I have never found a way to do it directly, so what I have done in the past
is to create a PIU system with a dummy chilled water system to simulate the
DX cooling. You have to remember to change the chiller performance curves
to DX curves, and set the CHW pump head to 0 so there will be no pump
energy.
Keir Howell
Bluestone Energy Services, Ltd.
phone: 781-982-2888
fax: 781-982-2811
----- Original Message -----
From: "Rohini Brahme" <rbrahme at harc.edu>
To: <BLDG-SIM at gard.com>
Sent: Thursday, July 06, 2006 10:41 AM
Subject: [BLDG-SIM] equest - fan powered box + DX cooling
>
> Hi All:
>
> Is there a system in equest that will allow DX-cooling and fan powered
> boxes? I tried PIU and PVAV systems. The PIU system does not allow DX
> cooling and the VAV systems do not allow fan-powered boxes.
>
> Thanks
> - Rohini
>