> In energy plus, can a zone surface facing another zone surface be sun
> exposed, if the second zone surface is part of a zone with all glass
> surfaces? (example: double skin facade)
>
Yes, but only if you select Solar Distribution =
FullInteriorAndExterior (in the BUILDING object). With this option
selected, direct sunlight is projected into the space onto the other
zone surfaces. If this option is not selected, then all direct
sunlight entering the space is projected onto the floor surfaces.
Use of this option requires that the zone be a completely enclosed
convex volume. EnergyPlus will also transmit sunlight from one zone
into another through a window placed on an interior wall. This may
be the configuration you have with your double-skin facade.
========================================================