[BLDG-SIM] eQuest question
    Jeff Haberl 
    jeffhaberl at tees.tamus.edu
       
    Wed May  4 07:12:29 PDT 2005
    
    
  
FYI
I would be very careful about underground calcs in DOE-2. I'm not sure about DOE 2.2, but DOE-2 users need to follow the latest advice from LBNL regarding effective U-values. 
Also, there is the issue of ground temps. DOE-2 uses the temps from the weather tape, and if this is Tmy-2,  Then these are synthetic temps from Kusuda's work in the 1960-70s, which may or may not be accurate. DOE-2 also does not calc infiltration below grade, so this needs adjusting. Finally, you must have CWFs turned to get an accurate answer. 
Jeff
BB 8=!  8=)  :=)  8=)  ;=)  8=)  8=(  8=)  :=')  8=)  8=)  8=? BB
Jeff S. Haberl, Ph.D., P.E.............................jhaberl at esl.tamu.edu
Professor......................................................Office Ph: 979-845-6507
Department of Architecture.......................Lab Ph: 979-845-6065 
Energy Systems Laboratory.......................FAX: 979-862-2457 
Texas A&M University..............................77843-3581
College Station, Texas, USA.......................URL: www-esl.tamu.edu
BB 8=/  8=)  :=)  8=)  ;=)  8=)  8=()  8=) 8=?  8=)  8=)  8= BB
-----Original Message-----
From: postman at gard.com <postman at gard.com>
To: BLDG-SIM at gard.com <BLDG-SIM at gard.com>
Sent: Wed May 04 08:45:17 2005
Subject: [BLDG-SIM] eQuest question
Don,
In addition to Renee's points, heres my 2 bits
1. I havent done it by converting an external wall to an underground wall before. I would be wary of just changing the properties (i.e. construction materials). I think there is a different thermal calculation set for underground walls than exterior walls (no solar radiation for instance), but to be honest I havent read the DOE2.2 documentation on this. What I normally do (and this might be what Renee was describing) is to right click on the space that you want the underground wall. It offers 3 child components that you can create - exterior, interior, and underground. I would pick underground, and then copy its properties from the exterior wall, before deleting the extrior wall.
2. If you are modelling district energy (either steam or chilled water), you should also create meters for them.
4. yes - you can model it as an exterior shade.
Vikram Sami,  LEED AP
Direct Phone 404-253-1466 | Direct Fax  404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
Responsive Design * Technological Expertise * Exceptional Service
www.lordaecksargent.com
-----Original Message-----
From: postman at gard.com [mailto:postman at gard.com]On Behalf Of Renee J.
Azerbegi
Sent: Tuesday, May 03, 2005 11:22 PM
To: BLDG-SIM at GARD.COM
Subject: [BLDG-SIM] eQuest question
Don, See below for your answers.
Renee
-----Original Message-----
From: postman at gard.com [mailto:postman at gard.com] On Behalf Of Don Saal
Sent: Tuesday, May 03, 2005 3:19 PM
To: BLDG-SIM at GARD.COM
Subject: [BLDG-SIM] eQuest question
To all,
A few questions regarding the modeling ability of eQuest:
1.  Can you model portions of a given shell as underground and exterior
wall?  If so, how (in the detailed mode)?
YES - IN DETAILED EDIT COPY THE EXISTING WALL THAT IS PARTIALLY UNDERGROUND
AND ADD ANOTHER WALL. CHANGE THE HEIGHT OF EACH WALL SO THAT THE TOTAL IS
THE SAME AS THE ORIGINAL WALL. CHANGE THE UNDERGROUND WALL TYPE TO
UNDERGROUND WALL AND DEFINE THE CHARACTERISTICS.
2.  The building in question gets its chilled and hot water from a central
facility.  Can you model this?
YES. IN DETAILED EDIT MODE MODEL AS DISTRICT HOT WATER AND DISTRICT CHILLED
WATER. INCLUDE THE EFFICIENCY OF THE HEAT EXCHANGERS (CONVERTERS).
3.  Can custom wall types, area types, etc be created to be used in the
Design Wizards?  Or can custom types only be used in the detailed mode?
I BELIEVE ONLY IN DETAILED EDIT MODE YOU CAN CREATE CUSTOM FEATURES.
4.  In the detailed mode, can you identify an exterior wall adjacent to a
conditioned space (ie another building that is not being modeled)?
YES.
Thank you for any input.  If you know of any resources (for eQuest
specifically) that address these issues and others please let me know.
SEE WWW.DOE2.COM FOR LIBRARY OF INFORMATION ON DOE2.2 (EQUEST/POWERDOE)
RENEE, AMBIENT ENERGY, INC.
Sincerely,
Don Saal, PE
Mechanical Systems
Affiliated Engineers, Inc.
5802 Research Park Blvd.
Madison, WI 53719
Phone: 608-236-1150 (direct)
Fax: 608-238-2614
Email: dsaal at aeieng.com
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
    
    
More information about the Bldg-sim
mailing list