[BLDG-SIM] Green Insulation Materials

karen hovenga - SBE karen.hovenga at sbe.com.au
Thu Aug 30 17:08:10 PDT 2007


 
What about polyester batts?

Here in Australia you can get them with up to 80% recycled PET. 

Karen Hovenga
ESD Engineer
sbe 
sustainable built environments 

-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Leonard
Sciarra
Sent: Friday, 31 August 2007 4:25 AM
To: BLDG-SIM at gard.com
Cc: Sean.Maxwell at csgrp.com
Subject: [BLDG-SIM] Green Insulation Materials

Another option would be rockwool insulation, primarily made from slag.
The issue is higher embodied energy costs due to the fabrication
process.  


Leonard Sciarra, AIA, LEED ap
312.577.6580 (Dir)
G E N S L E R | Architecture & Design Worldwide 30 West Monroe Street
Chicago IL, 60603
312.456.0123
leonard_sciarra at gensler.com 


-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Maxwell,
Sean
Sent: Thursday, August 30, 2007 12:21 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Green Insulation Materials

Have you considered cellulose insulation?  Damp-spray or
blown-in-blanket cellulose is a viable alternative to all of these
products.  

- impregnated with borate for excellent fire-resistance, mold and pest
control
- better than foam and batt insulation for sound management
- roughly R-3 per inch (about the same for fiberglass and low-density
spray foams)
- reduces infiltration significantly over batt insulation but not as
much as spray foam
- is roughly 1.5 times the cost of batt insulation (compared with 2
times the cost for LDF)
- installation defects are generally much easier to avoid than with batt
insulation
- generally good moisture management characteristics, though it has been
recommended to avoid applying directly to an exterior masonry assembly
- very low embodied energy - made from recycled newspapers

Green Fiber and National Fiber are two manufacturers that I am familiar
with in the northeast US.  


-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Kevin
Kyte
Sent: Thursday, August 30, 2007 12:06 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Green Insulation Materials

Commercially farmed soy is genetically modified.  
Genetically modified organisms require heavy pesticide use to grow.  
Pesticides are specifically designed to kill everything except a single
crop.
The man-made tandems cause us cancer and disease.
Health care is skyrocketing to epic proportions.
Our tax dollars go to an illegal war.
According to the law, which is apparently admissible in court, paying
taxes is a choice.

Don't tell the owner this, but there might be a better choice out there.


-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of David S
Eldridge
Sent: Thursday, August 30, 2007 11:24 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Green Insulation Materials

I wanted to chime in here since I spent my first 17 years as a Western
Illinois farm boy.

I think using the remnants of the soybeans that have already been used
for food purposes is a very good idea.  Not that there aren't other uses
for that material, or that there are both better and worse products to
use for insulation.  Also what industries are near the food plant so
that you can process and use the recovered material without shipping it
cross-country.

I think what you were hinting at in the second part Len is ethanol, then
yes that is a very complex issue with more variables than just energy.

As an aside, soybeans actually are a legume crop that reintroduces some
nutrients to the soil while growing, compared to corn which only takes
from the environment and can be a much more intensive as far as the
inputs required to grow them.  Many farmers will utilize crop rotations
where soybeans and corn are planted in alternating years to reduce the
amount of fertilizers used during the corn year.  Increasing the demand
for soybeans will help that balance.  (Where ethanol will tip the
balance towards more corn.)

Anyway, there are a lot of issues there, but probably not directly
related to building simulation.

David




> -----Original Message-----
> From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of
Leonard
> Sciarra
> Sent: Thursday, August 30, 2007 9:16 AM
> To: BLDG-SIM at gard.com
> Cc: klair at iastate.edu
> Subject: [BLDG-SIM] Green Insulation Materials
> 
> 
> I just found out that the soy based foams are made from the scrap of
the
> soybean plant after the bean ( protein ) has been removed for food.
> That said is using prime agricultural land for things like fuel and 
> building products the highest and best use of the land?  And when you 
> take into account conventional factory farming with its intensive use
of
> petroleum based fertilizers it becomes a complex issue.
> 
> Leonard Sciarra
> GENSLER
> 
> -----Original Message-----
> From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Kevin 
> Lair
> Sent: Thursday, August 30, 2007 6:49 AM
> To: BLDG-SIM at gard.com
> Subject: [BLDG-SIM] Green Insulation Materials
> 
> This is a challenge. I don't find soy being that great of an solution 
> given soybeans are not the ideal crop for sustainability, and the 
> protein
used
> is
> can be used for other things to make the foam. I think the best
product
> is
> straw products such as Stramit, but there are very limited options in 
> the US.
> Agriboard is a SIP panel with straw and is expensive upfront but will 
> pay off in overall savings. Again, these are probably not the 
> solutions you
are
> looking for in this large commercial project either, but that is
mostly
> what I
> have come across.
> 
> I also don't care for foam in that it is not a product that promotes 
> later reuse of the materials, or a more dynamic interactive envelop. 
> In the end, it seems like it mostly a trade-off to just have good 
> "green" by saving
in
> operation cost with good insulation and work for new products. If
there
> are
> better alternatives out there I would love to know as well.
> 
> 
> Kevin Lair
> (kslair at syr.edu)
> Assistant Professor, School of Architecture Syracuse University 350 W.

> Fayette Street Syracuse, NY 13202
> 
> 315 443 0298
> c: 515 418 1903
> 
> 
> > Does anyone know of any insulation materials that are particularly 
> > environmentally friendly in terms of embodied energy and life cycle 
> > cost?
> >
> > I am familiar with a soy-based spray foam and have heard of recycled

> > denim insulation being used in residential projects, but this is for
a
> > large commercial project in which code requires flame retardant 
> > insulation.
> >
> > Any ideas on green insulation materials that could be used in
> commercial
> > buildings?
> >
> > Thanks a lot!
> >
> > Kendra Tupper
> > LEED(r) AP
> >  FLACK + KURTZ
> > "Ensuring that today's built environment preserves the natural 
> > environment in which we all live."
> > 405 Howard Street		415.398.3833 Main
> > Suite 500			415.402.5840 Direct
> > San Francisco, CA 94105		415.433.5311 Fax
> > http://www.flackandkurtz.com	kendra.tupper at sf.fk.com
> > P  Please consider the environment before printing this e-mail
> >
> > This e-mail may contain confidential and/or privileged information.
> > If you are not the intended recipient (or have received this e-mail
in
> > error)
> > please notify the sender immediately and destroy this e-mail.
> > Any unauthorized copying, disclosure or distribution of the material

> > in this e-mail is strictly forbidden.
> >
> >
> >
> > =====================================================You received
this
> e-
> mail because you are subscribed
> > to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe from this 
> > mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
> 
> 
> Kevin Lair
> 
> 515 418 1903
> 
> Steering Committee GDRC(Green Design Research Collaborative)
> http://gdrc.iastate.edu <http://gdrc.iastate.edu/>
> 
> Co-Founder DRC (Design Research Consortium)
> http://cart.design.iastate.edu/drc/
> 
> Affiliate CBER (Center for Building Energy Research)
> http://www3.me.iastate.edu/cber/
> 
> Co-founder and member AFHIowa (Architecture for Humanity Iowa)
> http://afhiowa.org <http://afhiowa.org/>
> 
> Affiliate Center for Crops Utilization (CCUR)
> http://www.ag.iastate.edu/centers/ccur/
> 
> Advisory Board Member Center on Sustainable Communities
> http://www.icosc.com/
> 
> 
> 
> Principal Westbrook Design http://www.westbrookdesign.com
> <http://www.westbrookdesign.com/>
> 
> Director Westbrook Artists Site (WAS)  http://www.westbrookartists.com
> <http://www.westbrookartists.com/>
> 
> Board Member Ghana Education Project (GEP)
> http://www.ghanaeducation.org/
> 
> Founder/Principal MOD-ECO Architecture http://www.mod-eco.net
> <http://www.mod-eco.net/>
> 
> 
> 
> 
> 
> ======================================================
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
> 
> 
> ==================
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM


You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM




======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM


==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM


==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM


===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM



More information about the Bldg-sim mailing list