[BLDG-SIM] Condenser Water Reset in eQuest

Mike Tillou miket at etcgrp.com
Thu Aug 17 10:58:05 PDT 2006


> Hi all..I thought I would share a couple of tips on using Condenser
> Water Reset Strategies in eQuest . Hopefully some of you will find
> this useful.
> 
> We just finished modeling a chiller plant where we looked at using low
> condenser water temperatures ( below 60F ) as an energy efficiency
> measure.  The project is in a climate with very low wetbulb
> temperatures .  There are a couple of quirks I thought I would share
> about trying to model a strategy like this.  
> 
> The Condenser Loop Control tab has several options for resetting the
> loop temperature.  If you notice MIN-RESET-T always defaults to 70F. 
> 
> Issue  #1:  If you reset the Condenser loop MIN-RESET-T lower than 70F
> (say 65F) and then run an hourly report to check the loop temperature
> everything looks like it's working fine.  BUT..if you also check the
> chiller entering condenser temperature you will find it never goes
> below 70F even though the condenser loop says it should be lower.
> This is because the chiller has a keyword MIN-COND-T that defualts to
> 70F and cannot be changed from within eQuest.  You have to change the
> keyword manually in the input file by adding the line, MIN-COND-T = 65
> underneath the definition of your chiller.
>   
> The most likely reason this defaults to 70F is because the default
> chiller performance curves were not designed for condenser
> temperatures below 70F  ( someone should correct me if this is wrong)
> 
> 
> If you want to try and model condenser water temperatures below 70F I
> highly recommend you create custom performance curves that include
> data points that describe the operation of your chiller at the
> appropriate condenser water conditions.
> 
> That brings me to Issue #2.
> 
> The MIN-COND-T keyword has a lower limit of 60F.  In other words even
> if you create the appropriate performance curves  and then try to set
> MIN-COND-T lower than 60F you will get a simulation error.  
> 
> You can work around this by using the DIAGNOSTIC keyword "NO-LIMITS".
> In effect this turns off both the Max and Min keyword limits.  You can
> then simulate chiller operation with very low condesner water
> temperatures.  
> 
> If you use the "NO-LIMITS" keyword do so very carefully.  This is a
> very important error checking function of DOE2.2 eQuest.
> 
Mike 


Michael Tillou, PE
etc Group, Inc.
PO Box 7, Williamstown, MA 01267
ph. (413) 458-9870 fx. (413) 458-9875




 




===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20060817/0b276db7/attachment.htm>


More information about the Bldg-sim mailing list