[bldg-sim] eQUEST question - error with construction tab

Mattias Jarvegren x263 mattiasj at clallampud.net
Tue Sep 20 14:06:01 PDT 2005


A quick reminder before you go changing the inp file.  If you have put any substantial time into the project: make a back up copy of the inp file first.  Other than that, Mr. Sami's solution should do the trick for you.


Mattias

Mattias Järvegren
Utility Services Advisor
PUD No. 1 of Clallam County
2444 East Pioneer Road
P.O. Box 1090
Port Angeles, WA 98362
mattiasj at clallampud.net
Phone: (360) 565-3263
Fax:   (360) 452-9724 


-----Original Message-----
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Vikram Sami
Sent: Tuesday, September 20, 2005 1:38 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] eQUEST question - error with construction tab

Paul,
I tried repeating what I just suggested to you, and it turns out that you really cannot fix your problem without going into the inp file. It seems to be some kind of bug in the program, but it will not let you edit it in eQUEST. 

However, changing the inp is simple enough, so it shouldn't be a problem.


Vikram Sami,  LEED AP
Direct Phone 404-253-1466 | Direct Fax  404-253-1366 

LORD, AECK & SARGENT ARCHITECTURE
Responsive Design * Technological Expertise * Exceptional Service www.lordaecksargent.com 


-----Original Message-----
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Paul
Erickson
Sent: Tuesday, September 20, 2005 3:29 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] eQUEST question - error with construction tab

Hello,

I'm a DOE-2 (mainly VisualDOE) user just getting acquainted with eQUEST.

Has anyone else ever experienced a problem with the construction tab?  I
somehow inadvertently created a "new" construction that titles itself
"Construction", though when looking at the construction detail
window/screen, the "name" is actually blank.  This creates a problem
when I try to run eQUEST simulations...I get an error.

- When opening the file, it says that there is one BDL error.  I see the
error tree screen and it refers to a construction titled "Construction".
I double click on it, the construction tab comes up, I click "done" and
then it tells me there are no more errors.  However, when I run the
simulation, the output file is empty and I do not get the output reports
accessible through eQUEST.  

The inp and BDL files support the fact that there is a construction
error due to the lack of a name...only the command "CONSTRUCTION" is on
the line where it should be  "name" = CONSTRUCTION.

On the construction tab:

- I am not able to write a new name in for the construction.
- I cannot change the specification method.
- I can change the Construction Layers selection.
- I cannot delete the construction.  When I try I get a window that says
that there are no components that exist, but I get "error encountered
searching for keyword assignments."

Does anyone have a suggestion how to deal with this without going into
the inp file?  Or is there a way to manipulate the inp file and then
read it back into eQUEST?

Any help would be greatly appreciated. THanks!

Paul


==================
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM mailing list.  To unsubscribe from this mailing list
send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM


==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM



===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM



More information about the Bldg-sim mailing list