pump,          !- Comp1 Name
    Condenser Supply Inlet Node,
                             !- Comp1 Inlet Node Name
    Condenser Pump Outlet Node,
                             !- Comp1 Outlet Node Name
    ACTIVE;                  !- Comp1 Branch Control Type
BRANCH,
    Condenser Supply Tower Branch,
                             !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    COOLING TOWER:SINGLE SPEED,
                             !- Comp1 Type
    Big Tower,               !- Comp1 Name
    Condenser Tower Inlet Node,
                             !- Comp1 Inlet Node Name
    Condenser Tower Outlet Node,
                             !- Comp1 Outlet Node Name
    ACTIVE;                  !- Comp1 Branch Control Type
BRANCH,
    Condenser Supply Bypass Branch,
                             !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Condenser Supply Side Bypass,
                             !- Comp1 Name
    Cond Supply Bypass Inlet Node ,
                             !- Comp1 Inlet Node Name
    Cond Supply Bypass Outlet Node,
                             !- Comp1 Outlet Node Name
    BYPASS;                  !- Comp1 Branch Control Type
BRANCH,
    Condenser Supply Outlet Branch,
                             !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Condenser Supply Outlet, !- Comp1 Name
    Condenser Supply Exit Pipe Inlet Node,
                             !- Comp1 Inlet Node Name
    Condenser Supply Outlet Node,
                             !- Comp1 Outlet Node Name
    PASSIVE;                 !- Comp1 Branch Control Type
BRANCH,
    Condenser Demand Inlet Branch,
                             !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Condenser Demand Inlet Pipe,
                             !- Comp1 Name
    Condenser Demand Inlet Node,
                             !- Comp1 Inlet Node Name
    Condenser Demand Entrance Pipe Outlet Node,
                             !- Comp1 Outlet Node Name
!                                                                                                           Condenser Entrance pipe
    PASSIVE;                 !- Comp1 Branch Control Type
BRANCH,
    Little Chiller Condenser Branch,
                             !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    CHILLER:CONST COP,       !- Comp1 Type
    Little Chiller,          !- Comp1 Name
    Little Chiller Condenser Inlet Node,
                             !- Comp1 Inlet Node Name
    Little Chiller Condenser Outlet Node,
                             !- Comp1 Outlet Node Name
    PASSIVE;                 !- Comp1 Branch Control Type
BRANCH,
    Big Chiller Condenser Branch,
                             !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    CHILLER:BLAST,           !- Comp1 Type
    Big Chiller,             !- Comp1 Name
    Big Chiller Condenser Inlet Node,
                             !- Comp1 Inlet Node Name
    Big Chiller Condenser Outlet Node,
                             !- Comp1 Outlet Node Name
    ACTIVE;                  !- Comp1 Branch Control Type
BRANCH,
    Condenser Demand Bypass Branch,
                             !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Condenser Demand Side Bypass,
                             !- Comp1 Name
    Cond Demand Bypass Inlet Node,
                             !- Comp1 Inlet Node Name
    Cond Demand Bypass Outlet Node,
                             !- Comp1 Outlet Node Name
!                                                                                                           inlet to loop
    BYPASS;                  !- Comp1 Branch Control Type
BRANCH,
    Condenser Demand Outlet Branch,
                             !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Condenser Demand Outlet Pipe,
                             !- Comp1 Name
    Condenser Demand Exit Pipe Inlet Node,
                             !- Comp1 Inlet Node Name
    Condenser Demand Outlet Node,
                             !- Comp1 Outlet Node Name
!                                                                                                           exit to loop
    PASSIVE;                 !- Comp1 Branch Control Type
BRANCH,
    Heating Supply Inlet Branch,
                             !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PUMP:VARIABLE SPEED,     !- Comp1 Type
    HW Circ Pump,            !- Comp1 Name
    HW Supply Inlet Node,    !- Comp1 Inlet Node Name
    HW Pump Outlet Node,     !- Comp1 Outlet Node Name
    ACTIVE;                  !- Comp1 Branch Control Type
BRANCH,
    Heating Purchased Hot Water Branch,
                             !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PURCHASED:HOT WATER,     !- Comp1 Type
    Purchased Heating,       !- Comp1 Name
    Purchased Heat Inlet Node,
                             !- Comp1 Inlet Node Name
    Purchased Heat Outlet Node,
                             !- Comp1 Outlet Node Name
    ACTIVE;                  !- Comp1 Branch Control Type
BRANCH,
    Heating Supply Bypass Branch,
                             !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Heating Supply Side Bypass,
                             !- Comp1 Name
    Heating Supply Bypass Inlet Node ,
                             !- Comp1 Inlet Node Name
    Heating Supply Bypass Outlet Node,
                             !- Comp1 Outlet Node Name
    BYPASS;                  !- Comp1 Branch Control Type
BRANCH,
    Heating Supply Outlet Branch,
                             !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Heating Supply Outlet,   !- Comp1 Name
    Heating Supply Exit Pipe Inlet Node,
                             !- Comp1 Inlet Node Name
    HW Supply Outlet Node,   !- Comp1 Outlet Node Name
    PASSIVE;                 !- Comp1 Branch Control Type
BRANCH,
    Reheat Inlet Branch,     !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Reheat Inlet Pipe,       !- Comp1 Name
    HW Demand Inlet Node,    !- Comp1 Inlet Node Name
    HW Demand Entrance Pipe Outlet Node,
                             !- Comp1 Outlet Node Name
!                                                                                                           loop inlet
    PASSIVE;                 !- Comp1 Branch Control Type
BRANCH,
    Reheat Outlet Branch,    !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Reheat Outlet Pipe,      !- Comp1 Name
    HW Demand Exit Pipe Inlet Node,
                             !- Comp1 Inlet Node Name
    HW Demand Outlet Node,   !- Comp1 Outlet Node Name
    PASSIVE;                 !- Comp1 Branch Control Type
BRANCH,
    Zone 1 Reheat Branch,    !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    COIL:Water:SimpleHeating,!- Comp1 Type
    Reheat Coil Zone 1,      !- Comp1 Name
    Zone 1 Reheat Water Inlet Node,
                             !- Comp1 Inlet Node Name
    Zone 1 Reheat Water Outlet Node,
                             !- Comp1 Outlet Node Name
    ACTIVE;                  !- Comp1 Branch Control Type
BRANCH,
    Zone 2 Reheat Branch,    !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    COIL:Water:SimpleHeating,!- Comp1 Type
    Reheat Coil Zone 2,      !- Comp1 Name
    Zone 2 Reheat Water Inlet Node,
                             !- Comp1 Inlet Node Name
    Zone 2 Reheat Water Outlet Node,
                             !- Comp1 Outlet Node Name
    ACTIVE;                  !- Comp1 Branch Control Type
BRANCH,
    Zone 3 Reheat Branch,    !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    COIL:Water:SimpleHeating,!- Comp1 Type
    Reheat Coil Zone 3,      !- Comp1 Name
    Zone 3 Reheat Water Inlet Node,
                             !- Comp1 Inlet Node Name
    Zone 3 Reheat Water Outlet Node,
                             !- Comp1 Outlet Node Name
    ACTIVE;                  !- Comp1 Branch Control Type
BRANCH,
    Reheat Bypass Branch,    !- Branch Name
    0.001,                   !- Maximum Branch Flow Rate {m3/s}
    PIPE,                    !- Comp1 Type
    Reheat Bypass,           !- Comp1 Name
    Reheat Bypass Inlet Node,!- Comp1 Inlet Node Name
    Reheat Bypass Outlet Node,
                             !- Comp1 Outlet Node Name
!                                                                                                           inlet to loop
    BYPASS;                  !- Comp1 Branch Control Type
!-   ===========  ALL OBJECTS IN CLASS: PIPE ===========
PIPE,
    Demand Side Inlet Pipe,  !- PipeName
    CW Demand Inlet Node,    !- Inlet Node Name
    CW Demand Entrance Pipe Outlet Node;
                             !- Outlet Node Name
PIPE,
    Demand Side Bypass,      !- PipeName
    CW Demand Bypass Inlet Node,
                             !- Inlet Node Name
    CW Demand Bypass Outlet Node;
                             !- Outlet Node Name
PIPE,
    CW Demand Side Outlet Pipe,
                             !- PipeName
    CW Demand Exit Pipe Inlet Node,
                             !- Inlet Node Name
    CW Demand Outlet Node;   !- Outlet Node Name
PIPE,
    Supply Side Outlet Pipe, !- PipeName
    Supply Side Exit Pipe Inlet Node,
                             !- Inlet Node Name
    CW Supply Outlet Node;   !- Outlet Node Name
PIPE,
    Supply Side Bypass,      !- PipeName
    CW Supply Bypass Inlet Node,
                             !- Inlet Node Name
    CW Supply Bypass Outlet Node;
                             !- Outlet Node Name
PIPE,
    Condenser Supply Side Bypass,
                             !- PipeName
    Cond Supply Bypass Inlet Node,
                             !- Inlet Node Name
    Cond Supply Bypass Outlet Node;
                             !- Outlet Node Name
PIPE,
    Condenser Supply Outlet, !- PipeName
    Condenser Supply Exit Pipe Inlet Node,
                             !- Inlet Node Name
    Condenser Supply Outlet Node;
                             !- Outlet Node Name
PIPE,
    Condenser Demand Inlet Pipe,
                             !- PipeName
    Condenser Demand Inlet Node,
                             !- Inlet Node Name
    Condenser Demand Entrance Pipe Outlet Node;
                             !- Outlet Node Name
PIPE,
    Condenser Demand Side Bypass,
                             !- PipeName
    Cond Demand Bypass Inlet Node,
                             !- Inlet Node Name
    Cond Demand Bypass Outlet Node;
                             !- Outlet Node Name
PIPE,
    Condenser Demand Outlet Pipe,
                             !- PipeName
    Condenser Demand Exit Pipe Inlet Node,
                             !- Inlet Node Name
    Condenser Demand Outlet Node;
                             !- Outlet Node Name
PIPE,
    Heating Supply Side Bypass,
                             !- PipeName
    Heating Supply Bypass Inlet Node,
                             !- Inlet Node Name
    Heating Supply Bypass Outlet Node;
                             !- Outlet Node Name
PIPE,
    Heating Supply Outlet,   !- PipeName
    Heating Supply Exit Pipe Inlet Node,
                             !- Inlet Node Name
    HW Supply Outlet Node;   !- Outlet Node Name
PIPE,
    Reheat Inlet Pipe,       !- PipeName
    HW Demand Inlet Node,    !- Inlet Node Name
    HW Demand Entrance Pipe Outlet Node;
                             !- Outlet Node Name
PIPE,
    Reheat Outlet Pipe,      !- PipeName
    HW Demand Exit Pipe Inlet Node,
                             !- Inlet Node Name
    HW Demand Outlet Node;   !- Outlet Node Name
!-   ===========  ALL OBJECTS IN CLASS: PLANT LOOP ===========
PLANT LOOP,
!                                                                                                           ***********************PLANT SPECIFICATION********************************************
!                                                                                                           ***********************Chilled Water Loop********************************************
    Chilled Water Loop,      !- Plant Loop Name
    Water,                   !- Fluid Type
    CW Loop Operation,       !- Plant Operation Scheme List Name
    Work Eff Sch,            !- Loop Temperature Setpoint Schedule Name
!                                                                                                           [Maximum Loop Temperature]
    98,                      !- Maximum Loop Temperature {C}
!                                                                                                           [Minimum Loop Temperature]
    1,                       !- Minimum Loop Temperature {C}
!                                                                                                           [Loop Volumetric Flow Rate Setpoint ]
    0.001,                   !- Loop Volumetric Flow Rate Setpoint {m3/s}
!                                                                                                           [Maximum Loop Volumetric Flow Rate]
    0.001,                   !- Maximum Loop Volumetric Flow Rate {m3/s}
!                                                                                                           [Minimum Loop Volumetric Flow Rate]
    0,                       !- Minimum Loop Volumetric Flow Rate {m3/s}
!                                                                                                           plant supply side inlet/outlet
    CW Supply Inlet Node,    !- Plant Side Inlet Node Name
    CW Supply Outlet Node,   !- Plant Side Outlet Node Name
    Cooling Supply Side Branches,
                             !- Plant Side Branch List Name
    Cooling Supply Side Connectors,
                             !- Plant Side Connector List Name
!                                                                                                           plant demand side inlet/outlet
    CW Demand Inlet Node,    !- Demand Side Inlet Node Name
    CW Demand Outlet Node,   !- Demand Side Outlet Nodes Name
    Cooling Demand Side Branches,
                             !- Demand Side Branch List Name
    Cooling Demand Side Connectors,
                             !- Demand Side Connector List Name
    Optimal;                 !- Load Distribution Scheme
PLANT LOOP,
!                                                                                                           ***********************Hot Water Loop********************************************
    Hot Water Loop,          !- Plant Loop Name
    Water,                   !- Fluid Type
    Hot Loop Operation,      !- Plant Operation Scheme List Name
    Work Eff Sch,            !- Loop Temperature Setpoint Schedule Name
!                                                                                                           [Maximum Loop Temperature]
    100,                     !- Maximum Loop Temperature {C}
!                                                                                                           [Minimum Loop Temperature]
    10,                      !- Minimum Loop Temperature {C}
!                                                                                                           [Loop Volumetric Flow Rate Setpoint ]
    0.004,                   !- Loop Volumetric Flow Rate Setpoint {m3/s}
!                                                                                                           [Maximum Loop Volumetric Flow Rate]
    0.005,                   !- Maximum Loop Volumetric Flow Rate {m3/s}
!                                                                                                           [Minimum Loop Volumetric Flow Rate]
    0,                       !- Minimum Loop Volumetric Flow Rate {m3/s}
!                                                                                                           plant supply side inlet/outlet
    HW Supply Inlet Node,    !- Plant Side Inlet Node Name
    HW Supply Outlet Node,   !- Plant Side Outlet Node Name
    Heating Supply Side Branches,
                             !- Plant Side Branch List Name
    Heating Supply Side Connectors,
                             !- Plant Side Connector List Name
!                                                                                                           plant demand side inlet/outlet
    HW Demand Inlet Node,    !- Demand Side Inlet Node Name
    HW Demand Outlet Node,   !- Demand Side Outlet Nodes Name
    Heating Demand Side Branches,
                             !- Demand Side Branch List Name
    Heating Demand Side Connectors,
                             !- Demand Side Connector List Name
    Optimal;                 !- Load Distribution Scheme
!-   ===========  ALL OBJECTS IN CLASS: CONDENSER LOOP ===========
CONDENSER LOOP,
!                                                                                                           ***********************Condenser Loop********************************************
    Chilled Water Condenser Loop,
                             !- Condenser Loop Name
    Water,                   !- Fluid Type
    Tower Loop Operation,    !- Condenser Operation Scheme List Name
    Work Eff Sch,            !- Loop Temperature Setpoint Schedule Name
!                                                                                                           [Maximum Loop Temperature]
    80,                      !- Maximum Loop Temperature {C}
!                                                                                                           [Minimum Loop Temperature]
    0.5,                     !- Minimum Loop Temperature {C}
!                                                                                                           [Loop Volumetric Flow Rate Setpoint ]
    0.001,                   !- Loop Volumetric Flow Rate Setpoint {m3/s}
!                                                                                                           [Maximum Loop Volumetric Flow Rate]
    0.001,                   !- Maximum Loop Volumetric Flow Rate {m3/s}
!                                                                                                           [Minimum Loop Volumetric Flow Rate]
    0,                       !- Minimum Loop Volumetric Flow Rate {m3/s}
!                                                                                                           condenser supply side inlet/outlet
    Condenser Supply Inlet Node,
                             !- Condenser Side Inlet Node Name
    Condenser Supply Outlet Node,
                             !- Condenser Side Outlet Node Name
    Condenser Supply Side Branches,
                             !- Condenser Side Branch List Name
    Condenser Supply Side Connectors,
                             !- Condenser Side Connector List Name
!                                                                                                           plant demand side inlet/outlet
    Condenser Demand Inlet Node,
                             !- Demand Side Inlet Node Name
    Condenser Demand Outlet Node,
                             !- Demand Side Outlet Nodes Name
    Condenser Demand Side Branches,
                             !- Condenser Demand Side Branch List Name
    Condenser Demand Side Connectors;
                             !- Condenser Demand Side Connector List Name
!-   ===========  ALL OBJECTS IN CLASS: PLANT OPERATION SCHEMES ===========
PLANT OPERATION SCHEMES,
    CW Loop Operation,       !- PlantOperationSchemeName
    LOAD RANGE BASED OPERATION,
                             !- KEY--Control Scheme 1
    Peak Operation,          !- Control Scheme Name 1
    Work Eff Sch,            !- Control Scheme Schedule 1
    LOAD RANGE BASED OPERATION,
                             !- KEY--Control Scheme 2
    Off Peak Operation,      !- Control Scheme Name 2
    Work Eff Sch;            !- Control Scheme Schedule 2
PLANT OPERATION SCHEMES,
    Hot Loop Operation,      !- PlantOperationSchemeName
    LOAD RANGE BASED OPERATION,
                             !- KEY--Control Scheme 1
    Purchased Only,          !- Control Scheme Name 1
    Work Eff Sch;            !- Control Scheme Schedule 1
!-   ===========  ALL OBJECTS IN CLASS: CONDENSER OPERATION SCHEMES ===========
CONDENSER OPERATION SCHEMES,
    Tower Loop Operation,    !- CondenserOperationSchemeName
    LOAD RANGE BASED OPERATION,
                             !- KEY--Control Scheme 1
    Year Round Tower Operation,
                             !- Control Scheme Name 1
    Work Eff Sch;            !- Control Scheme Schedule 1
!-   ===========  ALL OBJECTS IN CLASS: LOAD RANGE BASED OPERATION ===========
LOAD RANGE BASED OPERATION,
    Peak Operation,          !- Name
    0,                       !- Load Range Lower Limit 1 {W}
    -1,                      !- Load Range Upper Limit 1 {W}
    Chiller Plant,           !- Priority Control Equip List Name 1
    -1,                      !- Load Range Lower Limit 2 {W}
    -1,                      !- Load Range Upper Limit 2 {W}
    Chiller Plant and Purchased,
                             !- Priority Control Equip List Name 2
    -1,                      !- Load Range Lower Limit 3 {W}
    -1,                      !- Load Range Upper Limit 3 {W}
    Purchased Only;          !- Priority Control Equip List Name 3
LOAD RANGE BASED OPERATION,
    Off Peak Operation,      !- Name
    0,                       !- Load Range Lower Limit 1 {W}
    -1,                      !- Load Range Upper Limit 1 {W}
    All Chillers;            !- Priority Control Equip List Name 1
LOAD RANGE BASED OPERATION,
    Year Round Tower Operation,
                             !- Name
    0,                       !- Load Range Lower Limit 1 {W}
    -1,                      !- Load Range Upper Limit 1 {W}
    All Towers;              !- Priority Control Equip List Name 1
LOAD RANGE BASED OPERATION,
    Purchased Only,          !- Name
    0,                       !- Load Range Lower Limit 1 {W}
    1,                       !- Load Range Upper Limit 1 {W}
    heating plant;           !- Priority Control Equip List Name 1
!-   ===========  ALL OBJECTS IN CLASS: LOAD RANGE EQUIPMENT LIST ===========
LOAD RANGE EQUIPMENT LIST,
    Chiller Plant,           !- Equip List Name
    CHILLER:CONST COP,       !- KEY--Plant Equip 1
    Little Chiller;          !- Equip Name 1
LOAD RANGE EQUIPMENT LIST,
    Chiller Plant and Purchased,
                             !- Equip List Name
    CHILLER:BLAST,           !- KEY--Plant Equip 1
    Big Chiller,             !- Equip Name 1
    PURCHASED:CHILLED WATER, !- KEY--Plant Equip 2
    Purchased Cooling;       !- Equip Name 2
LOAD RANGE EQUIPMENT LIST,
    Purchased Only,          !- Equip List Name
    PURCHASED:CHILLED WATER, !- KEY--Plant Equip 1
    Purchased Cooling;       !- Equip Name 1
LOAD RANGE EQUIPMENT LIST,
    All Chillers,            !- Equip List Name
    CHILLER:BLAST,           !- KEY--Plant Equip 1
    Big Chiller,             !- Equip Name 1
    CHILLER:CONST COP,       !- KEY--Plant Equip 2
    Little Chiller;          !- Equip Name 2
LOAD RANGE EQUIPMENT LIST,
    All Towers,              !- Equip List Name
    COOLING TOWER:SINGLE SPEED,
                             !- KEY--Plant Equip 1
    Big Tower;               !- Equip Name 1
LOAD RANGE EQUIPMENT LIST,
    heating plant,           !- Equip List Name
    PURCHASED:HOT WATER,     !- KEY--Plant Equip 1
    Purchased Heating;       !- Equip Name 1
!-   ===========  ALL OBJECTS IN CLASS: SPLITTER ===========
SPLITTER,
    CW Loop Splitter,        !- SplitterName
    CW Pump Branch,          !- Inlet Branch Name
    Little Chiller Branch,   !- Outlet Branch Name 1
    Big Chiller Branch,      !- Outlet Branch Name 2
    Purchased Cooling Branch,!- Outlet Branch Name 3
    Supply Bypass Branch;    !- Outlet Branch Name 4
SPLITTER,
    CW Demand Splitter,      !- SplitterName
    Cooling Demand Inlet,    !- Inlet Branch Name
    Demand Bypass Branch,    !- Outlet Branch Name 1
    Cooling Coil Branch;     !- Outlet Branch Name 2
SPLITTER,
    Condenser Demand Splitter,
                             !- SplitterName
    Condenser Demand Inlet Branch,
                             !- Inlet Branch Name
    Big Chiller Condenser Branch,
                             !- Outlet Branch Name 1
    Little Chiller Condenser Branch,
                             !- Outlet Branch Name 2
    Condenser Demand Bypass Branch;
                             !- Outlet Branch Name 3
SPLITTER,
    Condenser Supply Splitter,
                             !- SplitterName
    Condenser Supply Inlet Branch,
                             !- Inlet Branch Name
    Condenser Supply Tower Branch,
                             !- Outlet Branch Name 1
    Condenser Supply Bypass Branch;
                             !- Outlet Branch Name 2
SPLITTER,
    Reheat Splitter,         !- SplitterName
    Reheat Inlet Branch,     !- Inlet Branch Name
    Zone 1 Reheat Branch,    !- Outlet Branch Name 1
    Zone 2 Reheat Branch,    !- Outlet Branch Name 2
    Zone 3 Reheat Branch,    !- Outlet Branch Name 3
    Reheat Bypass Branch;    !- Outlet Branch Name 4
SPLITTER,
    Heating Supply Splitter, !- SplitterName
    Heating Supply Inlet Branch,
                             !- Inlet Branch Name
    Heating Purchased Hot Water Branch,
                             !- Outlet Branch Name 1
    Heating Supply Bypass Branch;
                             !- Outlet Branch Name 2
!-   ===========  ALL OBJECTS IN CLASS: MIXER ===========
MIXER,
    CW Loop Mixer,           !- MixerName
    Cooling Supply Outlet,   !- Outlet Branch Name
    Little Chiller Branch,   !- Inlet Branch Name 1
    Big Chiller Branch,      !- Inlet Branch Name 2
    Purchased Cooling Branch,!- Inlet Branch Name 3
    Supply Bypass Branch;    !- Inlet Branch Name 4
MIXER,
    CW Demand Mixer,         !- MixerName
    Cooling Demand Outlet,   !- Outlet Branch Name
    Cooling Coil Branch,     !- Inlet Branch Name 1
    Demand Bypass Branch;    !- Inlet Branch Name 2
MIXER,
    Condenser Demand Mixer,  !- MixerName
    Condenser Demand Outlet Branch,
                             !- Outlet Branch Name
    Big Chiller Condenser Branch,
                             !- Inlet Branch Name 1
    Little Chiller Condenser Branch,
                             !- Inlet Branch Name 2
    Condenser Demand Bypass Branch;
                             !- Inlet Branch Name 3
MIXER,
    Condenser Supply Mixer,  !- MixerName
    Condenser Supply Outlet Branch,
                             !- Outlet Branch Name
    Condenser Supply Tower Branch,
                             !- Inlet Branch Name 1
    Condenser Supply Bypass Branch;
                             !- Inlet Branch Name 2
MIXER,
    Reheat Mixer,            !- MixerName
    Reheat Outlet Branch,    !- Outlet Branch Name
    Zone 1 Reheat Branch,    !- Inlet Branch Name 1
    Zone 2 Reheat Branch,    !- Inlet Branch Name 2
    Zone 3 Reheat Branch,    !- Inlet Branch Name 3
    Reheat Bypass Branch;    !- Inlet Branch Name 4
MIXER,
    Heating Supply Mixer,    !- MixerName
    Heating Supply Outlet Branch,
                             !- Outlet Branch Name
    Heating Purchased Hot Water Branch,
                             !- Inlet Branch Name 1
    Heating Supply Bypass Branch;
                             !- Inlet Branch Name 2
!-   ===========  ALL OBJECTS IN CLASS: AIR PRIMARY LOOP ===========
AIR PRIMARY LOOP,
!                                                                                                            First Air Loop in the system
    Typical Terminal Reheat 1,
                             !- Primary Air Loop Name
    Reheat System 1 Controllers,
                             !- Name: Controller List
    Reheat System 1 Avail List,
                             !- Name: System Availability Manager List
    6,                       !- Primary air design volumetric flow rate {m3/s}
    Air Loop Branches,       !- Air Loop Branch List Name
    ,                        !- Air Loop Connector List Name
    Air Loop Inlet Node,     !- ReturnAir AirLoop Inlet Node
    Return Air Mixer Outlet, !- ZoneEquipGroup Outlet Node
    Zone Equipment Inlet Node,
                             !- SupplyAirPath ZoneEquipGroup Inlet Nodes
    Air Loop Outlet Node;    !- AirLoop Outlet Nodes
!-   ===========  ALL OBJECTS IN CLASS: CONTROLLER LIST ===========
CONTROLLER LIST,
    Reheat System 1 Controllers,
                             !- Name
    Controller:Simple,       !- KEY--Controller  1
    Main Cooling Coil Controller;
                             !- Controller Name 1
CONTROLLER LIST,
    OA Sys 1 Controllers,    !- Name
    CONTROLLER:OUTSIDE AIR,  !- KEY--Controller  1
    OA Controller 1;         !- Controller Name 1
!-   ===========  ALL OBJECTS IN CLASS: AIR LOOP EQUIPMENT LIST ===========
AIR LOOP EQUIPMENT LIST,
    OA Sys 1 Equipment,      !- Name
    DESICCANT DEHUMIDIFIER:SOLID,
                             !- KEY--System Component 1
    Desiccant 1,             !- Component Name 1
    HEAT EXCHANGER:AIR TO AIR:FLAT PLATE,
                             !- KEY--System Component 2
    OA Heat Recovery 1,      !- Component Name 2
    OUTSIDE AIR MIXER,       !- KEY--System Component 3
    OA Mixing Box 1;         !- Component Name 3
AIR LOOP EQUIPMENT LIST,
    OA Sys 2 Equipment,      !- Name
    HEAT EXCHANGER:AIR TO AIR:FLAT PLATE,
                             !- KEY--System Component 1
    OA Heat Recovery 2,      !- Component Name 1
    OUTSIDE AIR MIXER,       !- KEY--System Component 2
    OA Mixing Box 2;         !- Component Name 2
!-   ===========  ALL OBJECTS IN CLASS: SYSTEM AVAILABILITY MANAGER LIST ===========
SYSTEM AVAILABILITY MANAGER LIST,
    Reheat System 1 Avail List,
                             !- Name
    SYSTEM AVAILABILITY MANAGER:SCHEDULED,
                             !- KEY--System Availability Manager 1
    Reheat System 1 Avail;   !- System Availability Manager name 1
!-   ===========  ALL OBJECTS IN CLASS: SYSTEM AVAILABILITY MANAGER:SCHEDULED ===========
SYSTEM AVAILABILITY MANAGER:SCHEDULED,
    Reheat System 1 Avail,   !- Name
    ON;                      !- Schedule name
!-   ===========  ALL OBJECTS IN CLASS: OUTSIDE AIR SYSTEM ===========
OUTSIDE AIR SYSTEM,
    OA Sys 1,                !- Name
    OA Sys 1 Controllers,    !- Name: Controller List
    OA Sys 1 Equipment,      !- Name of an Air Loop Equipment List
    Reheat System 1 Avail List;
                             !- Name of a System Availability Manager List
OUTSIDE AIR SYSTEM,
    OA Sys 2,                !- Name
    OA Sys 2 Controllers,    !- Name: Controller List
    OA Sys 2 Equipment,      !- Name of an Air Loop Equipment List
    Reheat System 1 Avail List;
                             !- Name of a System Availability Manager List
!-   ===========  ALL OBJECTS IN CLASS: OUTSIDE AIR INLET NODE LIST ===========
OUTSIDE AIR INLET NODE LIST,
!                                                                                                           **********************AIR LOOP*******************************
    OutsideAirInletNodes,    !- 1st Node name or node list name
    Outside Air Inlet Node 2;!- 2nd Node name or node list name
!-   ===========  ALL OBJECTS IN CLASS: OUTSIDE AIR MIXER ===========
OUTSIDE AIR MIXER,
    OA Mixing Box 1,         !- Name
    mixed air node,          !- Mixed_Air_Node
    Heat Recovery Outlet Node,
                             !- Outside_Air_Stream_Node
    Relief Air Outlet Node,  !- Relief_Air_Stream_Node
    Air Loop Inlet Node;     !- Return_Air_Stream_Node
!-   ===========  ALL OBJECTS IN CLASS: CONTROLLED ZONE EQUIP CONFIGURATION ===========
CONTROLLED ZONE EQUIP CONFIGURATION,
    RESISTIVE ZONE,          !- Zone Name
    Zone1Equipment,          !- List Name: Zone Equipment
    Zone1Inlets,             !- List Name: Zone Inlet Nodes
    ,                        !- List Name: Zone Exhaust Nodes
    Zone 1 Node,             !- Zone Air Node Name
    Zone 1 Outlet Node;      !- Zone Return Air Node Name
CONTROLLED ZONE EQUIP CONFIGURATION,
    EAST ZONE,               !- Zone Name
    Zone2Equipment,          !- List Name: Zone Equipment
    Zone2Inlets,             !- List Name: Zone Inlet Nodes
    ,                        !- List Name: Zone Exhaust Nodes
    Zone 2 Node,             !- Zone Air Node Name
    Zone 2 Outlet Node;      !- Zone Return Air Node Name
CONTROLLED ZONE EQUIP CONFIGURATION,
    NORTH ZONE,              !- Zone Name
    Zone3Equipment,          !- List Name: Zone Equipment
    Zone3Inlets,             !- List Name: Zone Inlet Nodes
    ,                        !- List Name: Zone Exhaust Nodes
    Zone 3 Node,             !- Zone Air Node Name
    Zone 3 Outlet Node;      !- Zone Return Air Node Name
!-   ===========  ALL OBJECTS IN CLASS: ZONE CONTROL:THERMOSTATIC ===========
ZONE CONTROL:THERMOSTATIC,
!                                                                                                           *****************ZONE EQUIPMENT SPECIFICATION*********************
!                                                                                                            Valid Control Types are 1 - Single Heating Setpoint 2 - Single Cooling SetPoint
!                                                                                                                                     3 - Single Heating/Cooling Setpoint 4 - Dual Setpoint
!                                                                                                                                         (Heating and Cooling) with deadband
    Zone 1 Thermostat,       !- Thermostat Name
    RESISTIVE ZONE,          !- Zone Name
    Zone Control Type Sched, !- Control Type SCHEDULE Name
    SINGLE HEATING SETPOINT, !- Control Type #1
    Heating Setpoint with SB,!- Control Type Name #1
    SINGLE COOLING SETPOINT, !- Control Type #2
    Cooling Setpoint with SB;!- Control Type Name #2
ZONE CONTROL:THERMOSTATIC,
    Zone 2 Thermostat,       !- Thermostat Name
    EAST ZONE,               !- Zone Name
    Zone Control Type Sched, !- Control Type SCHEDULE Name
    SINGLE HEATING SETPOINT, !- Control Type #1
    Heating Setpoint with SB,!- Control Type Name #1
    SINGLE COOLING SETPOINT, !- Control Type #2
    Cooling Setpoint with SB;!- Control Type Name #2
ZONE CONTROL:THERMOSTATIC,
    Zone 3 Thermostat,       !- Thermostat Name
    NORTH ZONE,              !- Zone Name
    Zone Control Type Sched, !- Control Type SCHEDULE Name
    SINGLE HEATING SETPOINT, !- Control Type #1
    Heating Setpoint with SB,!- Control Type Name #1
    SINGLE COOLING SETPOINT, !- Control Type #2
    Cooling Setpoint with SB;!- Control Type Name #2
!-   ===========  ALL OBJECTS IN CLASS: ZONE EQUIPMENT LIST ===========
ZONE EQUIPMENT LIST,
    Zone1Equipment,          !- Name
    AIR DISTRIBUTION UNIT,   !- KEY--Zone Equipment Type 1
    Zone1TermReheat,         !- Type Name 1
    1,                       !- Cooling Priority
    1;                       !- Heating Priority
ZONE EQUIPMENT LIST,
    Zone2Equipment,          !- Name
    AIR DISTRIBUTION UNIT,   !- KEY--Zone Equipment Type 1
    Zone2TermReheat,         !- Type Name 1
    1,                       !- Cooling Priority
    1;                       !- Heating Priority
ZONE EQUIPMENT LIST,
    Zone3Equipment,          !- Name
    AIR DISTRIBUTION UNIT,   !- KEY--Zone Equipment Type 1
    Zone3TermReheat,         !- Type Name 1
    1,                       !- Cooling Priority
    1;                       !- Heating Priority
!-   ===========  ALL OBJECTS IN CLASS: AIR DISTRIBUTION UNIT ===========
AIR DISTRIBUTION UNIT,
    Zone1TermReheat,         !- Air Distribution Unit Name
    Zone 1 Reheat Air Outlet Node,
                             !- Air Dist Unit Outlet Node Name
    SINGLE DUCT:CONST VOLUME:REHEAT,
                             !- KEY--System Component Type 1
    Reheat Zone 1;           !- Component Name 1
AIR DISTRIBUTION UNIT,
    Zone2TermReheat,         !- Air Distribution Unit Name
    Zone 2 Reheat Air Outlet Node,
                             !- Air Dist Unit Outlet Node Name
    SINGLE DUCT:CONST VOLUME:REHEAT,
                             !- KEY--System Component Type 1
    Reheat Zone 2;           !- Component Name 1
AIR DISTRIBUTION UNIT,
    Zone3TermReheat,         !- Air Distribution Unit Name
    Zone 3 Reheat Air Outlet Node,
                             !- Air Dist Unit Outlet Node Name
    SINGLE DUCT:CONST VOLUME:REHEAT,
                             !- KEY--System Component Type 1
    Reheat Zone 3;           !- Component Name 1
!-   ===========  ALL OBJECTS IN CLASS: ZONE SUPPLY AIR PATH ===========
ZONE SUPPLY AIR PATH,
!                                                                                                           Zone Heating and Cooling Equipment are attached to zones by the following statements:
    TermReheatSupplyPath,    !- Supply Air Path Name
    Zone Equipment Inlet Node,
                             !- Supply Air Path Inlet Node
    Zone Splitter,           !- KEY--System Component Type
    Zone Supply Air Splitter;!- Component Name
!-   ===========  ALL OBJECTS IN CLASS: ZONE RETURN AIR PATH ===========
ZONE RETURN AIR PATH,
    TermReheatReturnPath,    !- Return Air Path Name
    Return Air Mixer Outlet, !- Return Air Path Outlet Node
    Zone Mixer,              !- KEY--System Component Type 1
    Zone Return Air Mixer;   !- Component Name 1
!-   ===========  ALL OBJECTS IN CLASS: ZONE SPLITTER ===========
ZONE SPLITTER,
!                                                                                                           Specify the Components in the Zone Equipment Group
    Zone Supply Air Splitter,!- Splitter Name
!                                                                                                            inlet node
    Zone Equipment Inlet Node,
                             !- Inlet_Node
!                                                                                                            outlet Nodes
    Zone 1 Reheat Air Inlet Node,
                             !- Outlet_Node_1
    Zone 2 Reheat Air Inlet Node,
                             !- Outlet_Node_2
    Zone 3 Reheat Air Inlet Node;
                             !- Outlet_Node_3
!-   ===========  ALL OBJECTS IN CLASS: ZONE MIXER ===========
ZONE MIXER,
    Zone Return Air Mixer,   !- Mixer Name
!                                                                                                            outlet Node
    Return Air Mixer Outlet, !- Outlet_Node
!                                                                                                            inlet nodes
    Zone 1 Outlet Node,      !- Inlet_Node_1
    Zone 2 Outlet Node,      !- Inlet_Node_2
    Zone 3 Outlet Node;      !- Inlet_Node_3
!-   ===========  ALL OBJECTS IN CLASS: SINGLE DUCT:CONST VOLUME:REHEAT ===========
SINGLE DUCT:CONST VOLUME:REHEAT,
!                                                                                                           ***********ZONE TERMINAL UNIT ONLY AIR LOOP COMPONENTS***************
!                                                                                                            Name of System
    Reheat Zone 1,           !- Name of System
!                                                                                                            Availability schedule for System
    ON,                      !- Availability schedule for VAV System
!                                                                                                            Air distribution Unit outlet & inlet nodes
    Zone 1 Reheat Air Outlet Node,
                             !- Damper Outlet Node
    Zone 1 Reheat Air Inlet Node,
                             !- Damper Inlet Node
!                                                                                                            Maximum air flow rate m^3/s
    2,                       !- Maximum air flow rate {m3/s}
!                                                                                                            Control node
    Zone 1 Reheat Water Inlet Node,
                             !- Control node
!                                                                                                            Reheat Component Object
    COIL:Water:SimpleHeating,!- Reheat Component Object
!                                                                                                            Name of Reheat Component
    Reheat Coil Zone 1,      !- Name of Reheat Component
!                                                                                                            Max Reheat Water Flow {Flow: kg/sec}
    1.3,                     !- Max Reheat Water Flow {kg/s}
!                                                                                                            Min Reheat Water Flow {Flow: kg/sec}
    0,                       !- Min Reheat Water Flow {kg/s}
!                                                                                                            Convergence Tolerance
    0.001;                   !- Convergence Tolerance
SINGLE DUCT:CONST VOLUME:REHEAT,
!                                                                                                            Name of System
    Reheat Zone 2,           !- Name of System
!                                                                                                            Availability schedule for System
    ON,                      !- Availability schedule for VAV System
!                                                                                                            Air distribution Unit outlet & inlet nodes
    Zone 2 Reheat Air Outlet Node,
                             !- Damper Outlet Node
    Zone 2 Reheat Air Inlet Node,
                             !- Damper Inlet Node
!                                                                                                            Maximum air flow rate m^3/s
    2,                       !- Maximum air flow rate {m3/s}
!                                                                                                            Control node
    Zone 2 Reheat Water Inlet Node,
                             !- Control node
!                                                                                                            Reheat Component Object
    COIL:Water:SimpleHeating,!- Reheat Component Object
!                                                                                                            Name of Reheat Component
    Reheat Coil Zone 2,      !- Name of Reheat Component
!                                                                                                            Max Reheat Water Flow {Flow: kg/sec}
    1.4,                     !- Max Reheat Water Flow {kg/s}
!                                                                                                            Min Reheat Water Flow {Flow: kg/sec}
    0,                       !- Min Reheat Water Flow {kg/s}
!                                                                                                            Convergence Tolerance
    0.001;                   !- Convergence Tolerance
SINGLE DUCT:CONST VOLUME:REHEAT,
!                                                                                                            Name of System
    Reheat Zone 3,           !- Name of System
!                                                                                                            Availability schedule for System
    ON,                      !- Availability schedule for VAV System
!                                                                                                            Air distribution Unit outlet & inlet nodes
    Zone 3 Reheat Air Outlet Node,
                             !- Damper Outlet Node
    Zone 3 Reheat Air Inlet Node,
                             !- Damper Inlet Node
!                                                                                                            Maximum air flow rate m^3/s
    2,                       !- Maximum air flow rate {m3/s}
!                                                                                                            Control node
    Zone 3 Reheat Water Inlet Node,
                             !- Control node
!                                                                                                            Reheat Component Object
    COIL:Water:SimpleHeating,!- Reheat Component Object
!                                                                                                            Name of Reheat Component
    Reheat Coil Zone 3,      !- Name of Reheat Component
!                                                                                                            Max Reheat Water Flow {Flow: kg/sec}
    1.3,                     !- Max Reheat Water Flow {kg/s}
!                                                                                                            Min Reheat Water Flow {Flow: kg/sec}
    0,                       !- Min Reheat Water Flow {kg/s}
!                                                                                                            Convergence Tolerance
    0.001;                   !- Convergence Tolerance
!-   ===========  ALL OBJECTS IN CLASS: CHILLER:BLAST ===========
CHILLER:BLAST,
    Big Chiller,             !- Chiller Name
    45000,                   !- Nominal Capacity {W}
    2.75,                    !- COP
    Big Chiller Inlet Node,  !- Plant_Side_Inlet_Node
    Big Chiller Outlet Node, !- Plant_Side_Outlet_Node
    Big Chiller Condenser Inlet Node,
                             !- Condenser_Side_Inlet_Node
    Big Chiller Condenser Outlet Node,
                             !- Condenser_Side_Outlet_Node
    0.15,                    !- Minimum Part Load Ratio
    1,                       !- Maximum Part Load Ratio
    0.65,                    !- Opt Part Load Ratio
    35,                      !- Temp Design Condenser Inlet {C}
    2.778,                   !- Temp Rise Coefficient
    7.2222,                  !- Temp Design Evaporator Outlet {C}
    0.0011,                  !- Design Evaporator Volumetric Water Flow Rate {m3/s}
!                                                                                                            Not Used
    0.0005,                  !- Design Condenser Volumetric Water Flow Rate {m3/s}
    0.9949,                  !- Coefficient1 of the capacity ratio curve
    -0.045954,               !- Coefficient2 of the capacity ratio curve
    -0.0013543,              !- Coefficient3 of the capacity ratio curve
    2.333,                   !- Coefficient1 of the power ratio curve
    -1.975,                  !- Coefficient2 of the power ratio curve
    0.6121,                  !- Coefficient3 of the power ratio curve
    0.03303,                 !- Coefficient1 of the full load ratio curve
    0.6852,                  !- Coefficient2 of the full load ratio curve
    0.2818,                  !- Coefficient3 of the full load ratio curve
    5;                       !- Temp Lower Limit Evaporator Outlet {C}
!-   ===========  ALL OBJECTS IN CLASS: CHILLER:CONST COP ===========
CHILLER:CONST COP,
    Little Chiller,          !- Chiller Name
    25000,                   !- Nominal Capacity {W}
    2.5,                     !- COP
    0.0011,                  !- Design Condenser Volumetric Water Flow Rate {m3/s}
    Little Chiller Inlet Node,
                             !- Plant_Side_Inlet_Node
    Little Chiller Outlet Node,
                             !- Plant_Side_Outlet_Node
    Little Chiller Condenser Inlet Node,
                             !- Condenser_Side_Inlet_Node
    Little Chiller Condenser Outlet Node;
                             !- Condenser_Side_Outlet_Node
!-   ===========  ALL OBJECTS IN CLASS: PURCHASED:CHILLED WATER ===========
PURCHASED:CHILLED WATER,
!                                                                                                            Plant Components
    Purchased Cooling,       !- Purchased ID
    Purchased Cooling Inlet Node,
                             !- Plant_Loop_Inlet_Node
    Purchased Cooling Outlet Node,
                             !- Plant_Loop_Outlet_Node
    680000;                  !- Nominal Capacity {W}
!-   ===========  ALL OBJECTS IN CLASS: PURCHASED:HOT WATER ===========
PURCHASED:HOT WATER,
    Purchased Heating,       !- Purchased ID
    Purchased Heat Inlet Node,
                             !- Plant_Loop_Inlet_Node
    Purchased Heat Outlet Node,
                             !- Plant_Loop_Outlet_Node
    1000000;                 !- Nominal Capacity {W}
!-   ===========  ALL OBJECTS IN CLASS: PUMP:VARIABLE SPEED ===========
PUMP:VARIABLE SPEED,
    Circ Pump,               !- Pump Name
    CW Supply Inlet Node,    !- Inlet_Node
    CW Pump Outlet Node,     !- Outlet_Node
    0.0011,                  !- Rated Volumetric Flow Rate {m3/s}
    300000,                  !- Rated Pump Head {Pa}
    500,                     !- Rated Power Consumption {W}
    0.87,                    !- Motor Efficiency
    0,                       !- Fraction of Motor Inefficiencies to Fluid Stream
    1,                       !- Coefficient1 of the Part Load Performance Curve
    0,                       !- Coefficient2 of the Part Load Performance Curve
    0,                       !- Coefficient3 of the Part Load Performance Curve
    0;                       !- Coefficient4 of the Part Load Performance Curve
PUMP:VARIABLE SPEED,
    Cond Circ Pump,          !- Pump Name
    Condenser Supply Inlet Node,
                             !- Inlet_Node
    Condenser Pump Outlet Node,
                             !- Outlet_Node
    0.0011,                  !- Rated Volumetric Flow Rate {m3/s}
    300000,                  !- Rated Pump Head {Pa}
    500,                     !- Rated Power Consumption {W}
    0.87,                    !- Motor Efficiency
    0,                       !- Fraction of Motor Inefficiencies to Fluid Stream
    1,                       !- Coefficient1 of the Part Load Performance Curve
    0,                       !- Coefficient2 of the Part Load Performance Curve
    0,                       !- Coefficient3 of the Part Load Performance Curve
    0;                       !- Coefficient4 of the Part Load Performance Curve
PUMP:VARIABLE SPEED,
    HW Circ Pump,            !- Pump Name
    HW Supply Inlet Node,    !- Inlet_Node
    HW Pump Outlet Node,     !- Outlet_Node
    0.0011,                  !- Rated Volumetric Flow Rate {m3/s}
    300000,                  !- Rated Pump Head {Pa}
    500,                     !- Rated Power Consumption {W}
    0.87,                    !- Motor Efficiency
    0,                       !- Fraction of Motor Inefficiencies to Fluid Stream
    1,                       !- Coefficient1 of the Part Load Performance Curve
    0,                       !- Coefficient2 of the Part Load Performance Curve
    0,                       !- Coefficient3 of the Part Load Performance Curve
    0;                       !- Coefficient4 of the Part Load Performance Curve
!-   ===========  ALL OBJECTS IN CLASS: COOLING TOWER:SINGLE SPEED ===========
COOLING TOWER:SINGLE SPEED,
    Big Tower,               !- Tower ID
    Condenser Tower Inlet Node,
                             !- Inlet_Node
    Condenser Tower Outlet Node,
                             !- Outlet_Node
    0.001,                   !- Design Water Flow Rate {m3/s}
    16,                      !- Design Air Flow Rate {m3/s}
    1000,                    !- Fan Power at Design Air Flow Rate {W}
    1750,                    !- Tower UA value at Design Air Flow Rate
    0,                       !- Air Flow Rate in Free Convection Regime {m3/s}
    0;                       !- Tower UA value at Free Convection Air Flow Rate
!-   ===========  ALL OBJECTS IN CLASS: SINGLE HEATING SETPOINT ===========
SINGLE HEATING SETPOINT,
    Heating Setpoint with SB,!- Name
    Heating Setpoints;       !- Setpoint Temperature SCHEDULE Name
!-   ===========  ALL OBJECTS IN CLASS: SINGLE COOLING SETPOINT ===========
SINGLE COOLING SETPOINT,
    Cooling Setpoint with SB,!- Name
    Cooling Setpoints;       !- Setpoint Temperature SCHEDULE Name
!-   ===========  ALL OBJECTS IN CLASS: COIL:WATER:SIMPLEHEATING ===========
COIL:Water:SimpleHeating,
!                                                                                                           Demand Heating Components
!                                                                                                           Name of cooling coil
    Reheat Coil Zone 1,      !- Coil Name
!                                                                                                           Cooling Coil Schedule
    Work Eff Sch,            !- Available Schedule
!                                                                                                           UA of the Coil
    400,                     !- UA of the Coil {W/K}
!                                                                                                           Max Water Flow Rate of Coil kg/sec
    1.3,                     !- Max Water Flow Rate of Coil {kg/s}
!                                                                                                           Coil Water Side Inlet & Outlet Node
    Zone 1 Reheat Water Inlet Node,
                             !- Coil_Water_Inlet_Node
    Zone 1 Reheat Water Outlet Node,
                             !- Coil_Water_Outlet_Node
!                                                                                                           Coil Air Side Inlet & Outlet Node
    Zone 1 Reheat Air Inlet Node,
                             !- Coil_Air_Inlet_Node
    Zone 1 Reheat Air Outlet Node;
                             !- Coil_Air_Outlet_Node
COIL:Water:SimpleHeating,
!                                                                                                           Name of cooling coil
    Reheat Coil Zone 2,      !- Coil Name
!                                                                                                           Cooling Coil Schedule
    Work Eff Sch,            !- Available Schedule
!                                                                                                           UA of the Coil
    400,                     !- UA of the Coil {W/K}
!                                                                                                           Max Water Flow Rate of Coil kg/sec
    1.3,                     !- Max Water Flow Rate of Coil {kg/s}
!                                                                                                           Coil Water Side Inlet & Outlet Node
    Zone 2 Reheat Water Inlet Node,
                             !- Coil_Water_Inlet_Node
    Zone 2 Reheat Water Outlet Node,
                             !- Coil_Water_Outlet_Node
!                                                                                                           Coil Air Side Inlet & Outlet Node
    Zone 2 Reheat Air Inlet Node,
                             !- Coil_Air_Inlet_Node
    Zone 2 Reheat Air Outlet Node;
                             !- Coil_Air_Outlet_Node
COIL:Water:SimpleHeating,
!                                                                                                           Name of cooling coil
    Reheat Coil Zone 3,      !- Coil Name
!                                                                                                           Cooling Coil Schedule
    Work Eff Sch,            !- Available Schedule
!                                                                                                           UA of the Coil
    400,                     !- UA of the Coil {W/K}
!                                                                                                           Max Water Flow Rate of Coil kg/sec
    1.8,                     !- Max Water Flow Rate of Coil {kg/s}
!                                                                                                           Coil Water Side Inlet & Outlet Node
    Zone 3 Reheat Water Inlet Node,
                             !- Coil_Water_Inlet_Node
    Zone 3 Reheat Water Outlet Node,
                             !- Coil_Water_Outlet_Node
!                                                                                                           Coil Air Side Inlet & Outlet Node
    Zone 3 Reheat Air Inlet Node,
                             !- Coil_Air_Inlet_Node
    Zone 3 Reheat Air Outlet Node;
                             !- Coil_Air_Outlet_Node
!-   ===========  ALL OBJECTS IN CLASS: COIL:GAS:HEATING ===========
COIL:Gas:Heating,
!                                                                                                            Coil Name
    Desiccant Regen Coil ,   !- Coil Name
!                                                                                                            Available Schedule
    Work Eff Sch,            !- Available Schedule
!                                                                                                            Gas Burner Efficiency of the Coil
    0.8,                     !- Gas Burner Efficiency of the Coil
!                                                                                                            Nominal Capacity of the Coil
    10000,                   !- Nominal Capacity of the Coil {W}
!                                                                                                            Coil_Air_Inlet_Node
    Regen Coil Inlet Node,   !- Coil_Air_Inlet_Node
!                                                                                                            Coil_Air_Outlet_Node
    Regen Coil Out Node ;    !- Coil_Air_Outlet_Node
!-   ===========  ALL OBJECTS IN CLASS: COIL:WATER:DETAILEDFLATCOOLING ===========
COIL:Water:DetailedFlatCooling,
!                                                                                                           Name of cooling coil
    Detailed Cooling Coil,   !- Coil Name
!                                                                                                           Cooling Coil Schedule
    Work Eff Sch,            !- Available Schedule
!                                                                                                           Max Water Flow Rate of Coil kg/sec
    1.1,                     !- Max Water Flow Rate of Coil {kg/s}
!                                                                                                           Tube Outside Surf Area
    6.23816,                 !- Tube Outside Surf Area {m2}
!                                                                                                           Tube Inside Surf Area
    6.20007018,              !- Total Tube Inside Area {m2}
!                                                                                                           Fin Surf Area
    101.7158224,             !- Fin Surface Area {m2}
!                                                                                                           Min Air Flow Area
    0.300606367,             !- Minimum Air Flow Area {m2}
!                                                                                                           Coil Depth
    0.165097968,             !- Coil Depth {m}
!                                                                                                           Coil Height
    0.43507152,              !- Fin Diameter {m}
!                                                                                                           Fin Thickness
    0.001499982,             !- Fin Thickness {m}
!                                                                                                           Tube Inside Diameter
    0.014449958,             !- Tube Inside Diameter {m}
!                                                                                                           Tube Outside Diameter
    0.015879775,             !- Tube Outside Diameter {m}
!                                                                                                           Tube Thermal Conductivity
    0.385764854,             !- Tube Thermal Conductivity {W/m-K}
!                                                                                                           Fin Thermal Conductivity
    0.203882537,             !- Fin Thermal Conductivity {W/m-K}
!                                                                                                           Fin Spacing
    0.001814292,             !- Fin Spacing {m}
!                                                                                                           Tube Depth
    0.02589977,              !- Tube Depth Spacing {m}
!                                                                                                           Number of Tube Rows
    6,                       !- Number of Tube Rows
!                                                                                                           Number of Tubes per Row
    16,                      !- Number of Tubes per Row
!                                                                                                           Coil Water Side Inlet & Outlet Node
    Cooling Coil Water Inlet Node,
                             !- Coil_Water_Inlet_Node
    Cooling Coil Water Outlet Node,
                             !- Coil_Water_Outlet_Node
!                                                                                                           Coil Air Side Inlet & Outlet Node
    Cooling Coil Air Inlet Node,
                             !- Coil_Air_Inlet_Node
    Air Loop Outlet Node;    !- Coil_Air_Outlet_Node
!-   ===========  ALL OBJECTS IN CLASS: FAN:SIMPLE:CONSTVOLUME ===========
FAN:SIMPLE:ConstVolume,
!                                                                                                           Fan Name
    Supply Fan 1,            !- Fan Name
!                                                                                                           Fan Schedule
    ON,                      !- Available Schedule
!                                                                                                           Fan Efficiency
    0.95,                    !- Fan Total Efficiency
!                                                                                                           Delta Pressure [N/M^2]
    1,                       !- Delta Pressure {Pa}
!                                                                                                           Max Vol Flow Rate  [m^3/Sec]
    6,                       !- Max Flow Rate {m3/s}
!                                                                                                           motor efficiency
    0.9,                     !- Motor Efficiency
!                                                                                                           motor in air stream fraction
    0,                       !- Motor In Airstream Fraction
    Mixed Air Node,          !- Fan_Inlet_Node
!                                                                                                           Inlet Node, Outlet Node
    Cooling Coil Air Inlet Node 1;
                             !- Fan_Outlet_Node
FAN:SIMPLE:ConstVolume,
!                                                                                                            A5 ; \field Coil_Temp_Setpoint_Node
!                                                                                                                \note optional if coil is temp and not load controlled
!                                                                                                           Fan Name
    Desiccant Regen Fan,     !- Fan Name
!                                                                                                           Fan Schedule
    Work Eff Sch,            !- Available Schedule
!                                                                                                           Fan Efficiency
    0.7,                     !- Fan Total Efficiency
!                                                                                                           Delta Pressure [N/M^2]
    600,                     !- Delta Pressure {Pa}
!                                                                                                           Max Vol Flow Rate  [m^3/Sec]
    1,                       !- Max Flow Rate {m3/s}
!                                                                                                           motor efficiency
    0.9,                     !- Motor Efficiency
!                                                                                                           motor in air stream fraction
    0,                       !- Motor In Airstream Fraction
    Outside Air Inlet Node 2,!- Fan_Inlet_Node
!                                                                                                           Inlet Node, Outlet Node
    Regen Coil Inlet Node;   !- Fan_Outlet_Node
FAN:SIMPLE:ConstVolume,
    Supply Fan 2,            !- Fan Name
    Work Eff Sch,            !- Available Schedule
    0.7,                     !- Fan Total Efficiency
    600,                     !- Delta Pressure {Pa}
    1,                       !- Max Flow Rate {m3/s}
    0.9,                     !- Motor Efficiency
    0,                       !- Motor In Airstream Fraction
    Outside Air Inlet Node 2,!- Fan_Inlet_Node
    fan heat recovery outlet node;
                             !- Fan_Outlet_Node
!-   ===========  ALL OBJECTS IN CLASS: EVAPCOOLER:INDIRECT:CELDEKPAD ===========
EvapCooler:InDirect:CelDekPad,
!                                           EvapCooler Name
    evaporative 1,           !- EvapCooler Name
!                                           Evap Schedule
    nightventilation,        !- Available Schedule
!                                           Pad Area in m^2
    1.6,                     !- Direct Pad Area {m2}
!                                           Pad Depth in m
    0.4,                     !- Direct Pad Depth {m}
!                                           Pump Power in W
    225,                     !- Recirc Water Pump Power Consumption {W}
!                                           Indirect Pad Fan Flow Rate in m^3/s
    10,                      !- Secondary Fan Flow Rate {m3/s}
!                                           Indirect Fan Efficiency
    0.9,                     !- Secondary Fan Efficiency
!                                           Indirect Fan Delta Pressure in Pa
    200,                     !- Secondary Fan Delta Pressure {Pa}
!                                           Indirect Heat Exchanger Effectiveness
    0.9,                     !- Indirect Heat Exchanger Effectiveness
    Cooling Coil Air Inlet Node 1,
                             !- Evap_Air_Inlet_Node
    Cooling Coil Air Inlet Node ,
                             !- Evap_Air_Outlet_Node
    Constant ;               !- Control Type
!-   ===========  ALL OBJECTS IN CLASS: DESICCANT DEHUMIDIFIER:SOLID ===========
DESICCANT DEHUMIDIFIER:SOLID,
    Desiccant 1,             !- Name
    Work Eff Sch,            !- Availability Schedule
    Outside Air Inlet Node,  !- Process Air Inlet Node
    Desiccant Process Outlet Node,
                             !- Process Air Outlet Node
    Regen Coil Out Node,     !- Regen Air Inlet Node
    Outside Air Inlet Node 2,!- Regen Fan Inlet Node
    LEAVING HUMRAT:BYPASS,   !- Control Type
    0,                       !- Leaving Max Humidity Ratio Setpoint
    0.007,                   !- Nominal Process Air Flow Rate {m3/s}
    1,                       !- Nominal Process Air Velocity {m/s}
    3.556,                   !- Nominal Regen Air Flow Rate {m3/s}
    1,                       !- Nominal Process Air Entering Dry Bulb {C}
    1,                       !- Nominal Process Air Entering Humidity Ratio {kgWater/kgAir}
    1,                       !- Nominal Water Removal Capacity {kg/m3}
    1,                       !- Nominal Regen Energy {J/kg}
    1,                       !- Rotor Power {W}
    Desiccant Regen Coil ,   !- Regen Coil Name
    Desiccant Regen fan,     !- Regen Fan Name
    Desiccant Regen Fan,     !- Performance Model
    ,                        !- Leaving Dry Bulb fTW Curve
    Desiccant DryBulb fTW Curve,
                             !- Leaving Dry Bulb fV Curve
    Desiccant DryBulb fV Curve,
                             !- Leaving Humidity Ratio fTW Curve
    Desiccant HumRat fTW Curve,
                             !- Leaving Humidity Ratio fV Curve
    Desiccant HumRat fV Curve,
                             !- Regen Energy fTW Curve
    Desiccant RegenEnergy fTW Curve,
                             !- Regen Energy fV Curve
    Desiccant RegenEnergy fV Curve,
                             !- Regen Velocity fTW Curve
    Desiccant RegenVel fTW Curve,
                             !- Regen Velocity fV Curve
    80;                      !- Nominal Regen Temperature {C}
!-   ===========  ALL OBJECTS IN CLASS: HEAT EXCHANGER:AIR TO AIR:FLAT PLATE ===========
HEAT EXCHANGER:AIR TO AIR:FLAT PLATE,
    OA Heat Recovery 1,      !- Name
    nightventilationh,       !- Available Schedule
!                                                                                                            flow arrangement
    Counter Flow,            !- flow arrangement
!                                                                                                            econo lockout
    no,                      !- Economizer lockout
!                                                                                                            hA ratio
    1,                       !- hA ratio
!                                                                                                            primary air volume flow rate
    5,                       !- Nominal supply air flow rate {m3/s}
!                                                                                                            primary air inlet temperature
    5,                       !- Nominal supply air inlet temperature {C}
!                                                                                                            primary air outlet temperature
    19,                      !- Nominal supply air outlet temperature {C}
!                                                                                                            secondary air volume flow rate
    5,                       !- Nominal secondary air flow rate {m3/s}
!                                                                                                            secondary air inlet temperature
    20,                      !- Nominal secondary air inlet temperature {C}
!                                                                                                            nominal power consumption
    0,                       !- Nominal electric power {W}
!                                                                                                            primary inlet node
    outside air inlet node,  !- Supply air inlet node
!                                                                                                            primary outlet node
    Heat Recovery Outlet Node,
                             !- Supply air outlet node
!                                                                                                            secondary inlet node
    Relief Air Outlet Node,  !- Secondary air inlet node
!                                                                                                            secondary outlet node
    Heat Recovery Secondary Outlet Node;
                             !- Secondary air outlet node
HEAT EXCHANGER:AIR TO AIR:FLAT PLATE,
    OA Heat Recovery 2,      !- Name
    ON,                      !- Available Schedule
    Counter Flow,            !- flow arrangement
    yes,                     !- Economizer lockout
    1,                       !- hA ratio
    0.6,                     !- Nominal supply air flow rate {m3/s}
    5,                       !- Nominal supply air inlet temperature {C}
    19,                      !- Nominal supply air outlet temperature {C}
    0.6,                     !- Nominal secondary air flow rate {m3/s}
    20,                      !- Nominal secondary air inlet temperature {C}
    0,                       !- Nominal electric power {W}
    outside air inlet node,  !- Supply air inlet node
    Heat Recovery Outlet Node,
                             !- Supply air outlet node
    Relief Air Outlet Node,  !- Secondary air inlet node
    Heat Recovery Secondary Outlet Node;
                             !- Secondary air outlet node
!-   ===========  ALL OBJECTS IN CLASS: SET POINT MANAGER:SCHEDULED ===========
SET POINT MANAGER:SCHEDULED,
!                                                                                                           ******************************************************
!                                                                                                            Set Point Manager Specification
    Supply Air Temp Manager, !- Name
    TEMP,                    !- Control variable
    Seasonal Reset Supply Air Temp Sch,
                             !- Schedule Name
    Supply Air Temp Nodes;   !- Name of the set point Node List
SET POINT MANAGER:SCHEDULED,
    Mixed Air Temp Manager,  !- Name
    TEMP,                    !- Control variable
    Seasonal Reset Supply Air Temp Sch,
                             !- Schedule Name
    Mixed Air Nodes;         !- Name of the set point Node List
!-   ===========  ALL OBJECTS IN CLASS: CONTROLLER:SIMPLE ===========
CONTROLLER:SIMPLE,
!                                                                                                           ******************************************************
!                                                                                                            Controller Specification
!                                                                                                           Controller Name
    Main Cooling Coil Controller,
                             !- Name
!                                                                                                           Control Variable
    TEMP,                    !- Control variable
!                                                                                                           Action
    Reverse,                 !- Action
!                                                                                                           Actuator variable
    FLOW,                    !- Actuator variable
!                                                                                                           Control node name
    Air Loop Outlet Node,    !- Control_Node
!                                                                                                           Actuator Node name
    Cooling Coil Water Inlet Node,
                             !- Actuator_Node
!                                                                                                           Convergence Tolerance
    0.1,                     !- Controller Convergence Tolerance: delta temp from setpoint temp {C}
!                                                                                                           Throttling Range
    6,                       !- Throttling Range: maximum controlled temperature range {C}
!                                                                                                           Max Actuated {Flow: kg/sec}
    1.1,                     !- Max Actuated Flow {kg/s}
!                                                                                                           Min Actuated {Flow: kg/sec}
    0;                       !- Min Actuated Flow {kg/s}
!-   ===========  ALL OBJECTS IN CLASS: CONTROLLER:OUTSIDE AIR ===========
CONTROLLER:OUTSIDE AIR,
    OA Controller 1,         !- Name
    NO ECONOMIZER,           !- EconomizerChoice
    NO RETURN AIR TEMP LIMIT,!- ReturnAirTempLimit
    RETURN AIR ENTHALPY LIMIT,
                             !- ReturnAirEnthalpyLimit
    LOCKOUT,                 !- Lockout
    FIXED MINIMUM,           !- MinimumLimit
    Mixed Air Node,          !- Control_Node
    Outside Air Inlet Node,  !- Actuated_Node
    3,                       !- minimum outside air flow rate {m3/s}
    3,                       !- maximum outside air flow rate {m3/s}
    28,                      !- temperature limit {C}
    4,                       !- temperature lower limit {C}
    47000,                   !- enthalpy limit {J/kg}
    Relief Air Outlet Node,  !- Relief_Air_Outlet_Node
    Air Loop Inlet Node,     !- Return_Air_Node
    nightventilationh;       !- Minimum Outside Air Schedule Name
!-   ===========  ALL OBJECTS IN CLASS: FLUIDNAMES ===========
FluidNames,
!                                                                                                             These are report variables Linda uses to trace changes
!                                                                                                            Please leave them in!!!!!
!                                                                                                           report variable,,outdoor dry bulb,timestep;
!                                                                                                           report variable,,mean air temperature,timestep;
!                                                                                                           report variable,,zone latent load,timestep;
!                                                                                                           report variable,,lights return air load,timestep;
!                                                                                                           report variable,,electric load,timestep;
!                                                                                                           report variable dictionary;
!                                                                                                           report,surfaces,dxf;
!                                                                                                            ***************************************************
!                                                                                                            FLUID PROPERTIES DATA
!                                                                                                            ***************************************************
!                                                                                                            unique list of fluid names which are valid for EnergyPlus (specifically fluid property routines)
    Water,                   !- fluid name 1
    GLYCOL;                  !- type of fluid for fluid name 1
!-   ===========  ALL OBJECTS IN CLASS: FLUIDPROPERTYTEMPERATURES ===========
FluidPropertyTemperatures,
    GlycolTemperatures,      !- temperature list name
    -35,                     !- temperature 1
    -30,                     !- temperature 2
    -25,                     !- temperature 3
    -20,                     !- temperature 4
    -15,                     !- temperature 5
    -10,                     !- temperature 6
    -5,                      !- temperature 7
    0,                       !- temperature 8
    5,                       !- temperature 9
    10,                      !- temperature 10
    15,                      !- temperature 11
    20,                      !- temperature 12
    25,                      !- temperature 13
    30,                      !- temperature 14
    35,                      !- temperature 15
    40,                      !- temperature 16
    45,                      !- temperature 17
    50,                      !- temperature 18
    55,                      !- temperature 19
    60,                      !- temperature 20
    65,                      !- temperature 21
    70,                      !- temperature 22
    75,                      !- temperature 23
    80,                      !- temperature 24
    85,                      !- temperature 25
    90,                      !- temperature 26
    95,                      !- temperature 27
    100,                     !- temperature 28
    105,                     !- temperature 29
    110,                     !- temperature 30
    115,                     !- temperature 31
    120,                     !- temperature 32
    125;                     !- temperature 33
!-   ===========  ALL OBJECTS IN CLASS: FLUIDPROPERTYCONCENTRATION ===========
FluidPropertyConcentration,
!                                                                                                            Specific heat in J/kg-K
    Water,                   !- fluid name (ethylene glycol, etc.)
    SPECIFICHEAT ,           !- fluid property type
    GlycolTemperatures,      !- temperatures list name
!                                                                                                            Concentration
    0,                       !- concentration {percentage (as a real decimal)}
    0,                       !- property value 1
    0,                       !- property value 2
    0,                       !- property value 3
    0,                       !- property value 4
    0,                       !- property value 5
    0,                       !- property value 6
    0,                       !- property value 7
    4217,                    !- property value 8
    4198,                    !- property value 9
    4191,                    !- property value 10
    4185,                    !- property value 11
    4181,                    !- property value 12
    4179,                    !- property value 13
    4180,                    !- property value 14
    4180,                    !- property value 15
    4180,                    !- property value 16
    4180,                    !- property value 17
    4181,                    !- property value 18
    4183,                    !- property value 19
    4185,                    !- property value 20
    4188,                    !- property value 21
    4192,                    !- property value 22
    4196,                    !- property value 23
    4200,                    !- property value 24
    4203,                    !- property value 25
    4208,                    !- property value 26
    4213,                    !- property value 27
    4218,                    !- property value 28
    4223,                    !- property value 29
    4228,                    !- property value 30
    4233,                    !- property value 31
    4238,                    !- property value 32
    4243;                    !- property value 33
FluidPropertyConcentration,
!                                                                                                            Specific heat in J/kg-K
    Water,                   !- fluid name (ethylene glycol, etc.)
    SPECIFICHEAT ,           !- fluid property type
    GlycolTemperatures,      !- temperatures list name
!                                                                                                            Concentration
    1,                       !- concentration {percentage (as a real decimal)}
    0,                       !- property value 1
    0,                       !- property value 2
    0,                       !- property value 3
    0,                       !- property value 4
    0,                       !- property value 5
    0,                       !- property value 6
    0,                       !- property value 7
    4217,                    !- property value 8
    4198,                    !- property value 9
    4191,                    !- property value 10
    4185,                    !- property value 11
    4181,                    !- property value 12
    4179,                    !- property value 13
    4180,                    !- property value 14
    4180,                    !- property value 15
    4180,                    !- property value 16
    4180,                    !- property value 17
    4181,                    !- property value 18
    4183,                    !- property value 19
    4185,                    !- property value 20
    4188,                    !- property value 21
    4192,                    !- property value 22
    4196,                    !- property value 23
    4200,                    !- property value 24
    4203,                    !- property value 25
    4208,                    !- property value 26
    4213,                    !- property value 27
    4218,                    !- property value 28
    4223,                    !- property value 29
    4228,                    !- property value 30
    4233,                    !- property value 31
    4238,                    !- property value 32
    4243;                    !- property value 33
!-   ===========  ALL OBJECTS IN CLASS: REPORT VARIABLE ===========
Report Variable,
    *  ,                     !- Key_Value
    Mean Air Temperature,    !- Variable_Name
    hourly,                  !- Reporting_Frequency
    ReportSch;               !- Schedule_Name
Report Variable,
    *  ,                     !- Key_Value
    Zone/Sys Sensible Heating Energy,
                             !- Variable_Name
    hourly,                  !- Reporting_Frequency
    ReportSch;               !- Schedule_Name
Report Variable,
    *  ,                     !- Key_Value
    Zone/Sys Sensible Cooling Energy,
                             !- Variable_Name
    hourly,                  !- Reporting_Frequency
    ReportSch;               !- Schedule_Name
Report Variable,
    *  ,                     !- Key_Value
    Zone/Sys Air Temp,       !- Variable_Name
    hourly,                  !- Reporting_Frequency
    ReportSch;               !- Schedule_Name
Report Variable,
    *,                       !- Key_Value
    Outdoor Dry Bulb,        !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *,                       !- Key_Value
    Outdoor Wet Bulb,        !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *,                       !- Key_Value
    Outdoor Humidity Ratio,  !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *,                       !- Key_Value
    Outdoor Enthalpy,        !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *,                       !- Key_Value
    Total Latent Gain,       !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
!                                                                                                             SET POINT MANAGER:SINGLE ZONE MIN HUM,
!                                                                                                               Zone Min Set Point Manager,
!                                                                                                               HUMRAT,
!                                                                                                               Min Relative Hum Set Sch,
!                                                                                                               Air Loop Outlet Node,
!                                                                                                               Zone 2 Node;
!                                                                                                           Report Variable,  , Mean Air Temperature, hourly;
!                                                                                                           Report Variable,  , Mean Radiant Temperature, hourly;
    ,                        !- Key_Value
    Zone/Sys Sensible Heating Energy,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    ,                        !- Key_Value
    Zone/Sys Sensible Cooling Energy,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    ,                        !- Key_Value
    Zone/Sys Sensible Cooling Rate,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    ,                        !- Key_Value
    Zone/Sys Sensible Heating Rate,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    ,                        !- Key_Value
    Zone/Sys Air Temp,       !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    ,                        !- Key_Value
    Zone Air Humidity Ratio, !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    ,                        !- Key_Value
    Total Water Heating Coil Rate,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    ,                        !- Key_Value
    outdoor dry bulb,        !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    ,                        !- Key_Value
    Zone-Total Latent Gain,  !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    Heat Recovery Outlet Node,
                             !- Key_Value
    System Node Temp,        !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    Relief Air Outlet Node,  !- Key_Value
    System Node Humidity Ratio,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    Heat Recovery Secondary Outlet Node,
                             !- Key_Value
    System Node Humidity Ratio,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    Air Loop Outlet Node,    !- Key_Value
    System Node Humidity Ratio,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    Air Loop Inlet Node,     !- Key_Value
    System Node Humidity Ratio,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *  ,                     !- Key_Value
    Total Convective Heat Gain,
                             !- Variable_Name
    hourly,                  !- Reporting_Frequency
    ReportSch;               !- Schedule_Name
Report Variable,
    *  ,                     !- Key_Value
    Outdoor Relative Humidity,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *  ,                     !- Key_Value
    Zone Air Relative Humidity,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *  ,                     !- Key_Value
    Zone/Sys latent Heating Energy,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *  ,                     !- Key_Value
    Zone/Sys latent cooling Energy,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *  ,                     !- Key_Value
    Average,                 !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *  ,                     !- Key_Value
    Sensible Heat Recovery Energy,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *  ,                     !- Key_Value
    System Node MassFlowRate,!- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *,                       !- Key_Value
    FangerPMV,               !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *,                       !- Key_Value
    PierceDISC,              !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    ,                        !- Key_Value
    Zone/Sys Moisture Load Rate Predicted,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    ,                        !- Key_Value
    Inside Surface Mass Flux,!- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    ,                        !- Key_Value
    Inside Surface Humidity Ratio,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    ,                        !- Key_Value
    Outside Surface Mass Flux,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
!-   ===========  ALL OBJECTS IN CLASS: REPORT METER ===========
Report Meter,
    ExteriorEquipment*,      !- Meter_Name
    hourly;                  !- Reporting_Frequency
Report Meter,
    Electricity:*,           !- Meter_Name
    hourly;                  !- Reporting_Frequency
!-   ===========  ALL OBJECTS IN CLASS: REPORT ===========
Report,
    Variable Dictionary;     !- Type_of_Report
Report,
    surfaces,                !- Type_of_Report
    dxf;                     !- Name_of_Report
Report,
    construction;            !- Type_of_Report
Report,
    Variable Dictionary;     !- Type_of_Report
======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
    
    
More information about the Bldg-sim
mailing list