[BLDG-SIM] Simulations Insensitive to Glass Changes
Taylor, Russell D UTRC
TaylorRD at utrc.utc.com
Mon Jul 23 14:46:37 PDT 2007
Brandon,
The first thing that I would do is open up the SIM file and look at the
LS-C report (Building Peak Load Components). This report tells you what
the total building envelope loads and internal heat gains are for peak
cooling and heating conditions. Here are the categories provided:
WALL CONDUCTION
ROOF CONDUCTION
WINDOW GLASS+FRM COND
WINDOW GLASS SOLAR
DOOR CONDUCTION
INTERNAL SURFACE COND
UNDERGROUND SURF COND
OCCUPANTS TO SPACE
LIGHT TO SPACE
EQUIPMENT TO SPACE
PROCESS TO SPACE
INFILTRATION
Since your building appears very insensitive to changes in glazing
U-value my guess is that this report will show that "WINDOW GLASS+FRM
COND" is small compared to the other loads or that one of these other
loads is much larger than the rest. This result may be correct,
especially if the gazing fraction of the facade is low. However, if
"UNDERGROUND SURF COND" is the largest conduction load then you may need
to set U-EFFECTIVE for the slab floors (reasonable values are between
0.01 and 0.02).
You may also find that the building is much more sensitive to changes in
window solar heat gain coefficient than changes in U-value.
Russ Taylor
________________________________________________________________________
_______
Russell D Taylor, Ph.D.
UTRC | 411 Silver Lane, MS 129-85 | East Hartford, CT 06108 | Ph: (860)
610-7485
________________________________________________________________________
_______
________________________________
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Brandon
Nichols
Sent: Monday, July 23, 2007 5:10 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Simulations Insensitive to Glass Changes
All,
I have a 3-story historic building, with circa-1920's windows on all
four exposures. Big, beautiful, clear-glass single-pane architectural
masterpieces. So while doing an optimization study, it became apparent
to me that substantially changing the U-value and infiltration
coefficients was having very little effect at all on the loads.
For example, varying the U-value from 1.27 to 0.55, 0.45 and at last
0.30 in the parametric runs using the 'simplified method' produced a
0.5% total (over all runs) change in the total energy consumption.
Selecting representative glass types using the 'library method' produced
essentially equivalent. Superimposing upon either of these a change in
the infiltration coefficient from 1/4" to 1/8" to 1/16" to 1/32"
produced no additional effect at all (the INF-METHOD = CRACK keyword is
specified) on the annual energy consumption.
Lastly, I changed the baseline glass to "unglazed opening", again with a
mystifying zero net effect on the overall energy consumption. It's as
if the glass is not being calculated at all, but I see no errors or
warnings in the SIM file.
Anyone have an idea on how to debug this?
Thanks in advance...
Brandon Nichols, PE
Mechanical
HARGIS ENGINEERS
600 Stewart Street
Suite 1000
Seattle, WA 98101
www.hargis.biz
d | 206.436.0400 c | 206.228.8707
o | 206.448.3376 f | 206.448.4450
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070723/a57a66cc/attachment-0008.htm>
More information about the Bldg-sim
mailing list