[BLDG-SIM] crawl Space
Abaza, Hussein
ABAZAH at ecu.edu
Mon Apr 9 06:54:17 PDT 2007
If it is a sealed crawl space, you can simulate it as a separate zone,
but if it is not, then, you might need to look at the ventilation rate
in the crawl space; for example, if the entire crawlspace floor is
covered, then you can reduce the number of openings, if not then you
have to provide the minimum amount of opining on the crawlspace as
specified by code. Second; did you insulate the crawlspace walls or the
floor of the first floor?
Hussein Abaza, Ph.D.
Assistant Professor
Construction Management
East Carolina University
Rawl 332
Greenville, NC 27858-4353
Phone: (252) 328-4140
FAX: (252) 328-1165
Email: abazah at mail.ecu.edu
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of chad K
Sent: Sunday, April 08, 2007 5:46 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] crawl Space
Might anyone know how eQuest models crawlspace
calculations, specifically, how one can derive load
requirements for the crawlspace itself.
________________________________________________________________________
____________
Sucker-punch spam with award-winning protection.
Try the free Yahoo! Mail Beta.
http://advision.webevents.yahoo.com/mailbeta/features_spam.html
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list