[BLDG-SIM] eQUEST Condensing Boiler Curve
Mark Nieman
MARKN at McKinstry.com
Thu Dec 21 09:42:04 PST 2006
Using eQUEST v.3.6, I've taken a stab at creating a performance curve
for an Aerco KC1000 condensing boiler. I've defined BOILER:HIR-FT =
"Aerco-KC1000-HIR-fEWT&LWT" as shown below. This boiler is being used
for a water source heat pump condenser water loop with a CT/HX & two
condensing boilers, piped in a primary loop configuration.
"Aerco-KC1000-HIR-fEWT&LWT" = CURVE-FIT
TYPE = BI-QUADRATIC-T
INPUT-TYPE = DATA
INDEPENDENT-1 = ( 180, 180, 180, 80, 80, 80, 100, 100, 100, 120,
120,
120, 140, 140, 140, 160, 160, 160 )
INDEPENDENT-2 = ( 180, 90, 135, 90, 135, 180, 90, 135, 180, 90,
135,
180, 90, 135, 180, 90, 135, 180 )
DEPENDENT = ( 1, 1.023, 1.019, 1.151, 1.077, 1.065, 1.102,
1.047,
1.038, 1.053, 1.026, 1.017, 1.033, 1.017, 1.012, 1.023, 1.017,
1.007 )
..
Question: Is this a proper curve for this equipment? Any comments and
critiques would be much appreciated. Part of my difficulty is that
HIR-FT is a Bi-Quadratic-T or Bi-Linear-T curve that needs two
temperatures (EWT & LWT) to define the HIR ratio modifier. When looking
at the curves, it's stated as thermal efficiency vs. EWT (return water
temperature) on several different curves based on fire rate of the
boiler. Basically, I assumed a LWT based on firing rate (90F=25%,
135F=75% & 180F=100%). I'm not sure if this is reasonable or not. Per
the manual, the DEPENDENT variable is the ratio of the actual efficiency
(based on the curves) / rated efficiency (at full fire, full load).
INDEPENDENT-1 = EWT, INDEPENDENT-2 = LWT.
The link to the data sheet is here:
http://www.aerco.com/cgi-bin/docsserv.cgi?idDocument=344
Mark Nieman, PE, CEM
Sr. Energy Engineer
McKinstry Essention
Direct: (206) 832-8152
Cell: (206) 510-4760
FAX: (206) 832-8552
http://www.mckinstry.com
"For The Life Of Your Building"
This email is the property of McKinstry or one of its affiliates and may contain confidential and/or privileged information. If you are not the intended recipient or have received this e-mail in error please notify the sender immediately and delete this e-mail.
Any unauthorized copying, disclosure or distribution of the material in this e-mail is strictly forbidden.
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20061221/27fc1ae9/attachment.htm>
More information about the Bldg-sim
mailing list