What you are doing is in the generally correct direction. I wouldn't
remove the lighting load from the equation just set the percentage of
heat going to the plenum at say 50%. I would calculate the ESHG for a
typical space and use the space operating temperature from the ESHG
calculations for the space operating temperature in DOE 2. Make sure the
supply temperature is 63F and check the calculated return temperature.
Don't forget to reduce the static pressure of the AHU down to about 2"
external. Compared to a conventional VAV your supply air volume will
increase but fan power will be reduced. You can also reset the chilled
water supply temperature to say 48F which will decrease chiller energy
consumption.
You overall results should be about 15-20% less than a conventional VAV.
Peter Simmonds Ph.D.
Associate,
IBE Consulting Engineers
5910 Lemona Ave. 3rd Floor
Van Nuys, CA 91411
USA
tel: 818-947-0000 #246
fax: 818-947-0047
Mobile USA: 818-219-1284
Mobile Europe: +44-7947-837-588
e-mail: peter.simmonds at ibece.net
-----Original Message-----
From: Gerald Pde [mailto:geraldpde at yahoo.com]
Sent: Friday, July 09, 2004 3:02 PM
To: BLDG-SIM at GARD.COM
Subject: [BLDG-SIM] eQUEST: Displacement Ventilation in offices
Hi All,
I am looking for a method for modeling displacement
ventilation in offices using eQUEST.
I could set supply air higher then the conventional
hvac and also cut off heat gain from lights.
Is there more advanced modeling methods on how to
model the plume in equest.
thanks,
Gerald
__________________________________
Do you Yahoo!?
Yahoo! Mail - 50x more storage than other providers!
http://promotions.yahoo.com/new_mail
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list