[BLDG-SIM] Infiltration: Standard versus Proposed Design
Marcus Sheffer
sheffer at paonline.com
Wed May 19 08:59:57 PDT 2004
Right now infiltration reduction is not an eligible item for energy cost
reduction for LEED. Infiltration rates must be the same in the proposed
and budget buildings.
My understanding is that the Energy & Atmosphere Technical Advisory Group
(EA TAG) of the USGBC is considering this issue with an eye toward
developing a modeling protocol.
I am aware of at least two projects that have applied for savings in this
area which have been put on hold (the LEED points were denied pending
further input from the EA TAG).
As At 10:33 AM 05/19/2004, you wrote:
>Can infiltration be considered in comparing standard versus proposed
>design models using the ECB method and for LEED credits under Optimize
>Energy Performance? Typically we use the same criteria in both models,
>but this is a particular case of a proposed double-wall
>building. 10CFR435 Table 402.2.1. Air Leakage for Fenestration & Doors
>Maximum Allowable Infiltration Rate provides standard model information
>for federal buildings. For example, the infiltration rate is 0.15 cfm/ft2
>for fixed aluminum windows. Can this be used for LEED standard design and
>can a lower rate be used for double wall buildings?
>
>The CFR table does not account for Heating & Cooling Degree Days as with
>Table-B Building Envelope Requirements of STD90. In my opinion, the peak
>design infiltration rate should be varied from maximum in winter to
>minimum in summer (typically zero for pressurized buildings) using a
>schedule. The maximum, of say 0.15 cfm/ft2, would apply to a cold climate
>such as Chicago and it should be scaled down for warmer climates. Since
>DOE2 does not allow infiltration rates on the basis of cfm/ft2 of wall or
>window area or cfm per lineal foot of window perimeter, we create a
>typical perimeter space and convert the window based infiltration rate to
>cfm/ft2 of space area or space air changes. We then look at the results in
>REPORT- LS-C BUILDING PEAK LOAD COMPONENTS of the DOE2 output to see if
>the infiltration load looks reasonable (relative to the other loads) for
>the location and type of building and make adjustments by trial and
>error. Judgment and experience is considered more reliable than
>theoretical mathematical models. The BEPS and BEPU reports in DOE2 should
>separate out the infiltration loads from the heating & cooling loads. Any
>comments?
>
>Thanks for the comments and suggestions to using different utilities in
>standard versus proposed design. They were very helpful in making some
>decisions here. Most of the responses seem to go directly to the person
>asking the question.
>
>Varkie Thomas
>Skidmore, Owings & Merrill LLP
>
>
>
>
>
>
>
>You received this e-mail because you are subscribed
>to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
>from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at GARD.COM
Marcus B. Sheffer energy & environmental consulting
Energy Opportunities, Inc 717-292-2636
1200 E Camping Area Road Fax: 717-292-0585
Wellsville, PA USA 17365-9783 sheffer at sevengroup.com
a 7group company www.sevengroup.com
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20040519/c2d40c1a/attachment-0002.htm>
More information about the Bldg-sim
mailing list