[BLDG-SIM] max number of tracked modifications exceeded
Vikram Sami
VSami at lasarchitect.com
Wed Aug 22 11:42:07 PDT 2007
Per Appendix G
7. Thermal Blocks - HVAC Zones Designed
Where HVAC zones are defined on HVAC design drawings, each
HVAC zone shall be modeled as a separate thermal block.
Exception: Different HVAC zones may be combined to create a
single thermal block or identical thermal blocks to which multipliers
are applied, provided that all of the following conditions are
met:
(a) The space use classification is the same throughout the thermal
block.
(b) All HVAC zones in the thermal block that are adjacent to glazed
exterior walls face the same orientation or their orientations vary by
less than 45 degrees.
(c) All of the zones are served by the same HVAC system or by the
same kind of HVAC system.
I would guess you do not need separate rooms if they are part of an HVAC
zone.
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
Responsive Design * Technological Expertise * Exceptional Service
www.lordaecksargent.com
Please don't print this email unless you really have to.
In the United States, we use enough office paper each year to build a
10-foot high wall that's 6,815 miles long or two and a half times the
distance from New York to Los Angeles.
~ Wisconsin Department of Natural Resources, "Recycling Facts and
Figures," PUBL CE-163, 2002.
________________________________
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Kevin
Kyte
Sent: Wednesday, August 22, 2007 1:29 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] max number of tracked modifications exceeded
Ok, this could be embarrassing, but I got to know.
Could anyone shed some light on this error message I keep getting? As
it turns out, I ended up with 405 zones. I heard Doe-2.1 was limited to
99zones, is there a new limit for Doe 2.2.
I was under the assumption that when modeling for LEED certification
each space in the architectural design should be modeled as a separate
space for building simulation, is this thought right or completely
wrong? Thanks for the help.
Kevin
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Ramana
Koti
Sent: Wednesday, August 22, 2007 11:50 AM
To: BLDG-SIM at gard.com
Cc: sbse at uidaho.edu
Subject: [BLDG-SIM] Renewable energy building projects
Dear all,
Is there a listing somewhere, of building projects with renewable energy
installations (in the US or worldwide), say in the order of size of
renewable energy installed etc?
Thanks,
Ramana Koti, LEED AP
Sustainable Building Analyst
ELEMENTS division of BNIM architects
106 W. 14th Street Suite 200
Kansas City, Missouri 64105
p 816.783.1635 f 816.783.1501
www.bnim.com| elements.bnim.com
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070822/bc04c8ed/attachment-0002.htm>
More information about the Bldg-sim
mailing list