[BLDG-SIM] System Type in Appendix G
gail
gail22 at gmail.com
Tue Dec 12 11:42:41 PST 2006
Hi Bill,
Your interpretation is the correct interpretation. This is specific to
Appendix G (the Performance Rating Method), and does not impact basic code
compliance (the Energy Cost Budget Method from Chapter 11).
I expect the change was made in order to encourage the selection of more
efficient system types for various buildings. With the energy cost budget
method, buildings that select inherently efficient system types are not
credited for this selection because the Baseline case moves with the
Proposed case. Similarly, buildings that select inherently inefficient
system types are not penalized for this selection. Appendix G attempts to
correct this by
You are correct that the number of systems modeled in the baseline building
may be high.
Gail Stranske
CTG Energetics, Inc.
On 12/12/06, Bill Talbert <btalbert at aeieng.com> wrote:
>
> All,
> I'm working on a LEED energy analysis for a small healthcare clinic
> project (~15K sqft). According to A90.1-2004 Appendix G, Table G3.1.1A,
> the baseline HVAC system for a nonresidential building with <=3 floors, <75K
> sqft, and fossil fuel heating should be a packaged single zone system with
> DX cooling and a gas-fired furnace for heating. This seems like a big
> departure from the baseline system types indicated in the ECB method. Is
> this a correct interpretation? If so, can anyone provide feedback as to why
> this change was made? It seems as though many buildings of this size
> would utilize a packaged rooftop VAV. Also, it potentially makes the number
> of systems necessary in the baseline building significantly high unless the
> thermal blocks are simplified in the proposed design model.
> Thanks,
> Bill Talbert, LEED AP
> Mechanical Engineer
> Phone: (608) 441-6677
>
>
>
>
>
> ======================================================
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20061212/d47e960f/attachment-0002.htm>
More information about the Bldg-sim
mailing list