[BLDG-SIM] ground source heat pump in eQUEST
Liu, Bing
Bing.Liu at pnl.gov
Fri Mar 19 09:31:14 PST 2004
Smita,
Here are some steps to lead you to model GSHP system in eQuest:
1. Set up eQuest to Detailed Data Edit Mode
2. Go to Water-Side HVAC tab
3. At the left side of menu, right click Project, then select Create
Circulation Loop. Use Water Loop Heat Pump type for GSHP system.
4. Go back to right click Project again, select Create Ground Loop Heat
Exchanger, a window screen will pop up for all the detail design inputs
of GSHP system.
Tips:
1. Download Ground Loop HP Curves from
http://www.doe2.com/download/eQUEST/
2. Make sure you have enough accurate GSHP system design data for your
eQuest modeling. eQuest has no capability to autosize GSHP systems as
it does to other conventional HVAC systems.
Good Luck!
Bing
____________________
Bing Liu, PE, CEM
LEED Accredited Professional
Pacific Northwest National Lab
902 Battelle Blvd. MSIN: K5-16
Richland, WA 99352
Tel: 509.375.3710
Fax: 509.375.3614
-----Original Message-----
From: mail at smitagupta.com [mailto:mail at smitagupta.com]
Sent: Thursday, March 18, 2004 3:24 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] ground source heat pump in eQUEST
Hi,
Can anyone give me pointers to modeling a ground source heat pump in
eQUEST. I have never done this before and would appreciate any tips and
advise on how to go about it.
Thanks,
-Smita
@smitagupta.com
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20040319/7365eb77/attachment-0002.htm>
More information about the Bldg-sim
mailing list