My understanding is that in App-G, the baseline
building fan power is calculated out from section
G3.1.2.9, while the proposed building will have the
actual designed fan power. Hence, the baseline
building and proposed building can have different fan
powers and thus, credit is given to good duct design.
Gerald
--- David S Eldridge <DSE at grummanbutkus.com> wrote:
>
> I think you have got it, the ECB Chapter 11 for code
> compliance, says to
> use the same kW/cfm in both models, with an upper
> limit on the baseline
> building fan system's power consumption.
>
> If you are performing a LEED EAC1 calculation (or
> other performance
> rating), Appendix G will use the baseline model fan
> system at the power
> consumption limit regardless of the design system
> using more or less
> power.
>
> David
>
> > -----Original Message-----
> > From: bldg-sim at gard.com [mailto:bldg-sim at gard.com]
> On Behalf
> > Of shruti narayan
> > Sent: Friday, December 08, 2006 2:21 PM
> > To: bldg-sim at gard.com
> > Subject: [bldg-sim] ASHRAE 90.1 2004 fan system
> efficiency
> >
> > I am just trying to establish whether ASHRAE 90.1
> 2004
> > requires the proposed building to use the same fan
> system
> > efficiency (kW/cfm) as the baseline (Refer to page
> 69 of the
> > standard) for the Energy cost budget methodology.
> >
> > Have there been any previous variances on this?
> >
> > Any direction will help.
> >
> > Thanks
> >
> >
>
_________________________________________________________________
> > Get up-to-date with movies, music and TV. Its
> happening on
> > MSN Entertainment
> http://content.msn.co.in/Entertainment/Default
> >
> >
> >
>
======================================================
> > You received this e-mail because you are
> subscribed
> > to the BLDG-SIM at GARD.COM mailing list. To
> unsubscribe
> > from this mailing list send a blank message to
> > BLDG-SIM-UNSUBSCRIBE at GARD.COM
> >
> >
>
>
=====================================================You
> received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To
> unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
____________________________________________________________________________________
Have a burning question?
Go to www.Answers.yahoo.com and get answers from real people who know.
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list