Common problem. You are using a recent version of DOE2 based on an
implementation by Jeff Hirsch, but using documentation and keywords from
older versions. All CHW & HW characteristics are now declared in Systems
Plant Assignment, not Plant Plant Parameters, CW stuff is still in PLANT.
Correct documentation is available from DOE2.com. The v110 bdl
supplement or something like that.
However, for plant analysis at this level of detail, I would highly
recommend DOE2.2, instead of DOE2.1.
Varkie Thomas wrote:
> DOE2.1E shows chiller LWT of 44 F (DOE2 default) no matter what the input. Here is the input and output for the option with 38 F Chiller LWT.
>
>
>
>----------------------------------------------------------------
>
>PLANT-PARAMETERS
>
>CHILL-WTR-T = 37 $ Def = 44. LWT at bottom of Thrott Range $
>CHILL-WTR-THROTT = 2.0 $ Def = 2.5. Thrott Range = 37 to 39. LWT = 38 $
>
>TWR-SETPT-T = 85
>TWR-DESIGN-RANGE = 15.0 $ Def = 10. Tower temp range :85 to 100 $
>
>CCIRC-DESIGN-T-DROP = 18 $ Def = 10. Chiller EWT = 56 $
>
======================================================