[bldg-sim] Horizontal shading in EQUEST
Aulbach, John
jaulbach at nexant.com
Wed Jan 17 16:46:32 PST 2007
What do you mean by Horizontal Shading? Like fins (the device fin are
vertical, but cut down light horizontally) ??
I just ran a typical office (250,000 sf) in Fresno, CA in eQuest. When
I put 2.5 ft fins on all the windows, I got a slight decrease in heating
as well (but not to your % level).
I traded the 2.5 ft fins with 2.5 overhangs. I got a 15% decrease in
cooling, and a 13% decrease in heating. This building is dominated by
VAV/reheat. What I can surmise is that when the cooling load decreased,
the need to reheat decreased as well. That the building is not skin
dominated for energy.
Anyone else have a clue?
John R. Aulbach, PE, CEM
Project Manager
Nexant, Inc.
100 North Barranca, Suite 820
West Covina, CA 91791 USA
Phone: 626-430-9054
Fax: 626-430-9060
email: jaulbach at nexant.com
________________________________
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Jaya
Mukhopadhyay
Sent: Wednesday, January 17, 2007 3:25 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] Horizontal shading in EQUEST
I am examining several options for Horizontal shading for an office
building using EQUEST.
A synopsis of the answers is as follows:
Total Annual Energy MBTU Space Cooling MBTU Space
Heating MBTU
Unshaded Option 8380 2411.9 308.1
2.5 ft Horizontal shading on East West and South
7936.8 2178.8 284.2
5 ft Horizontal shading on East West and South
7835
2158
269.7
The Questions:
1. Its very baffling to see the heating consumption go down too. I
wanted to see an increase in heating on implementing the shading
devices. How can I justify that decrease?
2. The building has a total area of 210273 sqft. with 15 ft deep
perimeter zones. The shading reduces the energy consumption by 5 to 6 %.
Is that acceptable?
Any help is greatly appreciated.
Thank you
Jaya Mukhopadhyay
________________________________
Get your own web address.
<http://us.rd.yahoo.com/evt=49678/*http://smallbusiness.yahoo.com/domain
s/?p=BESTDEAL>
Have a HUGE year through Yahoo! Small Business.
<http://us.rd.yahoo.com/evt=49678/*http://smallbusiness.yahoo.com/domain
s/?p=BESTDEAL>
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070117/1027656c/attachment-0002.htm>
More information about the Bldg-sim
mailing list