[BLDG-SIM] LEED energy saving calculations for Industrial Facility

Jon McHugh Jon.McHugh at h-m-g.com
Thu Apr 12 14:51:57 PDT 2007


Marcus,
 
I think a reasonable solution would be to include the heat loads from
machinery in the simulation but not the energy required to operate the
process load.  This can be accomplished by putting the process loads on
a separate "meter" in the simulation.  The energy required to operate
the process load is ignored by the other building meters for cooling and
lighting, but the heat addition for the process loads are accounted for.
 
In this way,  the LEED certification is for the building not the
process.
 
Many of he process measures for machine shops: compressed air controls,
fixing air leaks process, interlocking ventilation with welding or
painting operations, HVLP paint spray guns etc.  are not defined by the
building designer.   
 
 
 
Sincerely,
 
Jon McHugh, PE
________________________________

From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Marcus
Sheffer
Sent: Thursday, April 12, 2007 2:11 PM
To: BLDG-SIM at gard.com
Cc: yjiang_mit at yahoo.com
Subject: [BLDG-SIM] LEED energy saving calculations for Industrial
Facility


Under LEED v2.2 you must include all of the process loads and equipment.
 
The post-processing you describe was used under LEED v2.1 and is not
allowed under v2.2.
 
You are correct that the opportunity for savings will be less in this
type of facility as a result.  The USGBC has recognized that this is an
issue and is working on ways to address it.
 
Any thoughts are welcome.
 
Marcus Sheffer - Vice Chair USGBC EA TAG
Energy Opportunities, Inc/a 7group Company
1200 E Camping Area Road, Wellsville, PA  17365
717-292-2636, sheffer at sevengroup.com
www.sevengroup.com
 
 
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Yi Jiang
Sent: Thursday, April 12, 2007 4:17 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] LEED energy saving calculations for Industrial
Facility
 
We are working on a LEED NC 2.2 project to predict
energy savings with eQuest for a 200,000 sf machinery
workshop facility. 
 
One question we have is whether to include the process
loads in the workshop. We feel that it makes the most
sense to include the heat generated from the process
equipment as internal cooling load and treated by HVAC
systems. However, the electrical power specifically to
process equipment should not be included. For such a
machinery facility, the electrical power to process
equipment constitutes 50% of total electricity
consumption, and can significantly reduce the total
energy saving prediction by 10%. Has anyone has
experiences with such a industrial facility? Thanks
 
--Yi    
 

==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM


===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070412/201dd0d8/attachment-0002.htm>


More information about the Bldg-sim mailing list