[BLDG-SIM] false load and MIN-RATIO entry
Derek Whitehead
Derek.Whitehead at keen.ca
Wed Jul 27 16:24:26 PDT 2005
I am modelling an open reciprocating chiller in DOE2.1e. When I specify a MIN-RATIO lower than the default value of 0.25, the PS-C report shows a false load on the chiller. When I specify a value of 0.25, no false load is reported. This suggests to me that hot gas bypass is being modelled.
The reference manual says that, if the item of equipment operates with a demand that is more than zero but less than the MIN-RATIO, the chiller will cycle on and off. Could someone please tell me what I'm missing? Thanks.
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list