[BLDG-SIM] Modeling VAVS system
    Graham & Megan 
    hamnmegs at ozemail.com.au
       
    Sat Jul  1 21:43:42 PDT 2006
    
    
  
Check the SS-R reports to pinpoint the system / zone of concern.  Could be a number of control or sizing issues leading to this result.  Note that hours outside throttling range during optimum start and night ventilative cooling periods get reported within these hours so if you have a lot of nighttime ventilative cooling hours everything may in fact be alright ...
  ----- Original Message ----- 
  From: Jaya Mukhopadhyay 
  To: BLDG-SIM at gard.com 
  Sent: Friday, June 30, 2006 5:42 AM
  Subject: [BLDG-SIM] Modeling VAVS system
  I was trying to model a VAVS system using DOE-2.1e.
  However, I am unable to get rid the fact that:
  PERCENT OF HOURS ANY SYSTEM ZONE OUTSIDE OF THROTTLING RANGE =  5.0
  Can anybody give me pointers to what I should be looking at in order to eliminate this inadequacy in results.
  Your help is greatly appreciated.
  Thanks
  Jaya Mukhopadhyay
------------------------------------------------------------------------------
  Want to be your own boss? Learn how on Yahoo! Small Business. 
===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20060702/c00abad3/attachment.htm>
    
    
More information about the Bldg-sim
mailing list