[BLDG-SIM] Boiler Performance Curves
Michael Wilson
mwilsonbc at yahoo.com
Thu Feb 13 11:38:58 PST 2003
I haven't used Doe 2.2, just Doe2.1e, but I suspect
the problems with the boiler are the same. There's a
bit of a glitch in the boiler model when it comes to
part load, as Doe2 considers the boiler capable of
cycling "OFF". When it does, no energy is consumed. Of
course in reality boilers aren't OFF unless somebody
shuts them down for summer. When they're not firing
they still have jacket and stack losses, which have to
be accounted for when the boiler fires again. But in
Doe2, a boiler with a higher part load ratio will
cycle "OFF" more often, reducing consumption. So a
boiler with a low part load ratio will be less
efficient than one with a high PLR, the opposite of
what it should be. I get around this by specifying
boilers with a minimum PLR of 0.001 and then
incorporating all the losses and the cycling action
into the boiler curve.
Michael Wilson
--- Fred Porter <fporter at archenergy.com> wrote:
---------------------------------
Additionally:
First, in DOE2.x, if I'm not mistaken, the BOILER
"MIN-RATIO," or cyclingthreshold, holds the efficiency
(PLR modified EIR) constant below the specifiedPLR,
contrary to reality and intuition. I think this input
defaults to aPLR of 20%, just a bit above where boiler
efficiency starts to really godown the tubes. So this
needs to be dropped to a very low value(where
yourEIR-fPLR curve goes wacko) if you roll your own
curves.
Aquastat temp (under BOILER), and HW reset
scheds(HW-LOOP) can also have major effects. Actually
you need to create another custom curve(HIR-FT),and
reduce the aquastat minimum, if you want the HW temp
to interact withthe boiler, which it most certainly
does. See the DOE2.2 BOILER docs.
Also, if you set up your model with optimistic
assumptions (most defaults),you may miss many hours at
very low (<5%) heating loads.
In any case, most modulating boilers go down to 20 or
25%, and so may notshow great savings compared to a
33% low fire.
A method of calculating part load efficiency for
boilers is outlined in thespreadsheets that can be
downloaded from:
http://www.keh-ee.com/cycling.htm
These require some modification and care in use for
purpose of developingDOE2 curves. Steady-state
efficiency may vary somewhat with load, producingthe
manufacturer's cited increase in efficiency at 50%
load. This cited efficiencyimprovment may also take
into account some assumed HW reset, much as ARINPLV
chiller points include condenser "relief," at the
lower loads.
GOOD LUCK! In consideration of the other thread: Even
with 3D IFC/DXF interfaces,architects (are any still
reading) should not attempt this.
Fred
Wade McLaughlin wrote:
Hello All, As part of a comprehensive energy
studyfor a new elementary school, we are analyzing
fuel savings opportunitiesfor a proposed boiler with
fully modulating burners as compared to a
base-casesectional lo-hi-lo boiler. So far, we have
found that, all things beingequal, there are no
significant savings associated with such a measure
(atleast not for the boiler size and models we've been
considering). We use PowerDOE for most of our
energy simulations. In the course of this study, we
have come to question the default boiler part-load
heat-input-ratio curve (HW-Blr-HIR-fPLR) found in
Bdllib.dat. Until now, we have applied this curveto
most base-case boiler calculations (perhaps
mistakenly?). Does anyoneknow of the origins of this
curve or what it would have been based upon? Most
manufacturers we have spoken with state that peak
boiler efficiencyoccurs between 25% and 50% load.
Using the default curve, peak performanceoccurs at
full load and efficiency decreases by nearly 10% at
half load. Also, if this curve is in error, can
anyonesuggest a method for developing a more
reasonable curve estimate? Thanks, Wade Wade
McLaughlin
DMI
450 Lexington St.
Newton, MA 02466
p 617-527-1525 x103
f 617-527-6606
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================You
received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM mailing list. To unsubscribe from
this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
=====
Michael Wilson
455 Elphinstone Ave.
Gibsons, BC, V0N 1V1
604-886-9864 phone
604-676-2604 fax
__________________________________________________
Do you Yahoo!?
Yahoo! Shopping - Send Flowers for Valentine's Day
http://shopping.yahoo.com
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list