[bldg-sim] Radiant Heating/Cooling
Laouadi, Aziz
Aziz.Laouadi at nrc-cnrc.gc.ca
Wed Apr 14 10:43:46 PDT 2004
Cost of radiant systems:
According to the Consumer Energy Information: EREC Reference Briefs, the
cost of installing a radiant floor heating system is approximately $4 to $6
per square foot, depending on the size of the room, the type of
installation, the floor covering, remoteness of the site and the cost of
labor. (additional info may be found in:
http://www.gamanet.org/publist/publistordr.htm).
Dr. Abdelaziz (Aziz) Laouadi
Research Officer
Indoor Environment Research Program
Institute for Research in Construction
National Research Council of Canada
1200 Montreal Road, Building M-24
Ottawa, Ontario, Canada, K1A 0R6
Tel.: (613) 990 6868; Fax: (613) 954 3733
Email: Aziz.Laouadi at nrc-cnrc.gc.ca
Web: http://irc.nrc-cnrc.gc.ca/ie/light/skyvision/
-----Original Message-----
From: postman at gard.com [mailto:postman at gard.com]On Behalf Of Rick Strand
Sent: Wednesday, April 14, 2004 10:14 AM
To: bldg-sim at gard.com
Subject: [bldg-sim] Radiant Heating/Cooling
Steve:
In my studies, I have not looked at the installation costs though such
information would obviously be an important part of the decision of whether
or not to install a radiant system. I have heard the $10,000 number before
and seem to recall seeing it in an ASHRAE Journal article. This number
does seem somewhat high though this may relate more to the lack of
contractor experience with installing the systems. I am sure there are
others who participate in this mail list that can provide better answers to
this question.
I agree that the cost effectiveness question is a serious issue. If, due
to humidity/condensation concerns, it is necessary to use central air
conditioning, then it seems unlikely that one would go with a completely
different heating system (i.e., a radiant heating system). If the radiant
system will be able to provide both heating and cooling, then it certainly
seems more likely that a radiant system could be cost effective. In some
cases though, some people are willing to spend extra money up front because
they like some of the features of radiant heating (like, say, the warm
floor in the winter).
Rick
At 11:36 PM 4/13/2004, stvgates at pacbell.net wrote:
>Rick,
>
>Thanks for the information.
>
>Given that most houses built today have central air conditioning, the
>incremental cost of a forced-air heating unit is very small, probably on
the
>order of $1,000 for an 80% efficient unit (all of the equipment except for
>the furnace must be installed anyway). A radiant system is probably on the
>order of $10,000 additional for a 2,500 sq.ft. house.
>
>Questions:
>1. Did any of the studies you conducted address these costs? Are they
>reasonably accurate?
>2. If they are accurate, can the energy savings of a radiant system make
>the system even remotely cost effective?
>
>
>----- Original Message -----
>From: "Rick Strand" <rkstrand at uiuc.edu>
>To: <bldg-sim at gard.com>
>Sent: Tuesday, April 13, 2004 5:17 PM
>Subject: [bldg-sim] Radiant Heating/Cooling
>
>
>The discussion started by Dr. Laouadi has raised several issues related to
>radiant heating and cooling systems, and I will attempt to add some of my
>own perspective on these concerns raised by the various email
>postings. For those of you who are interested in modeling radiant heating
>and cooling systems, a model has been available in EnergyPlus for some time
>already and papers have been published regarding this model and its
>predecessor model which was part of a research version of the BLAST
>program. Some of these papers are available on the web from the EnergyPlus
>web site (www.energyplus.gov) and future papers describing some of the
>recent enhancements are in the works. Follow the link to Documentation and
>then to Research Papers and Articles. As Dr. Laouadi points out, an
>integrated radiant model (such as the one found in EnergyPlus) is essential
>to answering many of the questions posed here.
>
>In answering Question 1 from Steve, Dr. Laouadi pointed out in his email
>from earlier today that in many cases homeowners are not taking advantage
>of the potential for lowering their thermostat settings. That is not
>surprising as most homeowners are accustomed to the air systems. Steve
>noted: "But, if the thermostat is lowered to 65F, and the ambient
>temperature is 66F, then the radiant heat is off, and the mean radiant
>temperature drops." This is not exactly how the physics of all radiant
>systems work. Systems with any thermal mass will react more slowly than an
>"instantaneous" air system. The occupants will not notice a sudden drop in
>temperature because of the mass of the system. In addition, radiant
>systems are not typically "on-off" as forced air systems. Will there be
>greater variation in temperature or comfort? This depends on
>sophistication of the controls and the construction details. Clearly, more
>thought has to be put into the design of a radiant system. However, a
>poorly designed system, whether radiant or conventional forced air, will
>not make for a happy building owner.
>
>Question 2 from Steve asked whether the reduced infiltration loss or the
>increased surface heat loss will be the determining factor in whether a
>radiant system will be more energy efficient. Or, in a more broader sense,
>are radiant systems inherently more efficient than forced air systems. The
>answer is: it depends. In an ASHRAE paper, I showed that for a particular
>case while the average unheated surface temperature did increase slightly
>and thus increase the heat loss through those surfaces that the
>infiltration losses were higher. As a result, the radiant system was more
>efficient than the conventional forced air system. But this is by no means
>a definitive answer. It will depend on infiltration rates, exterior
>envelope construction, and other details. The question simply cannot be
>answered by a single study--which is why it is important to have simulation
>models that can help answer the question for a specific case. There are
>many single cases published in the literature that make great savings
>claims for radiant systems. They may be true for a particular building,
>but those numbers are not valid for *all* buildings.
>
>As for the delivery losses mentioned in Question 3, without appropriate
>insulation radiant systems are known to have problems with heat loss. Yet
>one also has to concede that fans consume quite a bit of energy. Which
>factor dominates? Again, it depends of various characteristics of the
>design.
>
>As far as setback issues are concerned, again it will depend on whether the
>system is a high mass system (like one embedded in concrete) or a low mass
>ceiling panel system. It is pretty clear that there is much less
>opportunity to effectively use simple setback controls with a high mass
>radiant system, but with more sophisticated controls on the system, one
>might be able to address these issues.
>
>Finally, I would invite all of those who are interested in radiant heating
>and cooling to become active in ASHRAE TC6.5. It would provide a further
>forum to discuss these issues and influence future research in this area.
>
>Rick Strand, Ph.D.
>Assistant Professor
>University of Illinois at Urbana-Champaign
>
>At 03:05 PM 4/13/2004, Alec Stevens wrote:
> >Steve
> >My 2c:
> >One aspect that should save energy on a radiant hydronic system is that
>your
> >supply and return water temps are lower year round than in a typical
> >convective system. If you consider a condensing hydronic boiler, you
>should
> >always be in condensing mode with radiant heat, but your HW reset
schedule
> >for other forms of hydronic heat would mean you would not be condensing
> >except when OA temps are relatively high (Above 40F?). Therefore, boiler
> >efficiency should be better with radiant for most of the heating season.
> >
> >You raise some good points about the other issues. I've only heard the
> >lower space temperature setpoint argument when it comes to spaces like
> >manufacturing areas, ice rinks, airplane hangars, etc. Don't think it
>would
> >apply so much to residential, especially if you are going to cycle zone
> >valves on and off. Modulating zone valves?
> >
> >
> >
> >Alec
> >
> >----- Original Message -----
> >From: <stvgates at pacbell.net>
> >To: <bldg-sim at gard.com>
> >Sent: Tuesday, April 13, 2004 11:48 AM
> >Subject: [bldg-sim] Radiant Heating/Cooling
> >
> >
> > > I also have some questions on radiant heating that I hope someone can
> > > answer:
> > >
> > > 1. It is well understood that, for a given comfort level, a higher
mean
> > > radiant temperature allows for a lower ambient temperature. This
>suggests
> > > that one can lower the thermostat setpoint. But, if the thermostat is
> > > lowered to 65F, and the ambient temperature is 66F, then the radiant
>heat
> >is
> > > off, and the mean radiant temperature drops. So are the people
> >comfortable
> > > when the space is 66F, or do they raise the thermostat?
> > >
> > > 2. Granted, infiltration heat losses can be lowered by reducing the
air
> > > temperature. But the radiant heat source is also warming the room
> >surfaces,
> > > including the exterior wall surfaces and window surfaces. If those
> >surface
> > > temperatures are then higher than they would be with a convective
>heating
> > > system, their conduction losses are now greater, even though the air
> > > temperature is lower. Also, infiltration/exfiltration losses are
> >typically
> > > through cracks. If the cracks in the interior surfaces are warmer
from
> > > radiant heating, then the crack warms the exfiltrating air, and space
> > > temperature is not a valid criterion for calculating exfiltration
loss.
> >So
> > > does a radiant heating system REALLY save any energy?
> > >
> > > 3. If the radiant elements are imbedded in the ceiling, which is
>common,
> > > the interior ceiling temperature can now be in excess of 90F, which
> > > increases the conduction losses to the attic. So if this loss is
>counted
> >as
> > > a delivery loss, the efficiency of the system drops compared to the
> > > theoretical. The same argument applies to radiant elements in floors.
>So
> > > is a radiant system REALLY any more efficient than a convective system
>in
> > > terms of delivered energy?
> > >
> > > 4. With a setback thermostat and a convective heating system, I can
>turn
> > > off the heat at night, but my home will be comfortable in less than a
>1/2
> > > hour the next morning. But most radiant heating systems have a slow
> > > response time. Do people turn them off/down at night, or do they run
>them
> > > continuously?
> > >
> > > ----- Original Message -----
> > > From: "Jon Maxwell" <jmaxwell at aspensys.com>
> > > To: <bldg-sim at gard.com>
> > > Sent: Monday, April 12, 2004 8:46 PM
> > > Subject: [bldg-sim] Radiant Heating/Cooling
> > >
> > >
> > > > I have modeled the savings for radiant systems for unvented low
> >intensity
> > > > gas fired radiant tube heating systems in high bay warehouses and
> > > > manufacturing facilities in particular by:
> > > >
> > > > 1. Reducing the setpoint dry bulb temperature a few degrees
>because
> > > > human comfort with radiant heating is reached at a lower ambient
than
> >with
> > > > convection heating systems. I am certain that comfort research
>supports
> > > > this.
> > > > 2. Reducing the setpoint temperature a few more degrees because
> >there
> > > is
> > > > less floor-to-ceiling temperature stratification. With the desired
> > > > temperature at belly button level, radiant systems will have a lower
> > > average
> > > > temperature floor-to-ceiling than unit heaters overall.
> > > > 3. Reducing the amount of infiltration, due to reduced stack
>effect,
> > > due
> > > > to reduced temperature stratification
> > > > 4. Increasing the heating system combustion efficiency slightly
>due
> >to
> > > > having no intermediate media such as air or water between the
>combustion
> > > air
> > > > and the space to be heated and lack of venting.
> > > >
> > > > While I cannot cite studies to validate the adjustments or quantify
>them
> > > > generally (though I have rules of thumb based on ceiling height),
such
> >an
> > > > approach has predicted savings roughly in the right ballpark, close
> >enough
> > > > to make a do/don't do decision at least.
> > > >
> > > > Would love to be able to cite rigorous research that proves or
>disproves
> > > my
> > > > approach.
> > > >
> > > > Jonathan B. Maxwell, PE
> > > > Senior Engineer
> > > > Aspen Systems Corporation
> > > > 710 Park Place
> > > > College Station, TX 77840
> > > > (979) 764-6779 wk
> > > > (979) 764-7810 fax
> > > > (979) 575-1281 mobile
> > > > jmaxwell at aspensys.com
> > > > www.OPUSPOWER.com
> > > > www.aspensys.com
> > > >
> > > > ----- Original Message -----
> > > > From: "Chris Jones" <cj at cr-jay.ca>
> > > > To: <BLDG-SIM at gard.com>
> > > > Sent: Monday, April 12, 2004 6:25 AM
> > > > Subject: [BLDG-SIM] Radiant Heating/Cooling
> > > >
> > > >
> > > > In your research with radiant heating cooling savings, have you
found
> >any
> > > > energy "savings" that can be attributed directly to the use of the
> >radiant
> > > > system vs other systems (air supply in particular). For example, I
>have
> > > > seen some papers that note that the heating setpoint can be relaxed
> >while
> > > > still maintaining thermal comfort with a radiant system.
> > > >
> > > >
> > > > At 10:47 07/04/2004, you wrote:
> > > > >Dear All,
> > > > >
> > > > >For those interested in the simulation of radiant heating/cooling
> > > systems,
> > > > >IRC has developed a semi-analytical model for integration in energy
> > > > >simulation software that use the one-dimensional numerical modeling
>to
> > > > >calculate the heat transfer within the building construction
> >assemblies.
> > > > >
> > > > >The model combines the one-dimensional model of the energy
simulation
> > > > >software with a two-dimensional analytical model. The advantage of
> >this
> > > > >model over the one-dimensional one is that it accurately predict
the
> > > > contact
> > > > >surface temperature of the circuit-tubing and the adjacent medium,
> > > required
> > > > >to compute the boiler/chiller power, and the minimum and maximum
> > > > >ceiling/floor temperatures, required for local moisture
condensation
> > > > >(ceiling cooling systems), thermal discomfort (heating floor
systems)
> >and
> > > > >controls. The model predictions for slab-on-grade heating systems
> > > compared
> > > > >very well with the results from a full two-dimensional numerical
>model.
> > > > >
> > > > >The model was implemented in the Canadian software HOT3000 and the
UK
> > > > >software ESP-r as a plant component. The implementation of this
model
> >in
> > > > the
> > > > >ESP-r program offers additional flexibilities to the radiant system
> > > > designer
> > > > >community, mainly:
> > > > >· Designers can use any control algorithm possible in ESP-r
>with
> > > the
> > > > >new plant component (e.g.., use the flux or temperature control,
and
> > > > compare
> > > > >their performance).
> > > > >· Designers can specify any number of radiant surfaces of the
> > > > building
> > > > >fed by the same or different heat source.
> > > > >· Designers can size realistic radiant systems, and get
>realistic
> > > > >energy consumption (from the source side) and cost.
> > > > >
> > > > >
> > > > >A copy may be downloaded from:
> > > > >Laouadi, A. "Development of a radiant heating and cooling model for
> > > > building
> > > > >energy simulation software," Building and Environment, 39, (4),
>April,
> > > pp.
> > > > >421-431, Apr, 2004
> > > > >(NRCC-46099)
> > > > ><http://irc.nrc-cnrc.gc.ca/fulltext/nrcc46099/>
> > > > >
> > > > >
> > > > >Thanks
> > > > >
> > > > >Dr. Abdelaziz (Aziz) Laouadi
> > > > >Research Officer
> > > > >Indoor Environment Research Program
> > > > >Institute for Research in Construction
> > > > >National Research Council of Canada
> > > > >1200 Montreal Road, Building M-24
> > > > >Ottawa, Ontario, Canada, K1A 0R6
> > > > >Tel.: (613) 990 6868; Fax: (613) 954 3733
> > > > >Email: Aziz.Laouadi at nrc-cnrc.gc.ca
> > > > >Web: http://irc.nrc-cnrc.gc.ca/ie/light/skyvision/
> > > > >
> > > > >
> > > > >You received this e-mail because you are subscribed
> > > > >to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> > > > >from this mailing list send a blank message to
> > > > >BLDG-SIM-UNSUBSCRIBE at GARD.COM
> > > >
> > > >
> > > > Chris Jones, P.Eng.
> > > > 14 Oneida Avenue
> > > > Toronto, ON M5J2E3
> > > > Tel. 416 203-7465
> > > > Fax. 416 946-1005
>
>==================
>You received this e-mail because you are subscribed
>to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
>from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
>======================================================
>You received this e-mail because you are subscribed
>to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
>from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at GARD.COM
=====================================================You received this
e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list