[BLDG-SIM] eQuest Geo-thermal Heat Pump Sweeden-G functions
Xia Fang
xfang at emcengineers.com
Wed Apr 18 14:38:10 PDT 2007
Hi, all
When I define Geothermal heat pump with "Vertical Well Sweeden-G"
functions, I encountered warning messages in the detailed simulation
output saying no real root messages like this.
"**WARNING**************************************************************
********
Pump: GSHP Loop Pump cannot match the
system
flow at the minimum required head.
Required system flow = 125.7 gpm at head = 150.0
Pump balance point = 91.8 gpm at head of 85.1
If the pump was sized by default, most likely this
is caused by a primary equipment unit operating at
greater than its design flow, and causing a pressure
drop greater than design. Try increasing the pump
head or head ratio to compensate.
First occurrence is on 1/ 1, hour 2
CURINV: No real root for CURVE:
1 1.353483 0.015932 -0.369414 0.000000 0.000000 0.000000
CURINV: Result out of limits for CURVE:
-0.136926 0.180053 1.353483 0.015932 -0.369414 0.000000 0.000000
0.000000
X, Y, and Z: 1.000000 0.000000 1.344375 MMDDHH: 1 1 2"
Though I havenot put in pump GPM OR FLOW HEAD..... Has anyone
experienced this before? And what would be the fix to it?
Thanks
Xia