Vikram and Jason,
I had a similar electric rate structure on a past project. I used a rate
schedule with each block having a flag value. For example, in the schedule
below, first 200 hours would be block 1 (flag value = 1), next 200 hours
would be block 2 (flag value = 2), next 200 hours would be block 3 (flag
value = 3), over 600 hours would be block 4 (flag value = 4). A 24/7 day =
"flag value" is needed for each block with a corresponding Week schedule.
The annual schedule would then break down each month as follows :
for any given month:
day 1 to day 8 Week 1 (200 hours/24 hours/day = 8.3 days, rounded to 8)
day 9 to day 17 Week 2 (400 hours/24 hours/day = 16.7 days, rounded to 17)
day 18 to day 25 Week 3 (600 hours/24 hours/day = 25 days)
day 26 to end of month Week 4
Setting up the annual schedule can get tedious but seemed to work when
checking by hand in the ES-E DOE2 report file. The DOE2 help files
concerning utility rates have an example of how to use the flagged rate
schedule.
Be careful of the KWH/KW-LIMITSUM blocks - I have only had luck getting the
limitsum to work when the schedule reads "first 200 kwh/ billing kW" not
when limit is based on hours.
Good Luck,
Sheila Sagerer
Energy Engineer
Energy Opportunities, Inc
-----Original Message-----
From: postman at gard.com [mailto:postman at gard.com]On Behalf Of K Emerson
Sent: Tuesday, March 09, 2004 10:10 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM]
Vikram, personally I'd just get the hourly data and
dump it into a spreadsheet. Keith Emerson
--- Jason Glazer <jglazer at gard.com> wrote:
> Vikram,
>
> Sounds like Georgia Power. I don't know exactly how
> to do
> this in DOE-2.2 but I know that it can be done in
> DOE-2.1e.
> If you look at Example 12 "Mixed Energy Block Types
> with
> Complex Demand Ratchets" on page 5.47 of the
> DOE-2.1e
> Supplement you will see this rate described (some of
> the
> numbers have changed since then).
>
> You will probably need to use the KWH/KW-LIMITSUM
> option. I
> think the only difference in DOE-2.2 is that the
> numbers in
> the block data are entered differently.
>
> Jason
>
> On 9 Mar 2004 at 13:28, Vikram Sami wrote:
>
> > Hi,
> > A project I'm currently workinghas a slightly
> complicated
> > electricity rate . I have already tried breaking
> up the
> > rates into 2 blocks - the first one is an energy
> block, and
> > the next one is a kWh/Kw block, but it doesnt
> seem to go to
> > the kwh/kw rate even when the ratio is over
> 200kwh/kw. Is
> > there something I am missing, or is it just
> something that
> > cant be modelled in eQUEST?
> >
> > Thanks
> >
> > Vikram Sami
> > _____
> >
> > Ensar Group Inc.
> > 2305 Broadway
> > Boulder, CO 80304
> > Tel: (303) 449-5226
> > Fax: (303) 449-5276
> >
> >
> >
> > _____
> >
> >
> > Base
> >
>
Charge......................................................
> > ..................................................
> $14.00
> > All consumption (kWh) not greater than 200 hours
> times the
> > billing demand: First 3,000 kWh
> >
>
............................................................
> > ..... at ............................. 8.757" per kWh
> Next
> > 7,000 kWh
> >
>
............................................................
> > ..... at ............................. 8.026" per kWh
> Next
> > 190,000 kWh
> >
>
............................................................
> > . at ............................. 6.910" per kWh
> Over 200,000
> >
>
kWh.........................................................
> > .... at ............................. 5.355" per kWh
> All
> > consumption (kWh) in excess of 200 hours and not
> greater
> > than 400 hours times the billing demand
> >
>
...................................................... at .....
> > ........................ 0.892" per kWh All
> consumption
> > (kWh) in excess of 400 hours and not greater than
> 600 hours
> > times the billing demand
> >
>
...................................................... at .....
> > ........................ 0.672" per kWh All
> consumption
> > (kWh) in excess of 600 hours times the billing
> demand
> >
>
........................................... at ................
> > ............. 0.586" per kWh Minimum Monthly Bill:
> A. $14.00
> > Base Charge plus $6.42 per kW of billing demand in
> excess of
> > 30 kW plus excess kVAR charges and Fuel Cost
> Recovery as
> > applied to the current month kWh.
> >
> >
> >
> >
> > _____
> >
> >
> >
> >
> >
> >
> >
> >
> > You received this e-mail because you are
> subscribed
> > to the BLDG-SIM at GARD.COM mailing list. To
> unsubscribe from
> > this mailing list send a blank message to
> > BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
>
=========================================================
> Jason Glazer, P.E. jglazer AT gard DOT com 847 698
> 5686
> GARD Analytics - http://www.gard.com/
> 1028 Busse Highway, Park Ridge, IL 60068
> Building Energy Simulation and Analysis
> Admin of BLDG-SIM list for building simulation users
>
>
=====================================================You
> received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To
> unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
__________________________________
Do you Yahoo!?
Yahoo! Search - Find what youre looking for faster
http://search.yahoo.com
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list