Shrikar,
To simulate movable shades, you will need to create 2
or 3 schedules.
1) Shading schedule which is a multiplier on the
shading coefficient of the glass. Eq. if you specify
the shading multiplier of 0.5, it will half the SC of
the glass.Shading multiplier of 1 will not manipulate
the glass SC.
2) You will also need to create a radiation threshold
schedule to trigger whether your shades are open or
closed. for eq. if the solar radiation hitting the
window exceedes 50 btu.sq.ft, the shades will be
initiated.
In addition, if you have daylighting in your model,
you will need to also create a daylighting schedule
which should logically follow the SC schedule.
Hope this helps.
Gerald
--- shrikar bhave <shrikarbhave at gmail.com> wrote:
> Hello everybody,
>
> I am a student at Arizona State University and
> currently interning at
> ConSol, Stockton,CA.
>
> I want to apply shading screen to a waste window
> with schedule ( so that It
> will be functional only during daytime on cooling
> design days and
> nonfunctional during heating design days)
> This residense is located in Roseville, CA. I am
> modelling this in eQUEST
> 3.55.
>
> I tried applying schedules and facing problem with
> that. esp what to assign
> in 'maximum solar schedule'.
>
> I would appreciate If anybody can help with this !
>
> Thanks and regards,
>
> Shrikar Bhave.
> 480 577 0370
>
>
>
======================================================
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To
> unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
__________________________________________________
Do You Yahoo!?
Tired of spam? Yahoo! Mail has the best spam protection around
http://mail.yahoo.com
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list