[BLDG-SIM] System 6 and High Efficiency Window
Fred Porter
fporter at archenergy.com
Thu Aug 23 16:23:35 PDT 2007
Newer DOE-2.2 versions allow choice of keyword COOL-SOURCE for PIU
system type. Values either ELEC-DX or CHILLED-WATER. Choosing
COOL-SOURCE = ELEC-DX and, for the zones, TERMINAL-TYPE = PARALLEL
creates "System 6."
This option may only be available in text mode. See the latest I can't
find it on the menu screens in my version of EQ v3.61.
--
Fred W. Porter, B.S., LEED A.P.
Senior Engineer
Architectural Energy Corp.
_____
From: Garcia, Robert [mailto:RGarcia at akf-eng.com]
Sent: Thursday, August 23, 2007 10:57 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] System 6 and High Efficiency Window
There seems to be little reponse to the issue of modeling System 6 of
ASHRAE 90.1-2004. Has anyone been able to model a Packaged VAV with PFP
Boxes in eQUEST?
Robert Garcia
AKF Engineers, LLP
1500 Walnut Street, Suite 1400
Philadelphia, PA 19102
Phone: (215) 282-2182
Fax: (215) 735-6706
www.akf-engineers.com
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of
Garcia, Robert
Sent: Wednesday, August 22, 2007 2:46 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] System 6 and High Efficiency Window
I would like to discuss question number 1 as well. Appendix G
specifies that Direct Expansion be used as the cooling type for
System 6. However, the PIU system in eQuest does not allow you to
use DX coils. I have seen several archived posts on this same
question that say to model a chiller equivalent to the DX coils, but
nothing further. I have redefined the chiller performance curves
accordingly with no success. Has anyone set up this system
succesfully in eQuest?
In response to Questions 2 and 3, the U-value and Shading Coefficient
of the glass has significant impact on the energy savings with the
HVAC system. In addition, the visible light transmittance of the
glass directly impacts the Daylighting controls within the rooms
affecting electric usage. The selection of glass should be
investigated when determining the window-wall ratio and the resulting
savings.
Robert Garcia
AKF Engineers, LLP
1500 Walnut Street, Suite 1400
Philadelphia, PA 19102
Phone: (215) 282-2182
Fax: (215) 735-6706
www.akf-engineers.com
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Virdi
Permana
Sent: Wednesday, August 22, 2007 1:59 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] System 6 and High Efficiency Window
Hello All,
Quick question on System 6: Package VAV w/PFP boxes.
1. How do you use system 6 in eQUEST? Do you have to use parallel
PIU at the zone?
2. At what percentage of window to wall ratio that high efficiency
can star contribute significant saving?
3. At what number is considered significant saving?
Any respond is greatly appreciated.
Sincerely,
Virdiansyah "Virdi" Permana
EMSI
Energy Analyst
(202) 291 3102 T
(202) 291 3107 F
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
D.COM blank message to bscribYou received this e-mail because you are
subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070823/9382893f/attachment-0002.htm>
More information about the Bldg-sim
mailing list