[BLDG-SIM] : eQuest Underfloor Air
Tupper, Kendra
Kendra.Tupper at sf.fk.com
Mon Sep 18 15:26:24 PDT 2006
I'm trying to use eQuest to compare an Underfloor Air System and
conventional VAV system. I have modeled the Underfloor case according
to the Addison/Nall paper, and am having some issues with the return air
temperatures.
I have modeled two stratified zones (a lower occupied 5' zone, and an
upper 8' plenum space). A portion of the internal gains and window
conduction is modeled in the plenum space, and the return air path is
set to PLENUM. I expected a portion of the cooling loads to be
transferred to the return air, raising the return air temperatures, and
allowed the loads in the occupied zone to be met with a higher supply
air temp (SAT).
However, when I increase my SAT for the underfloor case, my cfm and fan
energy increases accordingly. I output hourly return air temps for the
two cases and found that they were the same - adding heat gains to the
plenum space did not increase the return air temps. Further, I adjusted
my heating and cooling setpoints for the zones, and found that the
return air temps are equal to these zonal setpoints, regardless of what
load is imposed on the plenum spaces.
Has anyone experienced this problem?
Thanks!
Kendra
Kendra Tupper
LEED(r) AP
FLACK + KURTZ
405 Howard Street 415.398.3833 Main
Suite 500 415.402.5840 Direct
San Francisco, CA 94105 415.433.5311 Fax
http://www.flackandkurtz.com kendra.tupper at sf.fk.com
<mailto:kendra.tupper at sf.fk.com>
This e-mail may contain confidential and/or privileged information.
If you are not the intended recipient (or have received this e-mail in
error)
please notify the sender immediately and destroy this e-mail.
Any unauthorized copying, disclosure or distribution of the material
in this e-mail is strictly forbidden.
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20060918/17b87e92/attachment.htm>
More information about the Bldg-sim
mailing list