WINDOW program has comprehensive database of glasses, and in its newest
version 6.1, it also includes glasses that are partially or fully diffuse,
however, I am not sure if there are any stained glass entries.
BTW. there is no SHGC or U-factor data for single layers. Instead, there is
conductivity of glass, surface emissivities (e_f and e_b), Transmittance
(Tau), and front and back reflectance (Rho_f and Rho_b). Tau, Rho_b, and
Rho_f are given for each wavelength band from and inclusive of UV to near IR
(NIR). This data is obtained by measurements in a spectrophotometer with an
integrated sphere. For diffusing layers, it is desirable if these data is
also given for each incidence angle in the form of a matrix of incidence and
outgoing directions (i.e., Bi-Directional Transmittance and Reflectance
Distribution Functions or BTDF and BRDF). Bi-Directional measurements are
more complex because of the need to measure individual outgoing directions,
subject to individual incident directions. With these basic data, WINDOW
program calculates U-factor and SHGC for a glazing system that may consist
of single or multiple layers. So U-factor and SHGC is pertinent to glazing
system, as exposed to outdoor and indoor boundary conditions, not single
isolated layers.
D. Charlie Curcija
DesignBuilder Software
18 Tanglewood Rd.
Amherst, MA 01002
Tel: (413) 256-4647
Fax: (413) 256-4823
cell: (413) 575-3487
email: curcija at designbuildersoftware.com
web: http://www.designbuildersoftware.com
Support open document format as the best way to assure full compatibility
and interoperability!
STATEMENT OF CONFIDENTIALITY
The information contained in this electronic message and any attachments to
this message are intended for the exclusive use of the addressee(s) and may
contain confidential or privileged information. If you are not the intended
recipient, please notify DesignBuilder Software immediately at either +1
(413) 256-4647 or at home at designbuildersoftware.com, and destroy all copies
of this message and any attachments.
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Justin Wong
Sent: Friday, October 20, 2006 5:34 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] SHGC ofstain glass
Hi all,
Does anyone has any idea where can I get shgc or thermal properties of
stain glass? Any answer to the question will be very much appreciated.
Justin Wong
==================
You received this e-mail because you are subscribed to the BLDG-SIM at GARD.COM
mailing list. To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list