[BLDG-SIM] DOE2.1E Chiller performance
Fred Porter
fporter at archenergy.com
Fri May 16 10:10:59 PDT 2003
The old default DOE2 centrifugal chiller curves, evaluated directly for
leaving CHW Ts of 42 & 38 and completely independently of any other
inputs, show a consistent increase in chiller kW/ton of 11% for a range
of normal CW temperatures. The newer DOE2.2 curves use "lift"(CW-CHW)
and part load fraction in addition to a new CHW & CW, so I can't
evaluate the default curves as directly. There are other adjustments for
performance under varying, or off-rated, primary flow and temperature
that must be accounted for.
Results from TRACE probably reflect Trane chiller performance, which
tends to be less sensitive to chiller "lift," and more suited for these
lower temperature applications.
So even preliminary analysis can be biased by either generic or
manufacturer-specific curves, and the limitations of the simulation.
Resets of CHW, CW, and pressure along with coil performance, etc,
interact to affect the "optimum" system. Lowest life-cycle cost SYSTEMS
using different manufacturers' chillers may be very different.
Varkie Thomas wrote:
>This is in response to comments and questions that I received.
>
>This was a preliminary attempt using DOE2.1E to find out large tonnage chiller energy usage at decreasing LWTs and a fixed EWT to reduce the CHW-flow. I may not have used the DOE2.1E correctly because results showed the chiller LWT was always the default value of 44F. The test building was a single zone per floor, 70% single glass, with multiple floors to produce over 6000 tons. The DOE2 program was run with SOM office building template defaults. The TRACE program was run twice, with all TRACE defaults for an office building, VAV system and water-cooled centrifugal chillers, first with CHW temp range of 38 to 56 and next with 42 to 56. In the first case the program gave warning messages for LWT < 40 and CHW-DT > 15.
>
>The energy usage of a chiller operating from 38 to 56 was higher, but not significantly higher (relative to potential savings in the pump operating, heat transfer equipment and piping costs) than 42 to 56. This might be because of limitations in the energy program algorithms, and actual physical tests with chillers might produce different results. Cooling coil sizes in terms of fins, rows, etc are going to be affected. I did not check this out using cooling coil selection programs. I did not check or compare the results of the air-side system equipment performance.
>
>What would be the results from other energy programs such EnergyPlus, HAP and eQUEST? I would be particularly interested in the results from HAP. We do not have this program in this office. I would also be interested in comments from Trane regarding the results from TRACE. Was the program used incorrectly?
>
>Varkie
>-------------------------------------------
>
>-----Original Message-----
>From: Varkie Thomas
>Sent: Thursday, May 15, 2003 8:48 AM
>To: BLDG-SIM at gard.com
>Subject: [BLDG-SIM] DOE2.1E Chiller performance
>
>
>To those who responded to this inquiry:
>
>We tested the two conditions with TRACE-700. There is little difference in the energy consumed by the chillers for CHW temp range of 38F to 56F and 44F to 56F particularly in the large tonnage range. This is also indicated in chiller performance data catalogs. There is a big difference in pumping and piping costs.
>
>Varkie Thomas
>---------------------------------------
>
>We are trying to compare the performance of a 2000 ton chiller operating at (1) 42 F LWT and (2) 38 F LWT. The chiller EWT is 56 in both cases. The tower temp range is 85 F to 100 F. We want to know how the chiller COP varies under these conditions.
>
>The hourly output for the design day from DOE2.1E shows chiller LWT of 44 F (DOE2 default) no matter what the input. Here is the input and output for the option with 38 F Chiller LWT. Can the Chiller LWT be changed from the default value of 44 F ? How do I check that the CHW EWT & LWT temps are being maintained? Is the input below correct to model the conditions described?
>
>----------------------------------------------------------------
>
>PLANT-PARAMETERS
>
>CHILL-WTR-T = 37 $ Def = 44. LWT at bottom of Thrott Range $
>CHILL-WTR-THROTT = 2.0 $ Def = 2.5. Thrott Range = 37 to 39. LWT = 38 $
>
>TWR-SETPT-T = 85
>TWR-DESIGN-RANGE = 15.0 $ Def = 10. Tower temp range :85 to 100 $
>
>CCIRC-DESIGN-T-DROP = 18 $ Def = 10. Chiller EWT = 56 $
>
>----------------------------------------------------------------
>
>
>MMDDHH OPEN-CEN OPEN-CEN OPEN-CEN OPEN-CEN OPEN-CEN OPEN-CEN
> T-CHLR T-CHLR T-CHLR T-CHLR T-CHLR T-CHLR
> LOAD ELECTRIC OPER PT FRAC HR ENTERING LEAVING
> USE LD RATIO OPERATED COND TEM COLD TEM
> BTU/HR KW FRAC.OR FRAC.OR F F
> MULT. MULT.
> ----( 1) ----( 3) ----(10) ----(11) ----(12) ----(13)
> 7 1 1 0. 0.000 0.000 0.000 0.0 0.0
> 7 1 2 0. 0.000 0.000 0.000 0.0 0.0
> 7 1 3 0. 0.000 0.000 0.000 0.0 0.0
> 7 1 4 0. 0.000 0.000 0.000 0.0 0.0
> 7 1 5 0. 0.000 0.000 0.000 0.0 0.0
> 7 1 6 8887730. 528.301 0.328 1.000 84.6 44.0
> 7 1 7 20704076. 1019.228 0.760 1.000 83.7 44.0
> 7 1 8 25529894. 1301.530 0.940 1.000 84.3 44.0
> 7 1 9 25563408. 1312.150 0.944 1.000 84.7 44.0
> 7 110 22676038. 1142.870 0.838 1.000 84.9 44.0
> 7 111 23148816. 1167.610 0.855 1.000 84.7 44.0
> 7 112 22012680. 1103.797 0.813 1.000 84.7 44.0
> 7 113 22536236. 1132.213 0.832 1.000 84.7 44.0
> 7 114 22738694. 1144.069 0.840 1.000 84.7 44.0
> 7 115 22827700. 1149.287 0.843 1.000 84.7 44.0
> 7 116 22768860. 1146.011 0.841 1.000 84.7 44.0
> 7 117 21899154. 1097.228 0.809 1.000 84.7 44.0
> 7 118 20232738. 1007.025 0.747 1.000 84.7 44.0
> 7 119 0. 0.000 0.000 0.000 0.0 0.0
> 7 120 0. 0.000 0.000 0.000 0.0 0.0
> 7 121 0. 0.000 0.000 0.000 0.0 0.0
> 7 122 0. 0.000 0.000 0.000 0.0 0.0
> 7 123 0. 0.000 0.000 0.000 0.0 0.0
> 7 124 0. 0.000 0.000 0.000 0.0 0.0
>
>====================================================
>You received this e-mail because you are subscribed
>to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
>from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
--
Fred W. Porter
Senior Engineer
Architectural Energy Corp.
2540 Frontier Ave. Suite 201
Boulder CO 80301
email: fporter at archenergy.com
fax: 303-444-4304
office: 303-444-4149 x225
mobile: 303-748-4536
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list